Power Fluxuation with generator

Post by wpmaura » Thu Oct 15, 2020 5:30 pm

I run a generator for an hour at night to assist batteries or rain etc. But when I cut it.off there seems to be a dip in power. Should that be seemless?

raysun
Forum Emperor
Posts: 2998
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: Power Fluxuation with generator

Post by raysun » Thu Oct 15, 2020 6:22 pm

It depends on the manner of cutoff, perhaps.

Is the generator simply being powered down, or is the AC IN being DROPPED first?

wpmaura
Forum Whiz
Posts: 45
Joined: Wed Feb 19, 2020 1:25 pm
My RE system: flex power one 3kw. 16 x 6v 415ah Rolls, 15x 270watt 30V 9amp panels

Re: Power Fluxuation with generator

Post by wpmaura » Fri Oct 16, 2020 4:07 am

I just cut the generator off its a 6kw pull cord

wpmaura
Forum Whiz
Posts: 45
Joined: Wed Feb 19, 2020 1:25 pm
My RE system: flex power one 3kw. 16 x 6v 415ah Rolls, 15x 270watt 30V 9amp panels

Re: Power Fluxuation with generator

Post by wpmaura » Fri Oct 16, 2020 4:07 am

is there a way of dropping it from mate

raysun
Forum Emperor
Posts: 2998
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: Power Fluxuation with generator

Post by raysun » Fri Oct 16, 2020 8:02 am

The Mate3/3s has a hard button labeled AC INPUT.

It has a menu that will allow input DROP and USE.

provo
Forum Czar
Posts: 531
Joined: Thu Jul 27, 2006 4:34 pm
My RE system: Sixteen Evergreen EC-120
(4 strings, total 1920W)
Eight Rolls S-550 (2 strings, total ~800Ah @ 24V)
One FM80
One VFXR3524A
Hub 10
Mate3s
FNDC and Trimetric
Location: Sierra foothills

Re: Power Fluxuation with generator

Post by provo » Fri Oct 16, 2020 8:46 am

raysun wrote:
Fri Oct 16, 2020 8:02 am

It has a menu that will allow input DROP and USE.
DROP doesn't turn off generator, though. AGS does.

raysun
Forum Emperor
Posts: 2998
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: Power Fluxuation with generator

Post by raysun » Fri Oct 16, 2020 10:57 am

But its a manual start generator.

The smoothest manual transition is to DROP the AC INPUT, then power down the generator.

AGS will do it all programmatically, but requires an AGS compatible generator.

wpmaura
Forum Whiz
Posts: 45
Joined: Wed Feb 19, 2020 1:25 pm
My RE system: flex power one 3kw. 16 x 6v 415ah Rolls, 15x 270watt 30V 9amp panels

Re: Power Fluxuation with generator

Post by wpmaura » Sun Oct 18, 2020 5:11 pm

That did the trick. Thanks