adding a FM60 to an FP1

A place where users can meetup with other FlexPower One users and can find support for one another. A great place for people who have not purchased the FlexPower One yet to look up information.

adding a FM60 to an FP1

Postby Ryan on Wed Dec 04, 2013 12:41 pm

We are going to be installing a FP1 with the VFX3648 inverter, FM80 charge controller. We have 21 Grape solar 250w panels.... only 15 can go on the FM80 so we are adding an additional FM60 for the other 6 panels. They will be charging 12 -200AH batteries.

What changes to to FP1 do I need to make for the addition of the extra charge controller?

Thanks for the help
Ryan
Member
 
Posts: 6
Joined: Wed Dec 04, 2013 9:12 am

Re: adding a FM60 to an FP1

Postby dhamilton on Tue Dec 10, 2013 11:40 am

You will need to add an additional PV breaker and switch from the single GFDI to the dual GFDI.
dhamilton
OutBack Technical Service
 
Posts: 59
Joined: Tue Sep 13, 2011 9:42 am
My RE system: 2x VFXR3524A, FLEXmax80, 6x EnergyCell 106NC, Mate3

Re: adding a FM60 to an FP1

Postby Ryan on Wed Dec 11, 2013 12:17 pm

Thanks,

I will post some pictures after it is installed
Ryan
Member
 
Posts: 6
Joined: Wed Dec 04, 2013 9:12 am

Re: adding a FM60 to an FP1

Postby Ryan on Tue Jul 29, 2014 9:25 am

Here is the finished (to this point) installation.
Image
Image
Image

I say "to this point" because the client called today and wants to extend the battery bank. We will be adding an additional cabinet and 12 more batteries shortly. It has been working flawlessly since we put it in.
Ryan
Member
 
Posts: 6
Joined: Wed Dec 04, 2013 9:12 am

Re: adding a FM60 to an FP1

Postby csteel on Sat Dec 20, 2014 6:22 pm

Nice install, when adding 2nd charge controller is it not necessary to change settings so both work together without conflict?
csteel
Member
 
Posts: 19
Joined: Fri Jun 29, 2012 9:27 am
My RE system: Two separate systems one has 8 x Trojan T105, one has 16 x Trojan T105 otherwise both are FlexPower One 36/48 Flex max 80 15x235 Shott panels

Re: adding a FM60 to an FP1

Postby solar17 on Tue Feb 14, 2017 10:51 am

We would like to do a similar upgrade - add a FM80 charge controller to our FlexPower One - but I believe on a call with Outback Tech Support they said the MATE can't read another device and the display wouldn't be accurate - ? Is someone able to please clarify how we can overcome this?

Also - is someone able to detail further the change out from single to dual GFDI? Many thanks!
solar17
Junior Member
 
Posts: 2
Joined: Fri Feb 03, 2017 10:57 am
My RE system: FlexPower One (w/ VFX3524 and FM80)
1600W solar
24V battery bank, 600Ah

Re: adding a FM60 to an FP1

Postby Mike Curran on Tue Feb 14, 2017 6:39 pm

On page 6 of the Mate user manual (Rev A copyright 2007) it says "a single Outback Mate can ...link to as many as ten FX series inverter/chargers, OutBack charge controllers (my emphasis) and additional future Outback Power System products". I believe it handles extra CC's the same way as multiple FX's, through port assignments.

As far as dual GFDI, the one I installed in 2007 already has an extra breaker ganged for dual use (see schematic photo). If you're lucky yours may too.

20170214_203416.jpg
Mike Curran
OutBack Guru
 
Posts: 196
Joined: Sat Aug 28, 2004 6:28 pm
Location: Chagrin Falls, Ohio
My RE system: Outback: 8 (2x4) Evergreen 180's into one MX60, 6 (2×3) ALEO S79-300's into one FM80, 2 grid-tied GVFX3524's classic stacked for 120/240VAC, 12 Surrette/Rolls 2V x 1766Ah, Hub10.3, Mate3, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.

Westinghouse Solar: 30 (2x15) 235W panels with Enphase M215 microinverters. 6,450 nameplate watts AC, grid-tied.