AC Backfeed Error

Post by eesiason » Fri Jun 19, 2020 1:14 pm

System installed in 2012 and running perfectly for 8 years. 17kWh solar and two GS8048s. Got this error today "AC Backfeed Error GS2". We are off grid and the AC is running, along with an electric dryer at the time. Perhaps 8,000 watt load. Had the wet clothes moved to the gas dryer. What does this error mean and what should I be looking at?

fcwlp
Forum Czar
Posts: 533
Joined: Wed Jan 22, 2020 9:40 am
My RE system: GS8048A, FM80 w/3,600 W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed
I also install and maintain grid-tied and off-grid systems, details will be given for these system if required
Location: 80 miles NE of Phoenix at 5500'

Re: AC Backfeed Error

Post by fcwlp » Fri Jun 19, 2020 8:10 pm

Generally an "AC Backfeed Error" indicates that an AC source that is out of phase with the inverter was connected to the AC Output of the inverter. Given your 2012 install date, you likely have the GS8048 and not the newer GS8048A. For the GS8048A, errors are described on pp. 51-55 of the Radian Operator's Manual. Several errors related to "AC Backfeed" are caused by stacking issues.

As your error includes a "GS2", most likely there is an "out of phase AC back feed" into the slave inverter. Since your only other AC source is the master inverter it makes debugging interesting. The manual recommends disconnecting the output wires of the inverter with the error and measuring them to see if there is an external voltage source. With a stacked system this is not feasible as the output of the master inverter is paralleled with the output of the slave inverter(s). If you have an oscilloscope you could check if the output of the master and slave are in or out of phase. You could possibly due with a VM but that is beyond the scope of a forum posting.

If there were no physical alterations to the system, verify that both systems are not defined as masters.

eesiason
Forum Whiz
Posts: 48
Joined: Fri Oct 12, 2012 9:40 am
My RE system: Off-Grid 48ea Sunmodule SW240, sunmodule 240W Modules, 18 SolarWorld 290W modules, 2ea Radian 8000W GS8048 48V 120/240VAC Inverter, 4ea Flexmax 80, MATE 3s, Hub 10, 2kw Wind, two 15kw ecogen on a manual bypass. Everything is redundant.
Location: 648 Southbridge Rd., Warren MA
Contact:

Re: AC Backfeed Error

Post by eesiason » Sat Jun 20, 2020 3:38 am

You are correct. 8048s.

I went through all settings this morning and everything seems configured correctly, with one exception. The AC output on the master was rightly configured to 240, but the slave was set to 260. I don't know if it has been like this since 2012 or something changed it recently. I set it to 240. Not sure if this would cause the issue or not.

fcwlp
Forum Czar
Posts: 533
Joined: Wed Jan 22, 2020 9:40 am
My RE system: GS8048A, FM80 w/3,600 W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed
I also install and maintain grid-tied and off-grid systems, details will be given for these system if required
Location: 80 miles NE of Phoenix at 5500'

Re: AC Backfeed Error

Post by fcwlp » Sat Jun 20, 2020 6:12 am

eesiason wrote:
Sat Jun 20, 2020 3:38 am
I went through all settings this morning and everything seems configured correctly, with one exception. The AC output on the master was rightly configured to 240, but the slave was set to 260. I don't know if it has been like this since 2012 or something changed it recently. I set it to 240. Not sure if this would cause the issue or not.
I do not know if that would cause the backfeed error. Let us know what happens after you load the system to 8+kW.

eesiason
Forum Whiz
Posts: 48
Joined: Fri Oct 12, 2012 9:40 am
My RE system: Off-Grid 48ea Sunmodule SW240, sunmodule 240W Modules, 18 SolarWorld 290W modules, 2ea Radian 8000W GS8048 48V 120/240VAC Inverter, 4ea Flexmax 80, MATE 3s, Hub 10, 2kw Wind, two 15kw ecogen on a manual bypass. Everything is redundant.
Location: 648 Southbridge Rd., Warren MA
Contact:

Re: AC Backfeed Error

Post by eesiason » Sat Jun 20, 2020 6:19 am

OK. I may wait until Monday to do that load test, just in case it breaks something. We are an active Bed & Breakfast with guests this weekend, so we don't want to do that in crisis mode or on a generator. :-) Stay tuned.

