strange behavior overnight

Mate3 and Mate3s communications devices for Outback Power

strange behavior overnight

Postby Megunticook on Mon Apr 16, 2018 5:48 am

Yesterday I checked on my Radian system (with MATE3s) and found that the Mate's homescreen was looking odd (mostly blank except for the top line of information). I unplugged it then plugged it back in, and it looked fine. But I couldn't get my system to sell back to the grid, even after charge parameters were met, without my forcing both CCs into bulk mode several times until finally they moved into GT Mode. Very odd.

When I looked at the Event History in Optics, I saw a massive amount of activity after midnight, but can't make heads or tails of it. What exactly happened? Did some sort of update get pushed down from the server?

Here's the log:


Config main system CC 8 Limited: Upper Battery Voltage 64.3 64.4 VDC On-Site 04/15/2018 01:47 AM

Config main system CC 8 Disconnect < 48 54.4 VDC On-Site 04/15/2018 01:47 AM

Config main system COMM M OB AC Current SF -2 -1 -- On-Site 04/15/2018 01:47 AM

Config main system COMM M Inverter Mode On -- -- On-Site 04/15/2018 01:47 AM

Status main system CC 8 Firmware Update 0.0.0 3.3.0 -- -- 04/15/2018 01:39 AM

Status main system CC 8 Firmware Update 0.0.0 3.3.0 -- -- 04/15/2018 01:39 AM

Config main system CC 8 Re-Connect > 0 57.6 VDC On-Site 04/15/2018 01:39 AM

Config main system INV 1 AC Output Voltage Calibrate 8 -2 CF On-Site 04/15/2018 01:39 AM

Config main system INV 1 Re-Bulk Voltage 0 47.6 VDC On-Site 04/15/2018 01:39 AM

Config main system CC 8 Absorb Voltage 0 58.8 VDC On-Site 04/15/2018 01:39 AM

Config main system INV 1 Grid Zero DOD Amps 0 1.25 AAC On-Site 04/15/2018 01:39 AM

Config main system CC 8 Wakeup Interval 0 5 Minutes On-Site 04/15/2018 01:39 AM

Config main system CC 8 Current Limit 0 75 ADC On-Site 04/15/2018 01:39 AM

Config main system CC 8 Threshold 0 10 VDC On-Site 04/15/2018 01:39 AM

Config main system INV 1 Mini Grid Delay 0 10 Minutes On-Site 04/15/2018 01:39 AM

Config main system CC 8 Wakeup VOC Change 0 6 VDC On-Site 04/15/2018 01:39 AM

Config main system CC 8 Float Voltage 0 54 VDC On-Site 04/15/2018 01:39 AM

Config main system INV 1 Grid Zero DOD Volts 0 48 VDC On-Site 04/15/2018 01:39 AM

Config main system CC 8 Current Limit 0 75 ADC On-Site 04/15/2018 01:39 AM

Config main system INV 1 GSconfig EE Write Enable 0 1 -- On-Site 04/15/2018 01:39 AM

Config main system CC 8 Enable Voltage > 0 58.8 VDC On-Site 04/15/2018 01:39 AM

Config main system COMM M Sell Current Limit 0 30 AAC On-Site 04/15/2018 01:39 AM

Config main system INV 1 Mini Grid Connect to Grid 0 48 VDC On-Site 04/15/2018 01:39 AM

Config main system CC 8 EQ Voltage 0 62.4 VDC On-Site 04/15/2018 01:39 AM

Config main system CC 8 Disconnect < 0 48 VDC On-Site 04/15/2018 01:39 AM

Config main system CC 8 Enable Voltage > 0 140 VDC On-Site 04/15/2018 01:39 AM

Config main system INV 1 Mini Grid Connect to Grid 0 48 VDC On-Site 04/15/2018 01:39 AM

Config main system CC 8 Float Voltage 0 54 VDC On-Site 04/15/2018 01:39 AM

Config main system CC 8 Absorb Voltage 0 58.8 VDC On-Site 04/15/2018 01:39 AM

Config main system INV 1 Battery Voltage Calibrate -0.8 0.4 CF On-Site 04/15/2018 01:39 AM

Config main system INV 1 Battery Voltage Calibrate -0.8 0.4 CF On-Site 04/15/2018 01:39 AM

Config main system CC 8 Limited: Lower Battery Voltage 0 52.8 VDC On-Site 04/15/2018 01:39 AM

Config main system INV 1 Gen Input Voltage Calibrate 8 -1 CF On-Site 04/15/2018 01:39 AM

Config main system CC 8 EQ Voltage 0 62.4 VDC On-Site 04/15/2018 01:39 AM

Config main system INV 1 Gen Input Voltage Calibrate 8 -1 CF On-Site 04/15/2018 01:39 AM

Config main system CC 8 Disconnect < 0 48 VDC On-Site 04/15/2018 01:39 AM

Config main system CC 8 Enable Voltage > 0 58.8 VDC On-Site 04/15/2018 01:39 AM

Config main system INV 1 Pulse Length 0 8 Cycles On-Site 04/15/2018 01:39 AM

Config main system INV 1 Grid Zero DOD Amps 0 1.25 AAC On-Site 04/15/2018 01:39 AM

Config main system CC 8 U-Pick VOC 0 77 Percent On-Site 04/15/2018 01:39 AM

Config main system CC 8 Re-Bulk Voltage 0 48.8 VDC On-Site 04/15/2018 01:39 AM

Config main system INV 1 Grid Zero DOD Volts 0 48 VDC On-Site 04/15/2018 01:39 AM

