AC relay fault, Did OB add more relays?

Dual Input, 120/240, stainless steel form factor design for unsurpassed surge capability

AC relay fault, Did OB add more relays?

Postby kees.barendse on Wed Jan 11, 2017 11:38 pm

We have been having issues with intermittent AC relay faults on our three GS7048E Radian inverters. We have already replaced two relay boards where the relays burnt out when running the inverters at or close to the maximum 40 Amps output current, mostly due to run in currents of our machines like belt sanders and the like. Because we run out inverters in a three phase setup an AC relay fault on one of the inverters will cause the whole system to kick itself offline.

Our current AC relay boards have two relays, one for grid input and one for generator input. I noticed in an Outback instruction document which describes Radian board replacement procedures that currently Outback is delivering Radians with four relays! If that is the case, wouldn't it be nice if OB gave some kind of warranty on what appears to be a deficient design which has since been upgraded and improved upon..... ?

Here are the images that show the difference.

https://drive.google.com/file/d/0B_Wi1k ... sp=sharing
https://drive.google.com/file/d/0B_Wi1k ... sp=sharing

Regards,

Kees Barendse
kees.barendse
Member
 
Posts: 14
Joined: Mon May 02, 2011 11:04 am

Re: AC relay fault, Did OB add more relays?

Postby Sandra Herrera on Thu Jan 12, 2017 9:43 am

Kees,
These are the two differences between 7048E and the North America model 8048.
In North America we have two phases L1 and L2, this is why you see 4 relays in the North America models and only 2 relays for the E models.
The relays for both models have a maximum current rating, and this must be consider during the design of the system.
Sandra Herrera
Applications Engineering


OutBack Power Technologies
User avatar
Sandra Herrera
OutBack Management
 
Posts: 139
Joined: Wed Jul 08, 2015 8:54 am
Location: Arlington, Washington

Re: AC relay fault, Did OB add more relays?

Postby kees.barendse on Thu Jan 12, 2017 10:07 am

Dear Sandra,

Many thanks for the quick reply and the good explanation! I think you folk know better than I do whether other users of the 7048 inverters have issues with bad AC relays. Having had a closer look at those relays I would say that they seem a bit flimsy for the loads they are supposed to carry.

Let me find a way to change out this board one more time and confirm that we have the right output breakers now.

Regards,

Kees
kees.barendse
Member
 
Posts: 14
Joined: Mon May 02, 2011 11:04 am

Re: AC relay fault, Did OB add more relays?

Postby blackswan555 on Thu Jan 12, 2017 10:15 am

Not my game but a thought or two, Are you using a powersave of any description ? usually if inrush current is high but the relay is already closed, not a problem ,

Tim
My comments are based on my experience and research, They are not endorsed or checked by Outback.I am an independent British electrician living in Spain, So please take this into account when reading /acting on my post`s.