User avatar
EA6LE-ONE
Forum Guru
Posts: 274
Joined: Tue May 05, 2020 7:51 am
My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
4 x FLEXmax 100, HUB10,
2 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 4 x FLEXware ICS Plus,
54 x PANASONIC VBHN325SA17 325W

System 2:
MATE3s, 2 x VFX3648,
2 x FLEXmax 100, HUB10
1 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W
Location: Providenciales, Turks & Caicos Isl.

Re: AC Backfeed Error

Post by EA6LE-ONE » Sat Jun 20, 2020 6:27 am

fcwlp wrote:
Sat Jun 20, 2020 6:12 am

I do not know if that would cause the backfeed error. Let us know what happens after you load the system to 8+kW.
On GS8048A you don't have to go over 8KW to activate the next inverter. When is a big enough load all my 3 inverters activate to share the load. For a 5kw load I have the master inverting 2.5KW and the 2 slaves are 1.2KW and 1.3KW. Not sure if GS8048 does the same.

I think the difference in voltage might be the culprit but the out of phase scenario is more plausible. Also be sure to recheck the setting for master and slave, be sure that the master inverter is on port 1 of the hub and the slave on 2.

User avatar
EA6LE-ONE
Forum Guru
Posts: 274
Joined: Tue May 05, 2020 7:51 am
My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
4 x FLEXmax 100, HUB10,
2 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 4 x FLEXware ICS Plus,
54 x PANASONIC VBHN325SA17 325W

System 2:
MATE3s, 2 x VFX3648,
2 x FLEXmax 100, HUB10
1 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W
Location: Providenciales, Turks & Caicos Isl.

Re: AC Backfeed Error

Post by EA6LE-ONE » Sat Jun 20, 2020 6:37 am

I don't see any info about your battery. Be sure that the battery is OK and capable to sustain both inverters at peak power.

eesiason
Forum Whiz
Posts: 48
Joined: Fri Oct 12, 2012 9:40 am
My RE system: Off-Grid 48ea Sunmodule SW240, sunmodule 240W Modules, 18 SolarWorld 290W modules, 2ea Radian 8000W GS8048 48V 120/240VAC Inverter, 4ea Flexmax 80, MATE 3s, Hub 10, 2kw Wind, two 15kw ecogen on a manual bypass. Everything is redundant.
Location: 648 Southbridge Rd., Warren MA
Contact:

Re: AC Backfeed Error

Post by eesiason » Sat Jun 20, 2020 7:15 am

EAGLE-ONE is correct. The inverters do share load well before it gets to 8kW. We had full sun yesterday when this happened so there should not be a battery issue(?). They are 8 years old, DEKA flooded lead-acid 820 amp hours, showing no real signs of degradation. In the summer, they rarely go much below 80% overnight, in the winter I don't often let them get below 60%. When the sun is not full out, we don't use the AC or electric dryer, so the house sips along at 1000 watts or less. Right this moment, it's using 300 watts.

fcwlp
Forum Czar
Posts: 533
Joined: Wed Jan 22, 2020 9:40 am
My RE system: GS8048A, FM80 w/3,600 W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed
I also install and maintain grid-tied and off-grid systems, details will be given for these system if required
Location: 80 miles NE of Phoenix at 5500'

Re: AC Backfeed Error

Post by fcwlp » Sun Jun 21, 2020 8:16 am

eesiason wrote:
Sat Jun 20, 2020 7:15 am
EAGLE-ONE is correct. The inverters do share load well before it gets to 8kW.
In my experience debugging electro-mechanical systems/tools over the past 40 years is to replicate the conditions that caused the issue. Maybe it is one of the power modules that has an issue.

eesiason
Forum Whiz
Posts: 48
Joined: Fri Oct 12, 2012 9:40 am
My RE system: Off-Grid 48ea Sunmodule SW240, sunmodule 240W Modules, 18 SolarWorld 290W modules, 2ea Radian 8000W GS8048 48V 120/240VAC Inverter, 4ea Flexmax 80, MATE 3s, Hub 10, 2kw Wind, two 15kw ecogen on a manual bypass. Everything is redundant.
Location: 648 Southbridge Rd., Warren MA
Contact:

Re: AC Backfeed Error

Post by eesiason » Sun Jun 21, 2020 1:31 pm

True that fcwlp. I just don't want to push it on the weekend when there is no tech support available. I'm fairly certain it is the primary inverter that is losing it's mind. I have had the mate complain about a firmware mismatch on it (there is not) as well as the mate appearing to reprogram it a couple times. I woke this morning to a powered on system, but had to restart the mate to get it to re-see the master radian. An interesting Optics RE curve resulted.
Attachments
whacked curve.jpg

User avatar
EA6LE-ONE
Forum Guru
Posts: 274
Joined: Tue May 05, 2020 7:51 am
My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
4 x FLEXmax 100, HUB10,
2 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 4 x FLEXware ICS Plus,
54 x PANASONIC VBHN325SA17 325W

System 2:
MATE3s, 2 x VFX3648,
2 x FLEXmax 100, HUB10
1 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W
Location: Providenciales, Turks & Caicos Isl.