Config main system INV 1 Grid Input Voltage Calibrate 8 -1 CF On-Site 04/15/2018 01:39 AM

Config main system CC 8 Re-Connect > 0 57.6 VDC On-Site 04/15/2018 01:39 AM

Config main system CC 8 Re-Bulk Voltage 0 48.8 VDC On-Site 04/15/2018 01:39 AM

Config main system INV 1 Mini Grid Delay 0 10 Minutes On-Site 04/15/2018 01:39 AM

Config main system CC 8 U-Pick VOC 0 77 Percent On-Site 04/15/2018 01:39 AM

Config main system CC 8 Enable Voltage > 0 140 VDC On-Site 04/15/2018 01:39 AM

Config main system INV 1 Re-Bulk Voltage 0 47.6 VDC On-Site 04/15/2018 01:39 AM

Config main system CC 8 Threshold 0 10 VDC On-Site 04/15/2018 01:39 AM

Config main system INV 1 Grid Input Voltage Calibrate 8 -1 CF On-Site 04/15/2018 01:39 AM

Config main system CC 8 Wakeup VOC Change 0 6 VDC On-Site 04/15/2018 01:39 AM

Config main system INV 1 Pulse Spacing 0 60 Cycles On-Site 04/15/2018 01:39 AM

Config main system INV 1 GSconfig EE Write Enable 0 1 -- On-Site 04/15/2018 01:39 AM

Config main system INV 1 Search Sensitivity 0 10 -- On-Site 04/15/2018 01:39 AM

Config main system INV 1 Pulse Spacing 0 60 Cycles On-Site 04/15/2018 01:39 AM

Config main system INV 1 AC Output Voltage Calibrate 8 -2 CF On-Site 04/15/2018 01:39 AM

Config main system INV 1 Search Sensitivity 0 10 -- On-Site 04/15/2018 01:39 AM

Config main system INV 1 Pulse Length 0 8 Cycles On-Site 04/15/2018 01:39 AM

Config main system CC 8 Limited: Lower Battery Voltage 0 52.8 VDC On-Site 04/15/2018 01:39 AM

Config main system CC 8 Limited: Upper Battery Voltage 0 64.3 VDC On-Site 04/15/2018 01:39 AM

Config main system CC 8 Limited: Upper Battery Voltage 0 64.3 VDC On-Site 04/15/2018 01:39 AM

Config main system CC 8 Wakeup Interval 0 5 Minutes On-Site 04/15/2018 01:39 AM

Status main system CC 8 Firmware Update 3.3.0 0.0.0 -- -- 04/15/2018 01:36 AM

Status main system CC 8 Firmware Update 3.3.0 0.0.0 -- -- 04/15/2018 01:36 AM

Config main system INV 1 Mini Grid Delay 10 0 Minutes On-Site 04/15/2018 01:36 AM

Config main system INV 1 Mini Grid Delay 10 0 Minutes On-Site 04/15/2018 01:36 AM

Config main system COMM M Sell Current Limit 30 0 AAC On-Site 04/15/2018 01:36 AM

Config main system INV 1 Grid Input Voltage Calibrate -1 8 CF On-Site 04/15/2018 01:36 AM

Config main system INV 1 Grid Zero DOD Volts 48 0 VDC On-Site 04/15/2018 01:36 AM

Config main system INV 1 Re-Bulk Voltage 47.6 0 VDC On-Site 04/15/2018 01:36 AM

Config main system CC 8 Wakeup Interval 5 0 Minutes On-Site 04/15/2018 01:36 AM

Config main system INV 1 GSconfig EE Write Enable 1 0 -- On-Site 04/15/2018 01:36 AM

Config main system INV 1 Battery Voltage Calibrate 0.4 -0.8 CF On-Site 04/15/2018 01:36 AM

Config main system INV 1 Pulse Spacing 60 0 Cycles On-Site 04/15/2018 01:36 AM

Config main system INV 1 GSconfig EE Write Enable 1 0 -- On-Site 04/15/2018 01:36 AM

Config main system CC 8 Re-Connect > 57.6 0 VDC On-Site 04/15/2018 01:36 AM

Config main system INV 1 Grid Zero DOD Amps 1.25 0 AAC On-Site 04/15/2018 01:36 AM

Config main system CC 8 Re-Connect > 57.6 0 VDC On-Site 04/15/2018 01:36 AM

Config main system INV 1 Grid Zero DOD Amps 1.25 0 AAC On-Site 04/15/2018 01:36 AM

Config main system INV 1 Pulse Length 8 0 Cycles On-Site 04/15/2018 01:36 AM

Config main system INV 1 AC Output Voltage Calibrate -2 8 CF On-Site 04/15/2018 01:36 AM

Config main system CC 8 Re-Bulk Voltage 48.8 0 VDC On-Site 04/15/2018 01:36 AM

Config main system CC 8 Enable Voltage > 140 0 VDC On-Site 04/15/2018 01:36 AM

Config main system CC 8 Enable Voltage > 58.8 0 VDC On-Site 04/15/2018 01:36 AM

Config main system INV 1 Mini Grid Connect to Grid 48 0 VDC On-Site 04/15/2018 01:36 AM

Config main system CC 8 Limited: Lower Battery Voltage 52.8 0 VDC On-Site 04/15/2018 01:36 AM

Config main system INV 1 Re-Bulk Voltage 47.6 0 VDC On-Site 04/15/2018 01:36 AM

Config main system CC 8 Limited: Lower Battery Voltage 52.8 0 VDC On-Site 04/15/2018 01:36 AM

