Battery Type? For Lithium 48V (Simpliphi)

A place to post images of your OutBack Power System

Moderators: OutBack, OutBack Moderator Team

Post Reply
dmaskal
Forum Member
Posts: 5
Joined: Sun Jan 19, 2020 10:49 pm
My RE system: Mate 3, Charge Controler (FX80(x2)), Inverter FXR/VFXR(×2), Battery bank (Simpliphi) 48V(x2),305W panels (3x3), On grid.
Location: Addis Abeba, Ethiopia
Contact:

Battery Type? For Lithium 48V (Simpliphi)

Post by dmaskal » Mon Jan 20, 2020 6:00 am

Greetings. Just setup an OutBack FlexMax system with Simpliphi, Lithium Ferro Phosphate, batteries (LHPl). Is there a software/firware update for FX80 Charge controller to accomodate LFP type batteries?

Did not recieve any information with pre-configured system.
Last edited by dmaskal on Mon Feb 03, 2020 5:13 am, edited 2 times in total.

raysun
Forum Emperor
Posts: 1649
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower One: FX3048T, (2) FM80, MATE3s, FlexNetDC
Outback 200NC batteries (8 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: Batter type? For Lithium 48V (Simpliphi)

Post by raysun » Mon Jan 20, 2020 7:45 am

No specific firmware update that I'm aware of,but both Outback and SimpliPhi have published application notes on integration.

User avatar
Kurt Lundquist
Alpha Energy Engineering
Posts: 1447
Joined: Tue May 31, 2011 7:23 am
My RE system: VFX3524, Mate3, 200Ah 24V AGM Battery Bank
Location: Arlington, WA

Re: Batter type? For Lithium 48V (Simpliphi)

Post by Kurt Lundquist » Mon Jan 20, 2020 7:47 am

A firmware update is not necessary. Simpliphi has a guide for the settings you should use: https://simpliphipower.com/wp-content/u ... -guide.pdf

-Kurt
Kurt Lundquist
Renewable Energy Project Engineer
http://alphaenergy.us/

dmaskal
Forum Member
Posts: 5
Joined: Sun Jan 19, 2020 10:49 pm
My RE system: Mate 3, Charge Controler (FX80(x2)), Inverter FXR/VFXR(×2), Battery bank (Simpliphi) 48V(x2),305W panels (3x3), On grid.
Location: Addis Abeba, Ethiopia
Contact:

Re: Battery type? For Lithium 48V (Simpliphi)

Post by dmaskal » Fri Jan 24, 2020 11:34 pm

Raysu & Kurt, thanks from your prompt responce.
Could only find Upgraded Mate3s (to ver.03.019.001). Hoping recognition of LFP type battery will do some of my configuring. You were correct it does not.

I have Simpliphi's integration guide and Notes. I am getting it, slowly.

Will configure this week and get back to end this thread.
Last edited by dmaskal on Mon Feb 03, 2020 5:13 am, edited 1 time in total.

dmaskal
Forum Member
Posts: 5
Joined: Sun Jan 19, 2020 10:49 pm
My RE system: Mate 3, Charge Controler (FX80(x2)), Inverter FXR/VFXR(×2), Battery bank (Simpliphi) 48V(x2),305W panels (3x3), On grid.
Location: Addis Abeba, Ethiopia
Contact:

Re: Battery type? For Lithium 48V (Simpliphi)

Post by dmaskal » Wed Jan 29, 2020 10:01 am

The system powered up okay and has been running for 48hrs.

Conserned about overcharging lithium batteries. Because inverter low battery cut-out voltage will not go above 48V. Recommended is 50.4V @ 130 sec delay.

Battery "type" is just an information field and does not change configuration or set points.

Your thoughts would be appreciated.
Last edited by dmaskal on Mon Feb 03, 2020 5:14 am, edited 1 time in total.

raysun
Forum Emperor
Posts: 1649
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower One: FX3048T, (2) FM80, MATE3s, FlexNetDC
Outback 200NC batteries (8 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: Batter type? For Lithium 48V (Simpliphi)

Post by raysun » Wed Jan 29, 2020 10:24 am

Is there an FNDC in the system?

dmaskal
Forum Member
Posts: 5
Joined: Sun Jan 19, 2020 10:49 pm
My RE system: Mate 3, Charge Controler (FX80(x2)), Inverter FXR/VFXR(×2), Battery bank (Simpliphi) 48V(x2),305W panels (3x3), On grid.
Location: Addis Abeba, Ethiopia
Contact:

Re: Batter type? For Lithium 48V (Simpliphi)

Post by dmaskal » Thu Jan 30, 2020 4:16 am

Yes . FLEXnet DC, set to: Charge Termination Y, Auto grid-tie N, Low SOC 20%, Critical SOC 10%.

User avatar
Kurt Lundquist
Alpha Energy Engineering
Posts: 1447
Joined: Tue May 31, 2011 7:23 am
My RE system: VFX3524, Mate3, 200Ah 24V AGM Battery Bank
Location: Arlington, WA

Re: Batter type? For Lithium 48V (Simpliphi)

Post by Kurt Lundquist » Thu Jan 30, 2020 8:20 am

See pages 6-7 of the following app note for instructions on how to wire the FNDC relay to the Master FXR On/Off terminals.

http://www.outbackpower.com/downloads/d ... p_note.pdf

You can set the FNDC relay to cut out at 50.4 to turn the inverter off to help prevent the battery from over-discharge. Remember to pull the blue jumper on the inverter where it says On/Off after you wire to the terminal block. Manually test the setup by turning the FNDC relay On/Off to make sure it is working.

-Kurt
Kurt Lundquist
Renewable Energy Project Engineer
http://alphaenergy.us/

dmaskal
Forum Member
Posts: 5
Joined: Sun Jan 19, 2020 10:49 pm
My RE system: Mate 3, Charge Controler (FX80(x2)), Inverter FXR/VFXR(×2), Battery bank (Simpliphi) 48V(x2),305W panels (3x3), On grid.
Location: Addis Abeba, Ethiopia
Contact:

Re: Battery type? For Lithium 48V (Simpliphi)

Post by dmaskal » Sat Feb 01, 2020 12:33 pm

The FN-DC and FN-DC Comm Port are in two adjacent breaker slots. And I think they are connected.

Inverter firmware is 001.006.015 According to application notes this should allow setting LBCO to 50.4V. However I cannot go above 48V. This is bugging me.

The system was integrated (pre-configured) by Outback. It does not appear to be wired to the on/off relay on inverter and blue jumper is still in-place. So I will have to shut down and trace wires to make sure.

So if I need to wire relay contacts as per App Notes. Can I assume only the master inverter needs to be wired?

Post Reply