Re: AC Backfeed Error

Post by EA6LE-ONE » Sun Jun 21, 2020 1:48 pm

Might be the mate that is creating the problem. I had my mate started once to report mismatched firmware on my inverters. it did for few days that until I reset it. you should probably enable the mate reset every 24h. and check to be sure you have the latest firmware.

eesiason
Forum Whiz
Posts: 48
Joined: Fri Oct 12, 2012 9:40 am
My RE system: Off-Grid 48ea Sunmodule SW240, sunmodule 240W Modules, 18 SolarWorld 290W modules, 2ea Radian 8000W GS8048 48V 120/240VAC Inverter, 4ea Flexmax 80, MATE 3s, Hub 10, 2kw Wind, two 15kw ecogen on a manual bypass. Everything is redundant.
Location: 648 Southbridge Rd., Warren MA
Contact:

Re: AC Backfeed Error

Post by eesiason » Sun Jun 21, 2020 2:10 pm

EA6LE-ONE wrote:
Sun Jun 21, 2020 1:48 pm
Might be the mate that is creating the problem. I had my mate started once to report mismatched firmware on my inverters. it did for few days that until I reset it. you should probably enable the mate reset every 24h. and check to be sure you have the latest firmware.
Learned that one sometime ago. Set the Mate reset to every 24 hours, and solved a number of goofy issues years ago, some of which have probably been fixed in firmware updates over time.

When the original issue of AC Backfeed happened on Friday, there was the nasty smell of highly unhappy electronics that went with it. We will see what the tech support team says tomorrow.

User avatar
EA6LE-ONE
Forum Guru
Posts: 274
Joined: Tue May 05, 2020 7:51 am
My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
4 x FLEXmax 100, HUB10,
2 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 4 x FLEXware ICS Plus,
54 x PANASONIC VBHN325SA17 325W

System 2:
MATE3s, 2 x VFX3648,
2 x FLEXmax 100, HUB10
1 x EnergyCell 48V 2700RE,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W
Location: Providenciales, Turks & Caicos Isl.

Re: AC Backfeed Error

Post by EA6LE-ONE » Sun Jun 21, 2020 2:39 pm

The AC feedback you had might be because of the AC and the Dryer. Not sure if is something to do with reactive power.

fcwlp
Forum Czar
Posts: 533
Joined: Wed Jan 22, 2020 9:40 am
My RE system: GS8048A, FM80 w/3,600 W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed
I also install and maintain grid-tied and off-grid systems, details will be given for these system if required
Location: 80 miles NE of Phoenix at 5500'

Re: AC Backfeed Error

Post by fcwlp » Sun Jun 21, 2020 6:52 pm

EA6LE-ONE wrote:
Sun Jun 21, 2020 1:48 pm
Might be the mate that is creating the problem. I had my mate started once to report mismatched firmware on my inverters. it did for few days that until I reset it. you should probably enable the mate reset every 24h. and check to be sure you have the latest firmware.
I have had the mismatched firmware issue on one of the FlexPower 2 systems I support. It has been reported that it could be due to electrical noise with the cables running through the AC wiring boxes. I installed two CAT6 shielded cables last week for the inverters, when I was doing some other work. For $8 of cables, hopefully it saves some service calls down 8 miles of rough, dirt forest roads.
eesiason wrote:
Sun Jun 21, 2020 2:10 pm
When the original issue of AC Backfeed happened on Friday, there was the nasty smell of highly unhappy electronics that went with it. We will see what the tech support team says tomorrow.
That would definitely be a signal of where to look. You may want to take the covers off of the Radians before powering up to see if you can see the possible wisps of smoke. It is likely one of the power modules.