Config main system INV 1 Grid Input Voltage Calibrate -1 8 CF On-Site 04/15/2018 01:36 AM

Config main system CC 8 Absorb Voltage 58.8 0 VDC On-Site 04/15/2018 01:36 AM

Config main system CC 8 Float Voltage 54 0 VDC On-Site 04/15/2018 01:36 AM

Config main system INV 1 Search Sensitivity 10 0 -- On-Site 04/15/2018 01:36 AM

Config main system CC 8 Wakeup VOC Change 6 0 VDC On-Site 04/15/2018 01:36 AM

Config main system CC 8 Wakeup VOC Change 6 0 VDC On-Site 04/15/2018 01:36 AM

Config main system CC 8 Threshold 10 0 VDC On-Site 04/15/2018 01:36 AM

Config main system CC 8 Float Voltage 54 0 VDC On-Site 04/15/2018 01:36 AM

Config main system INV 1 Mini Grid Connect to Grid 48 0 VDC On-Site 04/15/2018 01:36 AM

Config main system CC 8 U-Pick VOC 77 0 Percent On-Site 04/15/2018 01:36 AM

Config main system CC 8 Wakeup Interval 5 0 Minutes On-Site 04/15/2018 01:36 AM

Config main system CC 8 Current Limit 75 0 ADC On-Site 04/15/2018 01:36 AM

Config main system CC 8 Re-Bulk Voltage 48.8 0 VDC On-Site 04/15/2018 01:36 AM

Config main system INV 1 Battery Voltage Calibrate 0.4 -0.8 CF On-Site 04/15/2018 01:36 AM

Config main system CC 8 Current Limit 75 0 ADC On-Site 04/15/2018 01:36 AM

Config main system CC 8 EQ Voltage 62.4 0 VDC On-Site 04/15/2018 01:36 AM

Config main system CC 8 Enable Voltage > 58.8 0 VDC On-Site 04/15/2018 01:36 AM

Config main system INV 1 Grid Zero DOD Volts 48 0 VDC On-Site 04/15/2018 01:36 AM

Config main system INV 1 Gen Input Voltage Calibrate -1 8 CF On-Site 04/15/2018 01:36 AM

Config main system INV 1 Search Sensitivity 10 0 -- On-Site 04/15/2018 01:36 AM

Config main system CC 8 Enable Voltage > 140 0 VDC On-Site 04/15/2018 01:36 AM

Config main system CC 8 Absorb Voltage 58.8 0 VDC On-Site 04/15/2018 01:36 AM

Config main system CC 8 Threshold 10 0 VDC On-Site 04/15/2018 01:36 AM

Config main system INV 1 AC Output Voltage Calibrate -2 8 CF On-Site 04/15/2018 01:36 AM

Config main system CC 8 Disconnect < 48 0 VDC On-Site 04/15/2018 01:36 AM

Config main system CC 8 Disconnect < 48 0 VDC On-Site 04/15/2018 01:36 AM

Config main system INV 1 Pulse Spacing 60 0 Cycles On-Site 04/15/2018 01:36 AM

Config main system CC 8 EQ Voltage 62.4 0 VDC On-Site 04/15/2018 01:36 AM

Config main system CC 8 U-Pick VOC 77 0 Percent On-Site 04/15/2018 01:36 AM

Config main system CC 8 Limited: Upper Battery Voltage 64.3 0 VDC On-Site 04/15/2018 01:36 AM

Config main system INV 1 Gen Input Voltage Calibrate -1 8 CF On-Site 04/15/2018 01:36 AM

Config main system INV 1 Pulse Length 8 0 Cycles On-Site 04/15/2018 01:36 AM

Config main system CC 8 Limited: Upper Battery Voltage 64.3 0 VDC On-Site 04/15/2018 01:36 AM

Status main system CC 8 Firmware Update 0.0.0 3.3.0 -- -- 04/15/2018 01:33 AM

Status main system CC 8 Firmware Update 0.0.0 3.3.0 -- -- 04/15/2018 01:33 AM

Config main system COMM M Sell Current Limit 0 30 AAC On-Site 04/15/2018 01:33 AM

Config main system CC 8 Current Limit 0 75 ADC On-Site 04/15/2018 01:33 AM

Config main system INV 1 Mini Grid Connect to Grid 0 48 VDC On-Site 04/15/2018 01:33 AM

Config main system INV 1 Pulse Spacing 0 60 Cycles On-Site 04/15/2018 01:33 AM

Config main system CC 8 Limited: Lower Battery Voltage 0 52.8 VDC On-Site 04/15/2018 01:33 AM

Config main system CC 8 U-Pick VOC 0 77 Percent On-Site 04/15/2018 01:33 AM

Config main system INV 1 GSconfig EE Write Enable 0 1 -- On-Site 04/15/2018 01:33 AM

Config main system CC 8 EQ Voltage 0 62.4 VDC On-Site 04/15/2018 01:33 AM

Config main system CC 8 Threshold 0 10 VDC On-Site 04/15/2018 01:33 AM

Config main system CC 8 Current Limit 0 75 ADC On-Site 04/15/2018 01:33 AM

Config main system INV 1 Mini Grid Delay 0 10 Minutes On-Site 04/15/2018 01:33 AM

Config main system INV 1 Grid Input Voltage Calibrate 8 -1 CF On-Site 04/15/2018 01:33 AM

