Northeast USA -- roof-mount or put in attic?

Post by jazzer » Sat Jun 23, 2007 9:12 am

I live in NH (43┬░N latitude) where we get a lot of snow. I was planning to vertically mount the PSPV box to a pipe (existing roof penetration). The roof is 6.5:12 so it could be mounted directly to the roof but I was concerned about snow accumulation so I opted for the vertical mount. Naturally I plan to use only USE-2 intermodule wiring.

The thought has crossed my mind to mount the box in my attic, just on the other side of the roof penetration. Of course it would be easier to access and I wouldn't have to worry about snow, but in the summer it would be exposed to higher temperatures. There are 6 strings of 48V-nominal wired panels, so that's more wiring to bring inside too, rather than just the PSPV output. Then again I don't know what NEC has to say about this. I'm no expert on NEC code either -- I'm learning as I go.

I was just wondering what you experts think about these options or if you have some alternate suggestions.

User avatar
crewzer
Forum Emperor
Posts: 1927
Joined: Mon Sep 27, 2004 10:50 am
Location: Vienna, VA

Post by crewzer » Sat Jun 23, 2007 2:10 pm

Jazzer,

IÔÇÖm not an NEC expert by any means. So my comments may need confirmation.

NEC 690.14 says that a photovoltaic disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest to the point of entrance of the system conductors. The photovoltaic disconnecting means shall not be installed in bathrooms. IÔÇÖd wonder if your inspector would consider the attic to be a ÔÇ£readily accessible locationÔÇØ.

On a separate but related note, you may want to take a look at NEC 690.5, which addresses the requirement for ground fault protection for arrayÔÇÖs mounted on a dwelling.

You may John Wiles' articles on PV installations and the NEC to be helpful. See: http://www.nmsu.edu/%7Etdi/Photovoltaic ... -Stds.html Additionally, this guide might be useful: http://www2.fsec.ucf.edu/en/education/c ... or_NEC.pdf

HTH,
Jim / crewzer
090805 System Configuration: 966 W STC (849 W CEC PTC) 48V PV array, FM80, 24V x 400 Ah AGM battery bank, FX2524T w/ BTS, Hub-4 & Mate; Link-10 w/ BTS, & E-Panel.

sparky
Forum Emperor
Posts: 1216
Joined: Fri May 20, 2005 8:24 am
My RE system: OFFGRID SOLAR "we go where power lines don't" Design, consulting, and installation advice on 300+ Offgrid homes.
Location: Sierra Mountains near Mariposa Ca. Webpage on next line
Contact:

Post by sparky » Sun Jun 24, 2007 6:14 am

Yea, what Jim said and ask your building department. They will be the ones who inspect it! If they are good they will know but if they are not you will have "show" them the way. Put a thermometer up there and get some data now that we just past the Solstice.

I tend to think that it is not the way to go but.........

Martin
Forum Guru
Posts: 240
Joined: Tue Dec 13, 2005 3:16 pm
Location: Somewhere in the hills above Silicon Valley

Post by Martin » Sun Jun 24, 2007 8:42 am

Definitely talk to your building department as Sparky says. The definition of 'readily accessible' usually means that the box has to be mounted in a location where there is a seven foot clearance floor to ceiling, and there are no obstructions for three feet in front of it. The clearance floor-to-ceiling has to be maintained to three feet from the box, too. The intent is that someone who is servicing the panel should be able to easily stand right in front of it.

I got dinged on that one because I mounted my PSPV on an array pole. They ended up letting me leave it there after I appealed for a variance, but I would have done it differently had I thought it through in the beginning.
Quad-stack GVFX3648, 6.4 kW Solar, 1 kW continuous hydro, 1690 amp-hour 48v Solar-One battery bank.

halfcrazy
Forum Guru
Posts: 410
Joined: Fri Apr 30, 2004 11:01 pm
Location: corinna, maine

Post by halfcrazy » Sun Jun 24, 2007 3:23 pm

my understanding of the code is that the combiner can be considered just that and not a disconnect so it can go on the roof or what ever but if you do that the pv wiring has to be in rigid metallic conduit till it gets to the disconnecting means witch has to be readily accessible.