How do I clear the data shown on the attached screenshot?

I think I went through all the MATE3s screens and cleared everything I could find. All other data items on the MATE3s web portal have cleared except the ones shown on the attached image.

Thanks!
Attachments
battery-info.jpg

Mike Curran
Forum Emperor
Posts: 1089
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback:
- 8 (2x4) Evergreen 180's into one MX60 (2007)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied GVFX3524's classic stacked for 120/240VAC (2007)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.

Westinghouse Solar: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied.

All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: How to clear data

Post by Mike Curran » Tue Jun 25, 2019 4:45 pm

I've never seen that screen, but I've only had a Mate3s for about a month. How do you get to it? Is it in Optics somewhere?
http://www.tigoenergy.com/site.php?95b2dca2-ca6c
https://enlighten.enphaseenergy.com/public/systems/Hctc107221

raysun
Forum Czar
Posts: 649
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower One: FX3048T, (2) FM80, MATE3s, FlexNetDC
Outback 200NC batteries (8 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 Strings @ 2 Series)
Hyundai 355 watt panels (6 - 3 strings @ 2 series)

Re: How to clear data

Post by raysun » Tue Jun 25, 2019 9:33 pm

That looks like the onboard web site. Is it?

svsimple
Forum Member
Posts: 13
Joined: Fri Feb 15, 2019 6:56 am
My RE system: FlexMax 60 / MATE3S / Solara 140W Panels

Re: How to clear data

Post by svsimple » Wed Jun 26, 2019 2:01 am

It's on the STATUS web page for the MATE3s.

raysun
Forum Czar
Posts: 649
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower One: FX3048T, (2) FM80, MATE3s, FlexNetDC
Outback 200NC batteries (8 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 Strings @ 2 Series)
Hyundai 355 watt panels (6 - 3 strings @ 2 series)

Re: How to clear data

Post by raysun » Wed Jun 26, 2019 9:00 am

Is there a FlexnetDC in the system.

svsimple
Forum Member
Posts: 13
Joined: Fri Feb 15, 2019 6:56 am
My RE system: FlexMax 60 / MATE3S / Solara 140W Panels

Re: How to clear data

Post by svsimple » Wed Jun 26, 2019 2:18 pm

Yes, there is an FNDC in the system. I'm not 100% sure since it's been installed for about 3 months, but I believe that section of the Status page only started showing after the FNDC was installed. Before, with just the MATE3s and the FM60 controller that section was blank (i'm 90% sure).

raysun
Forum Czar
Posts: 649
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower One: FX3048T, (2) FM80, MATE3s, FlexNetDC
Outback 200NC batteries (8 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 Strings @ 2 Series)
Hyundai 355 watt panels (6 - 3 strings @ 2 series)

Re: How to clear data

Post by raysun » Wed Jun 26, 2019 4:42 pm

The Days since full counter is read from the FNDC. Since it's been installed for about the time on the counter, I'd guess the FNDC doesn't think the charge parameters have ever been met.

Check the battery and charge settings on the FNDC to see if there is a parameter set in a way that charge parameters can never be met.

Also, I seem to recall a factory reset option on the FNDC, but don't recall what all it touches.

svsimple
Forum Member
Posts: 13
Joined: Fri Feb 15, 2019 6:56 am
My RE system: FlexMax 60 / MATE3S / Solara 140W Panels

Re: How to clear data

Post by svsimple » Wed Jun 26, 2019 5:14 pm

Could it be from the Charged Return Amps setting for the FNDC?

I was told it had to be set to 2% of capacity.... but I have 1740 AH capacity, so 2% is a LOT. I called tech support and they said if I set it to such a high value it might prevent the solar system from continuing to charge the battery when it was only producing about 5 or 10 AH.

