MX 60 will not run absorb cycle

Discussion about the MX60 Charge Controller

Moderators: OutBack Moderator Team, OutBack

MX 60 will not run absorb cycle

Postby freewilley on Mon Jul 31, 2017 9:25 am

I have an MX and an FM 60.
I have long been suffering because the MX goes to Float or Bat Full when the batteries are not nearly 80%.

Yesterday I installed 2 brand new S550s and the MX went to Float while the FM ran as expected.
I cannot get the MX to run absorb.

I have been over the settings and cannot see any issue and asked for advice on the Northern AZ forum, no answer yet.

I wonder if the MX needs replacement or there is a fix.

Also, anyone have a technique for running absorb with the FM and stopping the MX from screwing that up...

thanks!
freewilley
Junior Member
 
Posts: 3
Joined: Thu Sep 22, 2016 1:58 pm
My RE system: fm 60 and mx 60 2512 inverter, mate, 1400 watts panels, 4 s 550 surette battery bank

Re: MX 60 will not run absorb cycle

Postby petertearai on Mon Jul 31, 2017 7:00 pm

wind sun is a good choice . Have you tried the mx without the fm . Maybe need to set up the fine voltage adjustment for each one . Maybe raise the absorb voltage for the mx a few points at a time and see if the 2 stay more in sync ?
2220 pv. fm80. 4times rolls 450 ah 24 volts. victron battery monitor. outback fxr 2000 watt inverter
petertearai
OutBack Guru
 
Posts: 322
Joined: Fri Aug 06, 2010 4:35 pm
Location: NewZealand North Island
My RE system: 2220 watt pv, fm80, outback fxr 2000 watt inverter. Rolls s600 times 4 24 volt system victron battery moniter. optics RE


Return to MX60 Charge Controller