Config main system CC 8 Wakeup VOC Change 0 6 VDC On-Site 04/15/2018 01:33 AM

Config main system INV 1 Pulse Length 0 8 Cycles On-Site 04/15/2018 01:33 AM

Config main system INV 1 Search Sensitivity 0 10 -- On-Site 04/15/2018 01:33 AM

Config main system INV 1 GSconfig EE Write Enable 0 1 -- On-Site 04/15/2018 01:33 AM

Config main system INV 1 Grid Input Voltage Calibrate 8 -1 CF On-Site 04/15/2018 01:33 AM

Config main system INV 1 Search Sensitivity 0 10 -- On-Site 04/15/2018 01:33 AM

Config main system CC 8 Float Voltage 0 54 VDC On-Site 04/15/2018 01:33 AM

Config main system CC 8 EQ Voltage 0 62.4 VDC On-Site 04/15/2018 01:33 AM

Config main system CC 8 Wakeup Interval 0 5 Minutes On-Site 04/15/2018 01:33 AM

Config main system CC 8 Limited: Upper Battery Voltage 0 64.3 VDC On-Site 04/15/2018 01:33 AM

Config main system INV 1 Pulse Length 0 8 Cycles On-Site 04/15/2018 01:33 AM

Config main system CC 8 Enable Voltage > 0 140 VDC On-Site 04/15/2018 01:33 AM

Config main system INV 1 Re-Bulk Voltage 0 47.6 VDC On-Site 04/15/2018 01:33 AM

Config main system CC 8 Float Voltage 0 54 VDC On-Site 04/15/2018 01:33 AM

Config main system CC 8 Threshold 0 10 VDC On-Site 04/15/2018 01:33 AM

Config main system INV 1 AC Output Voltage Calibrate 8 -2 CF On-Site 04/15/2018 01:33 AM

Config main system INV 1 Pulse Spacing 0 60 Cycles On-Site 04/15/2018 01:33 AM

Config main system CC 8 Limited: Upper Battery Voltage 0 64.3 VDC On-Site 04/15/2018 01:33 AM

Config main system INV 1 AC Output Voltage Calibrate 8 -2 CF On-Site 04/15/2018 01:33 AM

Config main system CC 8 Disconnect < 0 48 VDC On-Site 04/15/2018 01:33 AM

Config main system CC 8 Re-Connect > 0 57.6 VDC On-Site 04/15/2018 01:33 AM

Config main system INV 1 Gen Input Voltage Calibrate 8 -1 CF On-Site 04/15/2018 01:33 AM

Config main system INV 1 Grid Zero DOD Amps 0 1.25 AAC On-Site 04/15/2018 01:33 AM

Config main system INV 1 Grid Zero DOD Volts 0 48 VDC On-Site 04/15/2018 01:33 AM

Config main system CC 8 Re-Connect > 0 57.6 VDC On-Site 04/15/2018 01:33 AM

Config main system CC 8 Wakeup VOC Change 0 6 VDC On-Site 04/15/2018 01:33 AM

Config main system CC 8 Wakeup Interval 0 5 Minutes On-Site 04/15/2018 01:33 AM

Config main system INV 1 Re-Bulk Voltage 0 47.6 VDC On-Site 04/15/2018 01:33 AM

Config main system CC 8 Limited: Lower Battery Voltage 0 52.8 VDC On-Site 04/15/2018 01:33 AM

Config main system INV 1 Grid Zero DOD Amps 0 1.25 AAC On-Site 04/15/2018 01:33 AM

Config main system INV 1 Gen Input Voltage Calibrate 8 -1 CF On-Site 04/15/2018 01:33 AM

Config main system CC 8 Enable Voltage > 0 58.8 VDC On-Site 04/15/2018 01:33 AM

Config main system INV 1 Mini Grid Delay 0 10 Minutes On-Site 04/15/2018 01:33 AM


Config main system CC 9 Re-Connect > 0 57.6 VDC On-Site 04/15/2018 01:27 AM

Config main system INV 1 Relay Mode Gen Alert 0 -- On-Site 04/15/2018 01:27 AM

Config main system CC 8 ON Time 0 4 Hours On-Site 04/15/2018 01:27 AM

Config main system INV 1 AC Output Voltage Calibrate -2 8 CF On-Site 04/15/2018 01:27 AM

Config main system INV 1 Re-Bulk Voltage 47.6 0 VDC On-Site 04/15/2018 01:27 AM

Config main system INV 1 Mini Grid Delay 10 0 Minutes On-Site 04/15/2018 01:27 AM

Config main system CC 8 Current Limit 75 0 ADC On-Site 04/15/2018 01:27 AM

Config main system INV 1 Mini Grid Connect to Grid 48 0 VDC On-Site 04/15/2018 01:27 AM

Config main system CC 9 Aux Mode Float Vent Fan -- On-Site 04/15/2018 01:27 AM

Config main system CC 9 U-Pick VOC 0 77 Percent On-Site 04/15/2018 01:27 AM

Config main system CC 9 Threshold 0 10 VDC On-Site 04/15/2018 01:27 AM

Config main system CC 8 Float Voltage 54 0 VDC On-Site 04/15/2018 01:27 AM

Config main system CC 9 Absorb Voltage 0 58.8 VDC On-Site 04/15/2018 01:27 AM

Config main system INV 1 Gen Input Voltage Calibrate -1 8 CF On-Site 04/15/2018 01:27 AM

Config main system CC 8 Absorb Voltage 58.8 0 VDC On-Site 04/15/2018 01:27 AM

Config main system CC 9 Low Battery Voltage < 0 46 VDC On-Site 04/15/2018 01:27 AM

