need dual battery cables if I only have 1 string?

Dual Input, 120/240, stainless steel form factor design for unsurpassed surge capability
Post Reply
User avatar
Megunticook
Forum Guru
Posts: 242
Joined: Fri Sep 29, 2017 4:08 am
My RE system: 6.4 kW solar array (21 QCell 305 panels in strings of 3)
GS8048A FLEXpower Radian (Radian 8048A, 2 FlexMax 80 cc's, Mate 3s, FlexNet DC, Hub)
8x6v Rolls-Surette 550 FLA batteries, 428AH
Location: Maine
Contact:

need dual battery cables if I only have 1 string?

Post by Megunticook » Thu Nov 30, 2017 11:49 am

Just finishing up wiring my FPR-8048A. The manual calls for dual 00 AWG cables from the battery bank to the inverter. A guy I spoke with on the phone at Outback says since I only have one bank of batteries (8 6v Rolls S-550, 428 AH), I'm fine with just one pair of cables. Can anyone please confirm that this is correct? The documentation is pretty clear about needing two pairs, but the rep. I spoke to says that assumes you have 2 strings of batteries in parallel.

Thanks.
https://sunnypower.org

User avatar
Kurt Lundquist
Alpha Energy Engineering
Posts: 1447
Joined: Tue May 31, 2011 7:23 am
My RE system: VFX3524, Mate3, 200Ah 24V AGM Battery Bank
Location: Arlington, WA

Re: need dual battery cables if I only have 1 string?

Post by Kurt Lundquist » Thu Nov 30, 2017 12:13 pm

The FPR-8048A has 2 x 175A breakers. That means you need a conductor that can continuously support 350A of current. Also voltage drop is a consideration if you have a long wire run from the batteries to the inverter. Off the top of my head I think the OutBack recommendation of 2 x 2/0 is for about a 10' or less run. At less than 10' a single 4/0 conductor in free air should be able to get the job done however you should make sure that whatever conductor size you use is acceptable per local codes. If the S-550 has an LT style terminal maybe you can double lug on it (one lug on each side of the terminal). I'd consult with Rolls to make sure that is acceptable.

-Kurt
Kurt Lundquist
Renewable Energy Project Engineer
http://alphaenergy.us/

User avatar
Megunticook
Forum Guru
Posts: 242
Joined: Fri Sep 29, 2017 4:08 am
My RE system: 6.4 kW solar array (21 QCell 305 panels in strings of 3)
GS8048A FLEXpower Radian (Radian 8048A, 2 FlexMax 80 cc's, Mate 3s, FlexNet DC, Hub)
8x6v Rolls-Surette 550 FLA batteries, 428AH
Location: Maine
Contact:

Re: need dual battery cables if I only have 1 string?

Post by Megunticook » Thu Nov 30, 2017 8:06 pm

So what the Outback rep. told me on the phone is wrong? I need to double up on those battery cables then? And I need to double up on the short cables connecting the batteries together in series as well? Plus a second fuse block? (I was going to install a 200amp class T fuse on the positive cable).

This does not reassure me about the quality of Outback tech. support if they told me the wrong thing here.

The cables are 8' long and run in 2" metal conduit from the battery box to the inverter. I sure hope I don't have to install a second run of conduit!
https://sunnypower.org

blackswan555
Forum Emperor
Posts: 2637
Joined: Sat Aug 30, 2008 5:50 am
My RE system: Other peoples, VFX "E" versions, FLA`s, Generators.
Location: Ibiza Spain,

Re: need dual battery cables if I only have 1 string?

Post by blackswan555 » Thu Nov 30, 2017 10:15 pm

Sorry to throw a spanner in the works but I would go a different route,
single 000 cable & a 250amp fuse/breaker on the battery end & link across breakers inverter end,
Why ?
The inverter is 8000/48 = 166 amps continuous and a reasonably easily obtainable surge of 12000/48= 250amps which the fuse should handle, The cable is rated just above so the fuse would protect that in the event of eg a dead short inverter end, The other benefit of going up a size would be less voltage drop,

Tim,
To add, I know you are not intending to use that much power with your size batteries, But it is possible so you have to size for it :smile: In the event of a dead short they could deliver into the 10s of thousands of amps, Thats what the fuse looks after,
My comments are based on my experience and research, They are not endorsed or checked by Outback.I am an independent British electrician living in Spain, So please take this into account when reading /acting on my post`s.

Kent Osterberg
Forum Emperor
Posts: 1523
Joined: Mon Jun 09, 2003 11:01 pm
My RE system: SMA Sunny Boy 2500 with eight Mobil Solar Ra 180 modules
Location: Cove, Oregon
Contact:

Re: need dual battery cables if I only have 1 string?

Post by Kent Osterberg » Fri Dec 01, 2017 3:01 pm

Outback recommends the doubled 2/0 cable because it has lower resistance and inductance than single 4/0 cable.

Four 2/0 cables will physically fit in 2" conduit within the allowed 40% fill, but passing the cable lugs through the 2" conduit will be a challenge. Unfortunately, four cables in conduit only carry 80% of the current in NEC table 310.15(B)(16), so four 2/0 cables in conduit only have an an ampacity of 140 amps (for 75┬░C rated wire) or 156 amps (for 90┬░C rated wire). However, 140 amps is sufficient ampacity to run the inverter to its maximum surge rating: 2 x 140A x 48V x 90% efficiency = 13 kW. Since the inverters can't sustain that amount of power, the cables cannot be overloaded and the 175-amp breakers still provide fault protection if the inverter fails. For 90┬░C rated wire, this arrangement complies with the NEC rules on breaker selection because the next available breaker size above 156 amps is the 175 amp breaker.

User avatar
Megunticook
Forum Guru
Posts: 242
Joined: Fri Sep 29, 2017 4:08 am
My RE system: 6.4 kW solar array (21 QCell 305 panels in strings of 3)
GS8048A FLEXpower Radian (Radian 8048A, 2 FlexMax 80 cc's, Mate 3s, FlexNet DC, Hub)
8x6v Rolls-Surette 550 FLA batteries, 428AH
Location: Maine
Contact:

Re: need dual battery cables if I only have 1 string?

Post by Megunticook » Thu Dec 07, 2017 6:14 pm

I was able to pull the 4 cables through the 2" EMT without much trouble--did a careful job taping them tightly together and pre-lubed the conduit before the pull. Pretty short run with just one 90 degree elbow.

Thanks for the advice, everyone. Cables are rated for 105┬░C incidentally, so I should be all set.

CEO came by this morning and the inspection went well--looks like we're good to go. I just need to hook up the batteries, program the MATE3, and we can start cranking out the watts!
https://sunnypower.org