My RE system: FM80, PV array of 6 310W panel, 2000W inverter

Equalization on 525FLA batteries

Post by ramiryx » Thu Aug 17, 2017 12:29 pm

I bought 4 batteries 525FLA and connected in series for a 24V battery system.

In the battery datasheet it show the equalization voltage, but do not mention about the duration and/or the frequency of this procedure.

Please help

salvadortorres
Forum Junior Member
Posts: 1
Joined: Tue Feb 06, 2018 9:04 pm

Re: Equalization on 525FLA batteries

Post by salvadortorres » Tue Feb 06, 2018 9:50 pm

okay.will help you. Batteries designed for residential or light-commercial off-grid renewable energy power demands.It has a heavy-duty internal connectors and terminal post structures enable unmatched electrical efficiency and durability.Equalizing lead acid batteries is a process designed to de-sulphate the battery plates by carrying out a controlled overcharge.For more refer on web please.
For academic works refer here

SandyP
Forum Guru
Posts: 321
Joined: Tue Jun 21, 2011 4:44 am
My RE system: 8 x 190W 24V Suntech panels (4 strings of 2)
4 x 325W 24V Suntech panels (2 strings of 2) added Sept2018
Mate2
Outback FM60 MPPT (max output lowered to 55amps)
12 x 2V Hoppecke GEL 660 Ah C100 - 24V System
Outback VFX3024 Inverter/Charger
Victron BMV-602s
Honda 5.5kW Genset
Location: Victoria, Australia

Re: Equalization on 525FLA batteries

Post by SandyP » Wed Feb 07, 2018 2:50 am

ramiryx wrote:..." the duration and/or the frequency of this procedure."

Please help
Not sure about the duration for your model batteries however regarding the frequency, equalisation "charges" need to be done when the SGs (specific gravity readings) of your individual battery cells start to diverge from each other ( generally some lower than normal), this can generally be as a result of incomplete charging cycles and/or too short an absorb charge period.
So, check your SGs regularly and take note of each cells readings in a written log, when things start changing ie SGs of one or more cells remain low then you can look to do an equalisation charge.

Mike Curran
Forum Emperor
Posts: 1217
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one MX60 (2007)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied GVFX3524's classic stacked for 120/240VAC (2007)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied.

Outback Skybox - Barn roof: (2019)
- 14 (2x7) Talesun 275W
- 2 SimpliPhi 3.8 batteries, 48V, 150Ah total
- future AC coupled input from both rows of Westinghouse AC modules*
- future AC coupled input from 14 Talesun 275W, Enphase M215 modules*
* waiting for firmware update from OB

All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: Equalization on 525FLA batteries

Post by Mike Curran » Wed Feb 07, 2018 7:20 am

Here's an excerpt from the Rolls battery manual describing the EQ process:
Screenshot_20180207-091549.jpg
The duration will depend on how long it takes for all your batteries' electrolyte to reach 1.265g/cc specific gravity.
http://www.tigoenergy.com/site.php?95b2dca2-ca6c