Config main system CC 9 Re-Bulk Voltage 0 48.8 VDC On-Site 04/15/2018 01:27 AM

Config main system INV 1 Pulse Spacing 60 0 Cycles On-Site 04/15/2018 01:27 AM

Config main system INV 1 AUX Relay OFF Delay 0.5 0 Minutes On-Site 04/15/2018 01:27 AM

Config main system CC 9 Wakeup Interval 0 5 Minutes On-Site 04/15/2018 01:27 AM

Config main system INV 1 Grid Input Voltage Calibrate -1 8 CF On-Site 04/15/2018 01:27 AM

Config main system CC 9 Limited: Upper Battery Voltage 0 64.4 VDC On-Site 04/15/2018 01:27 AM

Config main system CC 8 Enable Voltage > 58.8 0 VDC On-Site 04/15/2018 01:27 AM

Config main system CC 9 Threshold 0 10 VDC On-Site 04/15/2018 01:27 AM

Config main system INV 1 AUX Relay ON Delay 0.5 0 Minutes On-Site 04/15/2018 01:27 AM

Config main system CC 8 Aux Status Off Auto -- On-Site 04/15/2018 01:27 AM

Config main system CC 9 Enable Voltage > 0 58.8 VDC On-Site 04/15/2018 01:27 AM

Config main system CC 8 Float Voltage 54 0 VDC On-Site 04/15/2018 01:27 AM

Config main system CC 8 ON Time 0 4 Hours On-Site 04/15/2018 01:27 AM

Config main system CC 8 Threshold 10 0 VDC On-Site 04/15/2018 01:27 AM

Config main system INV 1 GSconfig EE Write Enable 1 0 -- On-Site 04/15/2018 01:27 AM

Config main system CC 8 Battery Voltage Calibrate 0 -0.2 VDC On-Site 04/15/2018 01:27 AM

Config main system CC 9 Enable Voltage > 0 140 VDC On-Site 04/15/2018 01:27 AM

Status main system CC 9 Firmware Update 3.3.0 0.0.0 -- -- 04/15/2018 01:24 AM

Status main system CC 8 Firmware Update 0.0.0 3.3.0 -- -- 04/15/2018 01:24 AM

Status main system CC 9 Firmware Update 3.3.0 0.0.0 -- -- 04/15/2018 01:24 AM

Status main system CC 8 Firmware Update 0.0.0 3.3.0 -- -- 04/15/2018 01:24 AM

Config main system CC 9 Limited: Lower Battery Voltage 52.8 0 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 9 Limited: Upper Battery Voltage 64.4 0 VDC On-Site 04/15/2018 01:24 AM

Config main system INV 1 Mini Grid Connect to Grid 0 48 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 9 Disconnect < 54.4 0 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 8 Hysteresis Time ON 1 0 Minutes On-Site 04/15/2018 01:24 AM

Config main system CC 8 Wakeup VOC Change 0 6 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 8 Disconnect < 0 48 VDC On-Site 04/15/2018 01:24 AM

Config main system INV 1 Re-Bulk Voltage 0 47.6 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 8 Battery Temp Comp Range Limited Wide -- On-Site 04/15/2018 01:24 AM

Config main system CC 8 Absorb Voltage 0 58.8 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 9 Wakeup Interval 5 0 Minutes On-Site 04/15/2018 01:24 AM

Config main system CC 9 Re-Connect > 57.6 0 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 8 Hysteresis Time OFF 1 0 Minutes On-Site 04/15/2018 01:24 AM

Config main system CC 9 Enable Voltage > 140 0 VDC On-Site 04/15/2018 01:24 AM

Config main system INV 1 Grid Input Voltage Calibrate 8 -1 CF On-Site 04/15/2018 01:24 AM

Config main system CC 8 Disconnect < 0 48 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 8 Aux Status Auto Off -- On-Site 04/15/2018 01:24 AM

Config main system CC 9 Limited: Lower Battery Voltage 52.8 0 VDC On-Site 04/15/2018 01:24 AM

Config main system INV 1 Gen Input Voltage Calibrate 8 -1 CF On-Site 04/15/2018 01:24 AM

Config main system CC 9 U-Pick VOC 77 0 Percent On-Site 04/15/2018 01:24 AM

Config main system INV 1 GSconfig EE Write Enable 0 1 -- On-Site 04/15/2018 01:24 AM

Config main system CC 9 Threshold 10 0 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 9 Absorb Voltage 58.8 0 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 8 Battery Voltage Calibrate -0.2 0 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 8 Float Voltage 0 54 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 9 Disconnect < 54.4 0 VDC On-Site 04/15/2018 01:24 AM

Config main system INV 1 Gen Input Voltage Calibrate 8 -1 CF On-Site 04/15/2018 01:24 AM

Config main system CC 8 Current Limit 0 75 ADC On-Site 04/15/2018 01:24 AM

Config main system CC 8 Threshold 0 10 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 9 Re-Bulk Voltage 48.8 0 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 8 Enable Voltage > 0 140 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 9 Current Limit 75 0 ADC On-Site 04/15/2018 01:24 AM

Config main system CC 9 Enable Voltage > 58.8 0 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 9 Re-Bulk Voltage 48.8 0 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 8 Threshold 0 10 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 9 Float Voltage 54 0 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 9 Low Battery Voltage < 46 0 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 9 Enable Voltage > 140 0 VDC On-Site 04/15/2018 01:24 AM

Config main system INV 1 Grid Zero DOD Amps 0 1.25 AAC On-Site 04/15/2018 01:24 AM

