Post by L3enigma » Thu May 21, 2020 11:17 pm

Hi All,

first time poster. <Neither framed nor laminated> :lol:

I read in the tech specs that the Vmax for a connected battery pack is 64VDC. Is that Vmax a nominal value, or is that a not-to-exceed value?

Many NCM cells are not quite fully charged at 4V/cell or 64V for a 16 cell pack.

Thank you all for the fine info already here.

Cheers!

Jim

fcwlp
Forum Guru
Posts: 288
Joined: Wed Jan 22, 2020 9:40 am
My RE system: GS8048A, FM80 w/3,600 W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed
I also install and maintain grid-tied and off-grid systems, details will be given for these system if required
Location: 80 miles NE of Phoenix at 5500'

Re: Radian Vmax

Post by fcwlp » Fri May 22, 2020 2:34 pm

Hi Jim,

The 64V is the max value that you can program the Radian for absorb and float (not sure why you would do that). The High Battery Cut Out (HBCO) and Equalization settings allow up to 68V.

L3enigma
Forum Junior Member
Posts: 4
Joined: Thu May 21, 2020 11:08 pm
My RE system: Radian 8048
Ancient MX60
4 parallel strings of 6@12V PV panels
14.4kWh nominal LFP battery pack
Orion 2 Jr BMS
All to run a 4-Ton AC unit from 4-9pm under TOU-5 rates in CA.
Tesla, pool pump and grid battery charge loading at night

Re: Radian Vmax

Post by L3enigma » Sat May 23, 2020 8:40 pm

That is a beautiful answer - many thanks! I can use the NMC cells now with total confidence