Postby Saggy on Mon Aug 14, 2017 6:14 am

Will one BTS sensor be sufficient for generator and mx 60 battery charging? I have a fx2524 with mate. Would BTS be connected to inverter or MX 60?
Saggy
Member
 
Posts: 8
Joined: Wed Aug 09, 2017 1:01 pm

Re: BTS sensor

Postby Mike Curran on Mon Aug 14, 2017 7:54 am

The manual for my GVFX's says "When a HUB is used, the RTS must be plugged into the master GFX which must be plugged into port 1 of the HUB. If this is the case, only one RTS is required for all devices plugged into the hub."

My translation: I would connect it to your inverter and make sure your inverter is plugged into port 1 of your Hub. You only need one (1) RTS (Remote Temperature Sensor) per system.

- Mike

Edit: Found this application note which may be helpful: http://outbackpower.com/downloads/docum ... p_note.pdf
Last edited by Mike Curran on Mon Aug 14, 2017 8:16 am, edited 1 time in total.
Mike Curran
OutBack Guru
 
Posts: 370
Joined: Sat Aug 28, 2004 6:28 pm
Location: Chagrin Falls, Ohio
My RE system: Outback:
- 8 (2x4) Evergreen 180's into one MX60
- 6 (2×3) ALEO S79-300's into one FM80
- 2 grid-tied GVFX3524's classic stacked for 120/240VAC
- 12 Surrette/Rolls 2V x 1766Ah
- Hub10.3, Mate3, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.

Westinghouse Solar:
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied.

Re: BTS sensor

Postby Saggy on Mon Aug 14, 2017 8:04 am

Thanks Mike,
Forgive my ignorance but is a mate considered a hub? My experience is with old Trace equipment from turn off the century.
Saggy
Member
 
Posts: 8
Joined: Wed Aug 09, 2017 1:01 pm

Re: BTS sensor

Postby jguzman on Mon Aug 14, 2017 8:21 am

Here's a quick video tutorial that talks about the RTS: https://youtu.be/O2rz4D_TQ_w

Your MX60 will need to be on a current firmware revision 5.11 is the latest. Once you have connected the RTS into the Master Inverter, you may check to see if the MX60 is also taking the data. From the home screen go to "Misc" then press "Next" twice. If the BT is other than 0 or 255 then it means it is reading it from the mater.

HUb: is a communications manager device that usually will allow 4 or 10 devices to connect.
Mate: is your remote controller/Display
Jorge Guzman
Technical Support Supervisor


Watch easy to follow video tutorials:
https://www.youtube.com/c/wattschool
jguzman
Applications Engineering
 
Posts: 151
Joined: Thu May 29, 2014 9:44 am
Location: Arlington, WA
My RE system: GVFX3524, FM80, MATE3. 3x 260W REC. 4x Trojan L16 FLA 370Ah.

Re: BTS sensor

Postby Mike Curran on Mon Aug 14, 2017 8:23 am

No, they are two different devices. A hub is like an ethernet switch, connecting various devices in your Outback system and allowing them to communicate with each other. Unfortunately you must use an Outback hub, a regular LAN switch will not work.

Sounds like you currently have a Mate, connected to your FX2524. If you're going to add an MX60 I strongly suggest you add a HUB so that charging is coordinated between your FX and MX. - Mike

PS Great video Jorge!
Mike Curran
OutBack Guru
 
Posts: 370
Joined: Sat Aug 28, 2004 6:28 pm
Location: Chagrin Falls, Ohio
My RE system: Outback:
- 8 (2x4) Evergreen 180's into one MX60
- 6 (2×3) ALEO S79-300's into one FM80
- 2 grid-tied GVFX3524's classic stacked for 120/240VAC
- 12 Surrette/Rolls 2V x 1766Ah
- Hub10.3, Mate3, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.

Westinghouse Solar:
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied.

Re: BTS sensor

Postby jguzman on Mon Aug 14, 2017 9:32 am

@Mike.

Thanks!
Jorge Guzman
Technical Support Supervisor


Watch easy to follow video tutorials:
https://www.youtube.com/c/wattschool
jguzman
Applications Engineering
 
Posts: 151
Joined: Thu May 29, 2014 9:44 am
Location: Arlington, WA
My RE system: GVFX3524, FM80, MATE3. 3x 260W REC. 4x Trojan L16 FLA 370Ah.

Re: BTS sensor

Postby Saggy on Mon Aug 14, 2017 6:01 pm

I think another BTS sensor is cheaper than a hub, I don't plan to have any remote monitoring. Thanks for the link.
Saggy
Member
 
Posts: 8
Joined: Wed Aug 09, 2017 1:01 pm

Re: BTS sensor

Postby blackswan555 on Mon Aug 14, 2017 10:53 pm

think another BTS sensor is cheaper than a hub,
I will second that, No point in spending 10 times as much money,,,, If you did the data you would get from MX would be limited anyway, Get another temp sensor and put it by the side of the FX one (about half way down what will be warmest cell)

Tim
My comments are based on my experience and research, They are not endorsed or checked by Outback.I am an independent British electrician living in Spain, So please take this into account when reading /acting on my post`s.
blackswan555
OutBack Emperor
 
Posts: 2536
Joined: Sat Aug 30, 2008 5:50 am
Location: Ibiza Spain,
My RE system: Other peoples, VFX "E" versions, FLA`s, Generators.


Return to MX60 Charge Controller

Who is online

Users browsing this forum: No registered users and 3 guests