Config main system CC 9 Aux Mode Vent Fan Float -- On-Site 04/15/2018 01:24 AM

Config main system INV 1 Mini Grid Delay 0 10 Minutes On-Site 04/15/2018 01:24 AM

Config main system CC 9 EQ Voltage 62.4 0 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 9 Wakeup VOC Change 6 0 VDC On-Site 04/15/2018 01:24 AM

Config main system INV 1 Battery Voltage Calibrate -0.8 0.4 CF On-Site 04/15/2018 01:24 AM

Config main system CC 9 Wakeup VOC Change 6 0 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 8 Re-Connect > 0 57.6 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 8 Battery Temp Comp Range Limited Wide -- On-Site 04/15/2018 01:24 AM

Config main system CC 8 Aux Status Auto Off -- On-Site 04/15/2018 01:24 AM

Config main system CC 9 Wakeup Interval 5 0 Minutes On-Site 04/15/2018 01:24 AM

Config main system CC 9 Aux Mode Vent Fan Float -- On-Site 04/15/2018 01:24 AM

Config main system INV 1 AC Output Voltage Calibrate 8 -2 CF On-Site 04/15/2018 01:24 AM

Config main system CC 9 Absorb Voltage 58.8 0 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 8 Float Voltage 0 54 VDC On-Site 04/15/2018 01:24 AM

Config main system INV 1 Pulse Length 0 8 Cycles On-Site 04/15/2018 01:24 AM

Config main system INV 1 Grid Zero DOD Amps 0 1.25 AAC On-Site 04/15/2018 01:24 AM

Config main system INV 1 Search Sensitivity 0 10 -- On-Site 04/15/2018 01:24 AM

Config main system CC 9 Re-Connect > 57.6 0 VDC On-Site 04/15/2018 01:24 AM

Config main system INV 1 Pulse Spacing 0 60 Cycles On-Site 04/15/2018 01:24 AM

Config main system INV 1 Battery Voltage Calibrate -0.8 0.4 CF On-Site 04/15/2018 01:24 AM

Config main system CC 8 Re-Bulk Voltage 0 48.8 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 8 Current Limit 0 75 ADC On-Site 04/15/2018 01:24 AM

Config main system CC 8 Re-Connect > 0 57.6 VDC On-Site 04/15/2018 01:24 AM

Config main system INV 1 GSconfig EE Write Enable 0 1 -- On-Site 04/15/2018 01:24 AM

Config main system CC 9 Current Limit 75 0 ADC On-Site 04/15/2018 01:24 AM

Config main system CC 8 EQ Voltage 0 62.4 VDC On-Site 04/15/2018 01:24 AM

Config main system INV 1 AC Output Voltage Calibrate 8 -2 CF On-Site 04/15/2018 01:24 AM

Config main system CC 8 Hysteresis Time ON 1 0 Minutes On-Site 04/15/2018 01:24 AM

Config main system CC 8 Re-Bulk Voltage 0 48.8 VDC On-Site 04/15/2018 01:24 AM

Config main system INV 1 Pulse Length 0 8 Cycles On-Site 04/15/2018 01:24 AM

Config main system CC 9 U-Pick VOC 77 0 Percent On-Site 04/15/2018 01:24 AM

Config main system CC 9 Float Voltage 54 0 VDC On-Site 04/15/2018 01:24 AM

Config main system COMM M Sell Current Limit 0 30 AAC On-Site 04/15/2018 01:24 AM

Config main system INV 1 Grid Zero DOD Volts 0 48 VDC On-Site 04/15/2018 01:24 AM

Config main system INV 1 Mini Grid Connect to Grid 0 48 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 8 Enable Voltage > 0 58.8 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 9 Threshold 10 0 VDC On-Site 04/15/2018 01:24 AM

Config main system INV 1 Grid Zero DOD Volts 0 48 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 9 Limited: Upper Battery Voltage 64.4 0 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 9 Hold 00:00:00 00:00:00 hh:mm:ss On-Site 04/15/2018 01:24 AM

Config main system INV 1 Mini Grid Delay 0 10 Minutes On-Site 04/15/2018 01:24 AM

Config main system CC 8 Wakeup VOC Change 0 6 VDC On-Site 04/15/2018 01:24 AM

Config main system INV 1 Pulse Spacing 0 60 Cycles On-Site 04/15/2018 01:24 AM

Config main system INV 1 Re-Bulk Voltage 0 47.6 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 8 Enable Voltage > 0 140 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 9 Hold 00:00:00 00:00:00 hh:mm:ss On-Site 04/15/2018 01:24 AM

Config main system CC 8 ON Time 4 0 Hours On-Site 04/15/2018 01:24 AM

Config main system CC 8 Battery Voltage Calibrate -0.2 0 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 9 Enable Voltage > 58.8 0 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 8 EQ Voltage 0 62.4 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 9 Low Battery Voltage < 46 0 VDC On-Site 04/15/2018 01:24 AM

Config main system INV 1 Search Sensitivity 0 10 -- On-Site 04/15/2018 01:24 AM

Config main system CC 8 Absorb Voltage 0 58.8 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 8 ON Time 4 0 Hours On-Site 04/15/2018 01:24 AM

Config main system CC 8 Enable Voltage > 0 58.8 VDC On-Site 04/15/2018 01:24 AM

Config main system INV 1 Grid Input Voltage Calibrate 8 -1 CF On-Site 04/15/2018 01:24 AM

Config main system CC 9 EQ Voltage 62.4 0 VDC On-Site 04/15/2018 01:24 AM

Config main system CC 8 Hysteresis Time OFF 1 0 Minutes On-Site 04/15/2018 01:24 AM

