FX3048T Firmware update

Post by raysun » Tue Nov 28, 2017 11:55 am

My strictly off-grid system is built around a Flexpower One with FX3048T inverter. (The inverter was already obsolete at the time of installation, but it was what our local supplier had at the time.) One minor issue is during various configuration activities a warning message pops up stating that the firmware needs updating. The reported firmware version is 67.0.0

Is there a firmware update for this inverter? If so, the firmware field updateable or does it require factory service?

Also, is the service manual for the FX3048T available? (The website returns a 404 when clicking on the appropriate link.)

User avatar
David LeBow
OutBack Management
Posts: 528
Joined: Sun May 03, 2015 10:42 am
Location: Bellingham, WA

Re: FX3048T Firmware update

Post by David LeBow » Tue Nov 28, 2017 12:04 pm

Could you tell me which link is broken (target link) and what page you found the link on?

Is this not what you're after? http://www.outbackpower.com/downloads/d ... manual.pdf

I'm 98.5% certain that the firmware is not field upgradeable. That said, I checked out your system in Optics and Optics seems quite happy with that inverter/firmware version - as if a firmware update weren't required.

Where are you seeing the warning message pop up? Could you post a screen shot (Optics) or picture? (Inverter, Mate3S)

Thanks.

David
David LeBow
Sr. Director, Software Engineering


Alpha Technologies Inc. / OutBack Power Technologies
3767 Alpha Way Bellingham WA 98226 USA
http://www.alpha.com

raysun
Forum Emperor
Posts: 1682
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower One: FX3048T, (2) FM80, MATE3s, FlexNetDC
Outback 200NC batteries (8 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: FX3048T Firmware update

Post by raysun » Tue Nov 28, 2017 1:13 pm

Hey David, thanks for the quick and inclusive response. The service manual attachment is appreciated.

I was having trouble downloading from http://www.outbackpower.com/products-mo ... ed-fx3048t, but it works now, so is a non-issue.

If the firmware on the FX3048T is not causing any issue with OpticsRE (as appears to be the case) then I will ignore the warnings. If I see one pop up again (I can't recall exactly where I saw it last) I will post - FYI.

I plan on purchasing another inverter for the system. We live way out in the sticks (actually on a lava field, so we have to import sticks) and am looking at the FXR3048A-01. Can I assume thus unit would be "plug compatible" in replacing the FX3048T in my Flexpower One installation? The existing inverter would be kept as a backup unit should we experience failure on the on-line unit.

R

User avatar
David LeBow
OutBack Management
Posts: 528
Joined: Sun May 03, 2015 10:42 am
Location: Bellingham, WA

Re: FX3048T Firmware update

Post by David LeBow » Tue Nov 28, 2017 1:17 pm

"Can I assume thus unit would be "plug compatible" in replacing the FX3048T in my Flexpower One installation?"

Whoops... now you've done it. You've fired over my head with that one. I'm just the resident software geek.

I'll forward it on to Tech Support. They'll have a better answer.

D.
David LeBow
Sr. Director, Software Engineering


Alpha Technologies Inc. / OutBack Power Technologies
3767 Alpha Way Bellingham WA 98226 USA
http://www.alpha.com

raysun
Forum Emperor
Posts: 1682
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower One: FX3048T, (2) FM80, MATE3s, FlexNetDC
Outback 200NC batteries (8 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: FX3048T Firmware update

Post by raysun » Tue Nov 28, 2017 1:18 pm

LOL! Thanks for that.

User avatar
Kurt Lundquist
Alpha Energy Engineering
Posts: 1447
Joined: Tue May 31, 2011 7:23 am
My RE system: VFX3524, Mate3, 200Ah 24V AGM Battery Bank
Location: Arlington, WA

Re: FX3048T Firmware update

Post by Kurt Lundquist » Tue Nov 28, 2017 1:35 pm

I'm not OutBack Tech Support but I can tell you the FX3048T has been replaced with the newer FXR3048A inverter. The two inverters are not compatible with each other.

Needless to say adding a second inverter for a FLEXpower ONE (FP1) is not for the faint of heart. The FP1 is a great power panel but it isn't very easy to expand. You will probably be better off selling the FP1 panel and then getting a new FLEXpower TWO (FP2) panel that already has 2 of the newer FXR model inverters installed or go with the FLEXpower Radian (FPR) system. The main benefit of the FPR would be if you have 2 AC sources like two different generators. If you have one (or less) AC sources then the FP2 is perfectly suitable.