eesiason
Forum Whiz
Posts: 48
Joined: Fri Oct 12, 2012 9:40 am
My RE system: Off-Grid 48ea Sunmodule SW240, sunmodule 240W Modules, 18 SolarWorld 290W modules, 2ea Radian 8000W GS8048 48V 120/240VAC Inverter, 4ea Flexmax 80, MATE 3s, Hub 10, 2kw Wind, two 15kw ecogen on a manual bypass. Everything is redundant.
Location: 648 Southbridge Rd., Warren MA
Contact:

Re: AC Backfeed Error

Post by eesiason » Thu Jun 25, 2020 3:41 pm

Master inverter failed today. I called tech support and am really disappointed to learn that Outback really does not want to talk to an owner/self-installer. They put you in a "call back queue" instead of connecting you to someone with a clue right away. The person answering the phone said it "might be three days". Wow is that BS. This is a wholly different experience than years ago when I put this all together.

Slave is reconfigured as master and we are running. But wow. What a negative experience.

Anyone ever seen a Beast Power Supply Board that looked like this?

House was probably using less than 1000 watts when this happened.
cooked.jpg

fcwlp
Forum Czar
Posts: 533
Joined: Wed Jan 22, 2020 9:40 am
My RE system: GS8048A, FM80 w/3,600 W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed
I also install and maintain grid-tied and off-grid systems, details will be given for these system if required
Location: 80 miles NE of Phoenix at 5500'

Re: AC Backfeed Error

Post by fcwlp » Thu Jun 25, 2020 8:09 pm

Try Northern Arizona Wind & Sun for the board their p/n SPARE-215, https://www.solar-electric.com/outback- ... ment.html.

I have found them to very responsive and get most of my Outback hardware through them.

eesiason
Forum Whiz
Posts: 48
Joined: Fri Oct 12, 2012 9:40 am
My RE system: Off-Grid 48ea Sunmodule SW240, sunmodule 240W Modules, 18 SolarWorld 290W modules, 2ea Radian 8000W GS8048 48V 120/240VAC Inverter, 4ea Flexmax 80, MATE 3s, Hub 10, 2kw Wind, two 15kw ecogen on a manual bypass. Everything is redundant.
Location: 648 Southbridge Rd., Warren MA
Contact:

Re: AC Backfeed Error

Post by eesiason » Fri Jun 26, 2020 5:49 am

fcwlp wrote:
Thu Jun 25, 2020 8:09 pm
Try Northern Arizona Wind & Sun for the board their p/n SPARE-215, https://www.solar-electric.com/outback- ... ment.html.

I have found them to very responsive and get most of my Outback hardware through them.
:-) I found that last night and bought it from them. Do they provide any level of tech support? I'd like to be able to understand what may have caused this board to expire. No response from Outback yet on my case. It's only $140 after shipping, but I'd hate to put it in and just have it fry too.

fcwlp
Forum Czar
Posts: 533
Joined: Wed Jan 22, 2020 9:40 am
My RE system: GS8048A, FM80 w/3,600 W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed
I also install and maintain grid-tied and off-grid systems, details will be given for these system if required
Location: 80 miles NE of Phoenix at 5500'

Re: AC Backfeed Error

Post by fcwlp » Fri Jun 26, 2020 6:27 am

eesiason wrote:
Fri Jun 26, 2020 5:49 am
Do they provide any level of tech support?
It would not hurt to give them a call. They are not tech support but they have a lot of experience.

The resistor labeled R19 failed, due to too much current flowing thru it.

It has happened before, http://outbackpower.com/forum/viewtopic.php?t=8896

The last post in the above topic suggests it is part of the circuit that powers the Hub and Mate, so that is likely the issue with your firmware mismatch and Mate errors. If it does power the Hub/Mate the failure is not likely due to a current surge but rather a design/component tolerance issue resulting in a little too much power to dissipate.

eesiason
Forum Whiz
Posts: 48
Joined: Fri Oct 12, 2012 9:40 am
My RE system: Off-Grid 48ea Sunmodule SW240, sunmodule 240W Modules, 18 SolarWorld 290W modules, 2ea Radian 8000W GS8048 48V 120/240VAC Inverter, 4ea Flexmax 80, MATE 3s, Hub 10, 2kw Wind, two 15kw ecogen on a manual bypass. Everything is redundant.
Location: 648 Southbridge Rd., Warren MA
Contact:

Re: AC Backfeed Error

Post by eesiason » Mon Jun 29, 2020 5:22 pm

Hopefully, someone from Outback is paying attention to this board and can help expedite this. I spoke to a tech on Friday around Noon west coast time. He setup the order for my board and said someone from the office would call to collect my payment information. I replied a couple of times to the support email asking for an update.