Config main system INV 1 AUX Relay OFF Delay 0 0.5 Minutes On-Site 04/15/2018 01:21 AM

Config main system CC 8 Disconnect < 48 0 VDC On-Site 04/15/2018 01:21 AM

Config main system INV 1 AUX ON Delay 0 0.5 Minutes On-Site 04/15/2018 01:21 AM

Config main system CC 8 Enable Voltage > 58.8 0 VDC On-Site 04/15/2018 01:21 AM

Config main system CC 8 Enable Voltage > 140 0 VDC On-Site 04/15/2018 01:21 AM

Config main system INV 1 AUX OFF Delay 0 5 Minutes On-Site 04/15/2018 01:21 AM

Config main system CC 8 EQ Voltage 62.4 0 VDC On-Site 04/15/2018 01:21 AM

Config main system INV 1 AUX Relay ON Delay 0 0.5 Minutes On-Site 04/15/2018 01:21 AM

Config main system INV 1 Relay Mode 0 Gen Alert -- On-Site 04/15/2018 01:21 AM

Config main system CC 8 Wakeup VOC Change 6 0 VDC On-Site 04/15/2018 01:21 AM

Config main system CC 8 Re-Bulk Voltage 48.8 0 VDC On-Site 04/15/2018 01:21 AM

Config main system CC 8 Re-Connect > 57.6 0 VDC On-Site 04/15/2018 01:21 AM

Status main system CC 8 Firmware Update 3.3.0 0.0.0 -- -- 04/15/2018 01:18 AM

Status main system CC 8 Firmware Update 3.3.0 0.0.0 -- -- 04/15/2018 01:18 AM

Config main system INV 1 AUX OFF Delay 5 0 Minutes On-Site 04/15/2018 01:18 AM

Config main system CC 8 Float Voltage 54 0 VDC On-Site 04/15/2018 01:18 AM

Config main system INV 1 GSconfig EE Write Enable 1 0 -- On-Site 04/15/2018 01:18 AM

Config main system INV 1 Relay Mode Gen Alert 0 -- On-Site 04/15/2018 01:18 AM

Config main system INV 1 Search Sensitivity 10 0 -- On-Site 04/15/2018 01:18 AM

Config main system INV 1 Battery Voltage Calibrate 0.4 -0.8 CF On-Site 04/15/2018 01:18 AM

Config main system CC 8 Absorb Voltage 58.8 0 VDC On-Site 04/15/2018 01:18 AM

Config main system INV 1 Mini Grid Connect to Grid 48 0 VDC On-Site 04/15/2018 01:18 AM

Config main system INV 1 AC Output Voltage Calibrate -2 8 CF On-Site 04/15/2018 01:18 AM

Config main system INV 1 Relay Mode Gen Alert 0 -- On-Site 04/15/2018 01:18 AM

Config main system INV 1 Battery Voltage Calibrate 0.4 -0.8 CF On-Site 04/15/2018 01:18 AM

Config main system INV 1 Gen Input Voltage Calibrate -1 8 CF On-Site 04/15/2018 01:18 AM

Config main system INV 1 Mini Grid Delay 10 0 Minutes On-Site 04/15/2018 01:18 AM

Config main system INV 1 Pulse Length 8 0 Cycles On-Site 04/15/2018 01:18 AM

Config main system INV 1 Re-Bulk Voltage 47.6 0 VDC On-Site 04/15/2018 01:18 AM

Config main system INV 1 AUX Relay ON Delay 0.5 0 Minutes On-Site 04/15/2018 01:18 AM

Config main system INV 1 Mini Grid Delay 10 0 Minutes On-Site 04/15/2018 01:18 AM

Config main system INV 1 Grid Input Voltage Calibrate -1 8 CF On-Site 04/15/2018 01:18 AM

Config main system INV 1 Search Sensitivity 10 0 -- On-Site 04/15/2018 01:18 AM

Config main system COMM M Sell Current Limit 30 0 AAC On-Site 04/15/2018 01:18 AM

Config main system INV 1 AUX ON Delay 0.5 0 Minutes On-Site 04/15/2018 01:18 AM

Config main system INV 1 AC Output Voltage Calibrate -2 8 CF On-Site 04/15/2018 01:18 AM

Config main system INV 1 AUX ON Delay 0.5 0 Minutes On-Site 04/15/2018 01:18 AM

Config main system CC 8 Threshold 10 0 VDC On-Site 04/15/2018 01:18 AM

Config main system INV 1 Grid Zero DOD Volts 48 0 VDC On-Site 04/15/2018 01:18 AM

Config main system INV 1 Gen Input Voltage Calibrate -1 8 CF On-Site 04/15/2018 01:18 AM

Config main system INV 1 Grid Zero DOD Amps 1.25 0 AAC On-Site 04/15/2018 01:18 AM

Config main system INV 1 Mini Grid Connect to Grid 48 0 VDC On-Site 04/15/2018 01:18 AM

Config main system INV 1 AUX Relay ON Delay 0.5 0 Minutes On-Site 04/15/2018 01:18 AM

Config main system INV 1 AUX Relay OFF Delay 0.5 0 Minutes On-Site 04/15/2018 01:18 AM