Do you know the specifics of that setting?

raysun
Forum Czar
Posts: 649
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower One: FX3048T, (2) FM80, MATE3s, FlexNetDC
Outback 200NC batteries (8 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 Strings @ 2 Series)
Hyundai 355 watt panels (6 - 3 strings @ 2 series)

Re: How to clear data

Post by raysun » Wed Jun 26, 2019 7:45 pm

From an old application note (7 steps to highly efficient FNDC programming):


The Return Amps must be entered. Return Amps, ADV/ DC/CHARGE This is the charge rate that is expected to be returned to your batteries when they are full or approaching full. This value is derived from a percentage of the total amp hours in your battery bank. This value can be obtained from your battery manufacturer. 2% of your total amp hours is a good default to establish our baseline. For example, a 250 Amp-hour battery bank @ 20hr discharge rate with a 2% value of return amps would be 250 x .02 = 5 amps. Another more concrete method to find your return amps value would be to charge your batteries until they are full using the battery manufacturer charging values to include specific gravity readings if applicable. Then simply do another rebulk and absorb. If you are using an off grid inverter simply turn off the AC source for about 1 minute, and turn on the generator again or reconnect the AC source. If you are using a grid interactive inverter that can sell back to the grid start a RE-BULK (push AC IN button 4 times). Then monitor the current holding your absorb voltage by viewing the shunt activity (positive amps) returning to the battery bank with no loads on the batteries at STATUS/DC/METER . Set the return amps to this value. FYI: This value will change as the batteries age. The return amps for brand new batteries could be as low as 1%. The return amps for older batteries may be as much as 3% perhaps more depending on their condition. Therefore, our suggested default value is 2%, and adjust the Battery Charge Factor (BCF) Step #5 if adjusting is needed.

svsimple
Forum Member
Posts: 13
Joined: Fri Feb 15, 2019 6:56 am
My RE system: FlexMax 60 / MATE3S / Solara 140W Panels

Re: How to clear data

Post by svsimple » Fri Jun 28, 2019 10:26 am

I set the Return Amps to 17 A (1%) and for the past two days the log shows the parameters are met a minute or two before the charger goes from BULK to ABSORB. Does this seem correct or should I tweak this a bit more so it is met at the end of ABSORB?

Does it even matter?

raysun
Forum Czar
Posts: 649
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower One: FX3048T, (2) FM80, MATE3s, FlexNetDC
Outback 200NC batteries (8 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 Strings @ 2 Series)
Hyundai 355 watt panels (6 - 3 strings @ 2 series)

Re: How to clear data

Post by raysun » Fri Jun 28, 2019 10:35 am

There are multiple parameters that need to be met before the FNDC sets the charge parameters met flag.

End Amps (or Charged Return Amps I can't recall which label applies) is one.

Absorb Time is another, and is independent of the battery State of Charge. What's happening with the Absorb cycle? Is it running for the full Absorb Time?

gtarolli
Forum Guru
Posts: 222
Joined: Thu Dec 21, 2017 11:39 am
My RE system: Outback: off-grid
- 1 GS8048A, Mate3, FlexNetDC, Hub10.3
- 2 FLEXmax 80
- 24 (8x3) 300w panels (7200w total)
- 6 SimpliPhi 3.4 kWh LI batteries (400ah , 20kWh)
- 1 Honda 3000 generator + one spare
Location: Wainiha, Kauai, HI

Re: How to clear data

Post by gtarolli » Sat Jun 29, 2019 4:10 pm

I just reset them the other day on my Mate3. Look around on the mate menus, I think it is in the system config, battery voltage min/Max reset. Section s-12 on the mate3 pgm sheet.

gtarolli
Forum Guru
Posts: 222
Joined: Thu Dec 21, 2017 11:39 am
My RE system: Outback: off-grid
- 1 GS8048A, Mate3, FlexNetDC, Hub10.3
- 2 FLEXmax 80
- 24 (8x3) 300w panels (7200w total)
- 6 SimpliPhi 3.4 kWh LI batteries (400ah , 20kWh)
- 1 Honda 3000 generator + one spare
Location: Wainiha, Kauai, HI

Re: How to clear data

Post by gtarolli » Sat Jun 29, 2019 4:17 pm

My last post was only re: batter voltage. The days since full is reset by fndc when the charge params are met.