The "phone plug" accidentally pulled off the temperature monitor cable.(My boo-boo.)

What is the pin connections to the plug? I can replace it.

/roger
RJRsolar
OutBack Whiz
 
Posts: 26
Joined: Wed Dec 12, 2007 6:21 pm
Location: Pullman, WA

Re: Damaged Battery Temperature Sensing Unit

Postby Mike Curran on Sat Mar 04, 2017 6:44 pm

Based on this thread: viewtopic.php?f=17&t=8414&p=47543&hilit=RTS#p47543 it sounds like the RTS is just a thermistor so it should be only two conductors and polarity won't matter. I say "should be" because I haven't examined the plug/number of conductors on my own RTS.
Mike Curran
OutBack Guru
 
Posts: 334
Joined: Sat Aug 28, 2004 6:28 pm
Location: Chagrin Falls, Ohio
My RE system: Outback: 8 (2x4) Evergreen 180's into one MX60, 6 (2×3) ALEO S79-300's into one FM80, 2 grid-tied GVFX3524's classic stacked for 120/240VAC, 12 Surrette/Rolls 2V x 1766Ah, Hub10.3, Mate3, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.

Westinghouse Solar: 30 (2x15) 235W panels with Enphase M215 microinverters. 6,450 nameplate watts AC, grid-tied.

Re: Damaged Battery Temperature Sensing Unit

Postby Vic on Sun Mar 05, 2017 2:24 pm

YES, Mike is correct, the Sensor is simply a 10 K NTC Thermistor -- temperature-variable resistor.

In the OB RTS cables that I've seen (dark green ones), the Red and Green wires in the cable are connected together, as are the Black and Yellow ones, at the Thermistor. The OB hardware looks for a resistance change twix these two pairs of wires (by running a small current through the Thermistor, and looking for a voltage change vs temperature change)

At room temperature, the Thermistor should read close to 10 K Ohms.

The sequence of the wires from one side of the four-pin cable connector is, Yellow - Green - Red - Black. And, it should not make a difference which side of the connector that you start the above sequence, there is no polarity required, as the RTS is just a resistor.

IMO, FWIW, Good Luck, Vic