Equalization on 525FLA batteries

Discussion about the OutBack Energy Cell Batteries

Equalization on 525FLA batteries

Postby ramiryx on Thu Aug 17, 2017 12:29 pm

I bought 4 batteries 525FLA and connected in series for a 24V battery system.

In the battery datasheet it show the equalization voltage, but do not mention about the duration and/or the frequency of this procedure.

Please help
ramiryx
Forum Junior Member
 
Posts: 1
Joined: Thu Aug 17, 2017 12:23 pm
My RE system: FM80, PV array of 6 310W panel, 2000W inverter

Re: Equalization on 525FLA batteries

Postby salvadortorres on Tue Feb 06, 2018 9:50 pm

okay.will help you. Batteries designed for residential or light-commercial off-grid renewable energy power demands.It has a heavy-duty internal connectors and terminal post structures enable unmatched electrical efficiency and durability.Equalizing lead acid batteries is a process designed to de-sulphate the battery plates by carrying out a controlled overcharge.For more refer on web please.
For academic works refer here
salvadortorres
Forum Junior Member
 
Posts: 1
Joined: Tue Feb 06, 2018 9:04 pm

Re: Equalization on 525FLA batteries

Postby SandyP on Wed Feb 07, 2018 2:50 am

ramiryx wrote:..." the duration and/or the frequency of this procedure."

Please help


Not sure about the duration for your model batteries however regarding the frequency, equalisation "charges" need to be done when the SGs (specific gravity readings) of your individual battery cells start to diverge from each other ( generally some lower than normal), this can generally be as a result of incomplete charging cycles and/or too short an absorb charge period.
So, check your SGs regularly and take note of each cells readings in a written log, when things start changing ie SGs of one or more cells remain low then you can look to do an equalisation charge.
SandyP
Forum Guru
 
Posts: 253
Joined: Tue Jun 21, 2011 4:44 am
Location: Victoria, Australia
My RE system: 8 x 190W 24V Suntech panels (4 strings of 2)
Mate2
Outback FM60 MPPT
12 x 2V Hoppecke GEL 660 Ah C100 - 24V System
Outback VFX3024 Inverter/Charger
Victron BMV-602s
Honda 5.5kW Genset

Re: Equalization on 525FLA batteries

Postby Mike Curran on Wed Feb 07, 2018 7:20 am

Here's an excerpt from the Rolls battery manual describing the EQ process:
Screenshot_20180207-091549.jpg

The duration will depend on how long it takes for all your batteries' electrolyte to reach 1.265g/cc specific gravity.
Mike Curran
Forum Guru
 
Posts: 463
Joined: Sat Aug 28, 2004 6:28 pm
Location: Chagrin Falls, Ohio
My RE system: Outback:
- 8 (2x4) Evergreen 180's into one MX60
- 6 (2×3) ALEO S79-300's into one FM80
- 2 grid-tied GVFX3524's classic stacked for 120/240VAC
- 12 Surrette/Rolls 2V x 1766Ah
- Hub10.3, Mate3, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.

Westinghouse Solar:
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied.


Return to OutBack Energy Cell Batteries

Who is online

Users browsing this forum: No registered users and 1 guest