Crickets.

What a dismal support experience.

raysun
Forum Emperor
Posts: 2951
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: AC Backfeed Error

Post by raysun » Mon Jun 29, 2020 5:57 pm

Did you try calling the Outback main office directly? On the occasions I've had to contact Sales, I've gotten right through to them.

eesiason
Forum Whiz
Posts: 48
Joined: Fri Oct 12, 2012 9:40 am
My RE system: Off-Grid 48ea Sunmodule SW240, sunmodule 240W Modules, 18 SolarWorld 290W modules, 2ea Radian 8000W GS8048 48V 120/240VAC Inverter, 4ea Flexmax 80, MATE 3s, Hub 10, 2kw Wind, two 15kw ecogen on a manual bypass. Everything is redundant.
Location: 648 Southbridge Rd., Warren MA
Contact:

Re: AC Backfeed Error

Post by eesiason » Mon Jul 20, 2020 12:58 pm

So, this is now resolved, and I think I know root cause.

I had to send the board in for repair, because none were available. (But the tech notes on the slip in the box said "Burned components on power board - replaced board, tested OK". But it is what it is. My system is back on two inverters and my ACs are all running. Wheeeeeeee.

While I had the system down and disconnected from the battery bank, I figured I would check all connections and do a little inspection. It took 3 seconds to ID the issue. The leads from two of my FM80s to the shunt were severely burned from arcing. They were loose. :shock: The "last mile" connections are all I paid someone to do for my system and I should have done that myself too. That is the gift that just keeps giving. The PV company that I hired eventually gave me a full refund on the electrician bill, so you can just imagine the issues...

I suppose that over time, 1000's of charging cycles later, the connection could have loosened. But I'm thinking that should not be the case. Perhaps I will add this to an annual maintenance checklist that I have for the B&B to make sure everything is still tight.

pss
Forum Czar
Posts: 634
Joined: Mon Jul 24, 2017 8:40 am
My RE system: 8330 watts in three strings, Flexmax 60 x 3, Radian 8048A, GSLC load center, Mate 3S, Hub 10.3, FN-DC and 900 Amp, 48V Trojan T105-RE battery bank.

Re: AC Backfeed Error

Post by pss » Mon Jul 20, 2020 2:10 pm

A good rule to follow or best practice is to tighten the connection, wait 20-30 seconds and tighten up again. As my electrician explained in basic terms, copper wire can relax and loosen, so tighten twice to specs.

fcwlp
Forum Czar
Posts: 533
Joined: Wed Jan 22, 2020 9:40 am
My RE system: GS8048A, FM80 w/3,600 W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed
I also install and maintain grid-tied and off-grid systems, details will be given for these system if required
Location: 80 miles NE of Phoenix at 5500'

Re: AC Backfeed Error

Post by fcwlp » Mon Jul 20, 2020 8:25 pm

eesiason wrote:
Mon Jul 20, 2020 12:58 pm
While I had the system down and disconnected from the battery bank, I figured I would check all connections and do a little inspection. It took 3 seconds to ID the issue. The leads from two of my FM80s to the shunt were severely burned from arcing. They were loose.
I am not sure this is the issue that caused the burned component but it definitely needed to be fixed.
pss wrote:
Mon Jul 20, 2020 2:10 pm
As my electrician explained in basic terms, copper wire can relax and loosen, so tighten twice to specs.
Copper will creep (i.e. deform) due to the pressure of the terminal screw and the temperature of the connection. Higher temperature increases the creep rate. So as the joint loosened slightly due to creep, resistance increased causing the temperature to increase thus increasing the creep rate resulting in more loosening. After many cycles the issue developed. Fortunately we are not dealing with Al wire, as it creeps faster and the Al2O3 (aluminum oxide) that forms is not conductive. :grin: (FYI, I am a mechanical engineer)

pss
Forum Czar
Posts: 634
Joined: Mon Jul 24, 2017 8:40 am
My RE system: 8330 watts in three strings, Flexmax 60 x 3, Radian 8048A, GSLC load center, Mate 3S, Hub 10.3, FN-DC and 900 Amp, 48V Trojan T105-RE battery bank.

Re: AC Backfeed Error

Post by pss » Mon Jul 20, 2020 9:15 pm

Another trick to try is using a laser thermometer on connection terminals, they should be very close to room temperature, if warm, further investigation is needed.