Thanks,

-Kurt
Kurt Lundquist
Renewable Energy Project Engineer
http://alphaenergy.us/

sodamo
Forum Czar
Posts: 736
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Radians GG8048/GS4048 w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
12 SimpliPhi 3.8
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
10Kw MEP 803a Military gen

Honda EU7000i

Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

Re: FX3048T Firmware update

Post by sodamo » Tue Nov 28, 2017 7:02 pm

So are you asking about a one for one inverter replacement or adding a second inverter? I read as replacement, but could be wrong.
IÔÇÖm curious as to the answer as to replacement as I have an order system with 4 FX3048T inverters that I can see needing replacement in future and wonder if a direct swap out is doable or if I will have to upgrade to a Radian.
raysun wrote: I plan on purchasing another inverter for the system. We live way out in the sticks (actually on a lava field, so we have to import sticks) and am looking at the FXR3048A-01. Can I assume thus unit would be "plug compatible" in replacing the FX3048T in my Flexpower One installation? The existing inverter would be kept as a backup unit should we experience failure on the on-line unit.

R
David
Please visit http://vacation.ninolehawaii.com

raysun
Forum Emperor
Posts: 1682
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower One: FX3048T, (2) FM80, MATE3s, FlexNetDC
Outback 200NC batteries (8 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: FX3048T Firmware update

Post by raysun » Tue Nov 28, 2017 8:42 pm

I am looking to replace the FX3048T in my Flexpower One with an FXR3048A-1. I'll keep the FX3048T on the shelf as a spare should the installed inverter ever need to be taken off for service.

sodamo
Forum Czar
Posts: 736
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Radians GG8048/GS4048 w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
12 SimpliPhi 3.8
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
10Kw MEP 803a Military gen

Honda EU7000i

Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

Re: FX3048T Firmware update

Post by sodamo » Tue Nov 28, 2017 9:01 pm

Hopefully Kurt or someone from OB will return and answer from that perspective.

Where is your lava field?
David
Please visit http://vacation.ninolehawaii.com

raysun
Forum Emperor
Posts: 1682
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower One: FX3048T, (2) FM80, MATE3s, FlexNetDC
Outback 200NC batteries (8 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: FX3048T Firmware update

Post by raysun » Tue Nov 28, 2017 9:04 pm

Yes, I don't see an issue with the physical replacemebt, but I might not know where to look.

We abut HVNP at the Kahuku unit. Overlooking South Poibt.

sodamo
Forum Czar
Posts: 736
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Radians GG8048/GS4048 w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
12 SimpliPhi 3.8
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
10Kw MEP 803a Military gen

Honda EU7000i

Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

Re: FX3048T Firmware update

Post by sodamo » Tue Nov 28, 2017 9:13 pm

My thinking also. My are mounted in the older PS4. IÔÇÖve upgraded to FM80s from Mx60s, but also wonder how the environment is on the breakers and other components.

We are on the green side, between Hilo and Laupahoehoe.
David
Please visit http://vacation.ninolehawaii.com

User avatar
Kurt Lundquist
Alpha Energy Engineering
Posts: 1447
Joined: Tue May 31, 2011 7:23 am
My RE system: VFX3524, Mate3, 200Ah 24V AGM Battery Bank
Location: Arlington, WA

Re: FX3048T Firmware update

Post by Kurt Lundquist » Wed Nov 29, 2017 7:30 am

Hi raysun,

The FXR3048A-1 will fit in place of the FX3048T.

As far as I know the FXR3048A-1 model only works with the Mate3S controller. If you only have a Mate3 then you should plan on upgrading that as well.

The FLEXware AC and DC breaker boxes on the FP1 panel are extremely compact and screw into the top/bottom of the Inverter respectively. I've wired more than one of these panels from scratch and I can tell you it is a pain in the watt. You should plan on having a second set of hands around and it isn't a bad idea to take the whole panel off the wall first. I suggest you take pictures inside both breaker boxes before removing any wires so you have an example to reference. Finally double...no.. triple check your battery polarity with a multi-meter from the hot side of the 175A DC breaker to the Inverter negative battery terminal before turning on the 175A breaker.

See page 3 of this quick start guide for step by step instructions on how to commission the system. Remember you will need to reprogram the Inverter if you use it for charging with a generator.

http://outbackpower.com/downloads/docum ... qsg_na.pdf

Thanks,

-Kurt
Kurt Lundquist
Renewable Energy Project Engineer
http://alphaenergy.us/

raysun
Forum Emperor
Posts: 1682
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower One: FX3048T, (2) FM80, MATE3s, FlexNetDC
Outback 200NC batteries (8 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: FX3048T Firmware update

Post by raysun » Wed Nov 29, 2017 7:35 am

Thank you Kurt. It sounds like I'm in for a lot of fun. ;)

I have a Mate3s on my system now.

Rgds,
Ray