Slave Radian Power Consumption

Post by AllPawDrive » Tue Aug 04, 2020 3:45 pm

When a radian is placed in slave mode, if the master radian is handling the load and has not commanded the slave radian to provide power, does the slave use the idle power consumption of 34W or the off power consumption of 4W?

Thanks,

Dave

fcwlp
Forum Guru
Posts: 476
Joined: Wed Jan 22, 2020 9:40 am
My RE system: GS8048A, FM80 w/3,600 W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed
I also install and maintain grid-tied and off-grid systems, details will be given for these system if required
Location: 80 miles NE of Phoenix at 5500'

Re: Slave Radian Power Consumption

Post by fcwlp » Tue Aug 04, 2020 4:29 pm

Dave, with two Radians and a big battery bank are really concerned about 30W. Just kidding. :grin:

Starting on p.38 of the current GS8048a Operator Manual there is a good discussion of the Power Save function. It does state the following:

"Each inverter consumes approximately 30 watts of idle power while it remains on, even if it is not actively inverting or charging. The Power Save function allows the option to put part of a parallel system into a quiescent state known as Silent mode. This mode minimizes the idle consumption. The inverters will come on again when the loads require power."

Not sure where you found the "4W" number but it does reduce the power when the slaves are idle.

AllPawDrive
Forum Whiz
Posts: 29
Joined: Thu Jul 23, 2020 8:08 pm
My RE system: Still shopping
Location: Prince Edward Island

Re: Slave Radian Power Consumption

Post by AllPawDrive » Tue Aug 04, 2020 6:49 pm

fcwlp wrote:
Tue Aug 04, 2020 4:29 pm
Dave, with two Radians and a big battery bank are really concerned about 30W. Just kidding. :grin:
I’ve probably watched Apollo 13 too many times.
fcwlp wrote:
Tue Aug 04, 2020 4:29 pm
Not sure where you found the "4W" number but it does reduce the power when the slaves are idle.
From page 57 of the version of the manual currently on outback’s website. Too large to attach.

Dave

fcwlp
Forum Guru
Posts: 476
Joined: Wed Jan 22, 2020 9:40 am
My RE system: GS8048A, FM80 w/3,600 W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed
I also install and maintain grid-tied and off-grid systems, details will be given for these system if required
Location: 80 miles NE of Phoenix at 5500'

Re: Slave Radian Power Consumption

Post by fcwlp » Tue Aug 04, 2020 7:51 pm

AllPawDrive wrote:
Tue Aug 04, 2020 6:49 pm
From page 57 of the version of the manual currently on outback’s website.
Thanks for the heads up. I was still using the 2014 Operator's manual. Outback moved most of the "Power Save" section from the 2014 Operator's manual to the 2017 Installation manual.