klundquist wrote:Unless you lose grid power frequently I wouldn't bother with AC coupling the GT inverters to the OutBack system. My 2 cents.
-Kurt
Kurt, here we are about 5 months later, and I've just ordered an ROCB kit to complete the A/C Coupling. As it turns out, running a hybrid system, and a grid tie system, on the same feed, is not viable.
Over the last 3 or 4 months that I've been running both, side by side, I've lost about 1000kWh of potential generation because the inverters get into a pissing match.
In order to sell, the inverters will push amperage at a slightly higher voltage than the current grid voltage. Well, when you have two systems tied to the same feed in close proximity, you end up with each system raising the voltage until one, or both, drop out due to high grid voltage. With the two separate systems running, I regularly hit 264V and have even managed to see over 280V when messing with settings to diagnose this.
So.... No, you can't do it. At least, not if both systems are connected to the feed in close proximity.
When my ROCB kit shows up, I'll correct this issue, then move on to the next phase of testing. I'm about to roof a new pole building that will then get 20 more panels. When I set that up, I'm going to run a direct grid tie inverter to the feed, but I'm going to do it over about 175ft of line, versus a literal side by side connection that I have been running. The assumption is that over that distance, it allows the loads to draw down the voltage. No idea of that theory is good, but will find out soon enough.
So, anyway, that brings me back to the other two original questions in my first post on this thread, neither of which, anyone has addressed thus far.
Question 2. As I have 2 Radians, can I feed each with a 6kw GT inverter?
Question 3. (unrelated) Can I run GS8048 and GS8048a inverters together? (almost ready to add a couple more to what I already have)