Outback RE200's DEAD

Discussion about the OutBack Energy Cell Batteries
Post Reply
mrobinson
Forum Junior Member
Posts: 3
Joined: Sun Dec 11, 2016 12:04 pm
My RE system: Radian 8048 - AC Coupled - GS LOAD 175-AC-120/240, 48V IBR 8 - Enphase 5.6kw

Outback RE200's DEAD

Post by mrobinson » Wed Nov 21, 2018 5:10 pm

Hello,

I have a AC coupled system, Radian8048A (48v) with 8 batteries connected in an IBR. We have never had a power outage in our area since installed. I've checked them periodically for SOC and they have always been fine.

This afternoon I noticed my Mate3 was off, went to check it out and the batteries were at 11V.

I have no idea how this happened, more bad luck. There was no data logging going on.

Thoughts on how to get these batteries charged back up?

Mike

SandyP
Forum Guru
Posts: 321
Joined: Tue Jun 21, 2011 4:44 am
My RE system: 8 x 190W 24V Suntech panels (4 strings of 2)
4 x 325W 24V Suntech panels (2 strings of 2) added Sept2018
Mate2
Outback FM60 MPPT (max output lowered to 55amps)
12 x 2V Hoppecke GEL 660 Ah C100 - 24V System
Outback VFX3024 Inverter/Charger
Victron BMV-602s
Honda 5.5kW Genset
Location: Victoria, Australia

Re: Outback RE200's DEAD

Post by SandyP » Wed Nov 21, 2018 5:55 pm

mrobinson wrote:... I've checked them periodically for SOC and they have always been fine.
How did you check the batteries?
SOC is an only an estimate of the charge level and if based off the FNDC can be wrong.

mrobinson
Forum Junior Member
Posts: 3
Joined: Sun Dec 11, 2016 12:04 pm
My RE system: Radian 8048 - AC Coupled - GS LOAD 175-AC-120/240, 48V IBR 8 - Enphase 5.6kw

Re: Outback RE200's DEAD

Post by mrobinson » Wed Nov 21, 2018 6:00 pm

Multimeter

SandyP
Forum Guru
Posts: 321
Joined: Tue Jun 21, 2011 4:44 am
My RE system: 8 x 190W 24V Suntech panels (4 strings of 2)
4 x 325W 24V Suntech panels (2 strings of 2) added Sept2018
Mate2
Outback FM60 MPPT (max output lowered to 55amps)
12 x 2V Hoppecke GEL 660 Ah C100 - 24V System
Outback VFX3024 Inverter/Charger
Victron BMV-602s
Honda 5.5kW Genset
Location: Victoria, Australia

Re: Outback RE200's DEAD

Post by SandyP » Thu Nov 22, 2018 4:39 am

mrobinson wrote:Multimeter
Unfortunately a multimeter will not be accurate but may give you a guide if you isolate the battery bank and allow it to "rest" for at least 12 hours.

Regards getting the batteries charged up, I hope someone else can provide you with some input as I am sure it has been mentioned in other topics. I can only recommend getting a suitable external charger or somehow getting the solar charge controller (FM80) to power up by getting more than 10V to its battery/output terminals then "the LCD should be on, and once solar is available it should start it normal wake-up."?