Config main system CC 8 Float Voltage 54 0 VDC On-Site 04/15/2018 01:18 AM

Config main system INV 1 Pulse Length 8 0 Cycles On-Site 04/15/2018 01:18 AM

Config main system CC 8 Current Limit 75 0 ADC On-Site 04/15/2018 01:18 AM

Config main system INV 1 Pulse Spacing 60 0 Cycles On-Site 04/15/2018 01:18 AM

Config main system INV 1 Grid Zero DOD Volts 48 0 VDC On-Site 04/15/2018 01:18 AM

Config main system INV 1 AUX Relay OFF Delay 0.5 0 Minutes On-Site 04/15/2018 01:18 AM

Config main system INV 1 Pulse Spacing 60 0 Cycles On-Site 04/15/2018 01:18 AM

Config main system INV 1 Grid Input Voltage Calibrate -1 8 CF On-Site 04/15/2018 01:18 AM

Config main system INV 1 Grid Zero DOD Amps 1.25 0 AAC On-Site 04/15/2018 01:18 AM

Config main system CC 8 Current Limit 75 0 ADC On-Site 04/15/2018 01:18 AM

Config main system INV 1 Re-Bulk Voltage 47.6 0 VDC On-Site 04/15/2018 01:18 AM

Config main system INV 1 GSconfig EE Write Enable 1 0 -- On-Site 04/15/2018 01:18 AM

Config main system CC 8 Absorb Voltage 58.8 0 VDC On-Site 04/15/2018 01:18 AM

Config main system INV 1 AUX OFF Delay 5 0 Minutes On-Site 04/15/2018 01:18 AM

Config main system CC 8 Threshold 10 0 VDC On-Site 04/15/2018 01:18 AM

Status main system CC 9 Firmware Update 0.0.0 3.3.0 -- -- 04/15/2018 01:12 AM

Config main system CC 9 Threshold 0 10 VDC On-Site 04/15/2018 01:12 AM

Config main system CC 9 Re-Bulk Voltage 0 48.8 VDC On-Site 04/15/2018 01:12 AM

Config main system CC 8 Battery Voltage Calibrate 0 -0.2 VDC On-Site 04/15/2018 01:12 AM

Config main system CC 9 Disconnect < 0 54.4 VDC On-Site 04/15/2018 01:12 AM

Config main system CC 9 Enable Voltage > 0 58.8 VDC On-Site 04/15/2018 01:12 AM

Config main system CC 8 Aux Status Off Auto -- On-Site 04/15/2018 01:12 AM

Config main system CC 8 Battery Temp Comp Range Wide Limited -- On-Site 04/15/2018 01:12 AM

Config main system CC 8 ON Time 0 4 Hours On-Site 04/15/2018 01:12 AM

Config main system CC 9 Re-Connect > 0 57.6 VDC On-Site 04/15/2018 01:12 AM

Config main system CC 9 Enable Voltage > 0 140 VDC On-Site 04/15/2018 01:12 AM

Config main system CC 9 Wakeup VOC Change 0 6 VDC On-Site 04/15/2018 01:12 AM

Config main system CC 8 Hysteresis Time OFF 0 1 Minutes On-Site 04/15/2018 01:12 AM

Config main system CC 9 Current Limit 0 75 ADC On-Site 04/15/2018 01:12 AM

Config main system CC 9 EQ Voltage 0 62.4 VDC On-Site 04/15/2018 01:12 AM

Config main system CC 9 Absorb Voltage 0 58.8 VDC On-Site 04/15/2018 01:12 AM

Config main system CC 9 Float Voltage 0 54 VDC On-Site 04/15/2018 01:12 AM

Config main system CC 8 Hysteresis Time ON 0 1 Minutes On-Site 04/15/2018 01:12 AM

Status main system CC 9 Firmware Update 3.3.0 0.0.0 -- -- 04/15/2018 01:09 AM

Status main system CC 9 Firmware Update 3.3.0 0.0.0 -- -- 04/15/2018 01:09 AM

Config main system CC 8 ON Time 4 0 Hours On-Site 04/15/2018 01:09 AM

Config main system CC 9 Wakeup VOC Change 6 0 VDC On-Site 04/15/2018 01:09 AM

Config main system CC 8 Hysteresis Time OFF 1 0 Minutes On-Site 04/15/2018 01:09 AM

Config main system CC 9 Absorb Voltage 58.8 0 VDC On-Site 04/15/2018 01:09 AM

Config main system CC 9 Re-Connect > 57.6 0 VDC On-Site 04/15/2018 01:09 AM

Config main system CC 9 Disconnect < 54.4 0 VDC On-Site 04/15/2018 01:09 AM

Config main system CC 9 EQ Voltage 62.4 0 VDC On-Site 04/15/2018 01:09 AM

Config main system CC 9 Wakeup VOC Change 6 0 VDC On-Site 04/15/2018 01:09 AM

Config main system CC 9 Enable Voltage > 58.8 0 VDC On-Site 04/15/2018 01:09 AM

Config main system CC 8 Battery Temp Comp Range Limited Wide -- On-Site 04/15/2018 01:09 AM

Config main system CC 8 Hysteresis Time OFF 1 0 Minutes On-Site 04/15/2018 01:09 AM

Config main system CC 9 Enable Voltage > 140 0 VDC On-Site 04/15/2018 01:09 AM

Config main system CC 9 Float Voltage 54 0 VDC On-Site 04/15/2018 01:09 AM

Config main system CC 8 Battery Temp Comp Range Limited Wide -- On-Site 04/15/2018 01:09 AM

Config main system CC 9 Float Voltage 54 0 VDC On-Site 04/15/2018 01:09 AM

Config main system CC 9 Threshold 10 0 VDC On-Site 04/15/2018 01:09 AM

Config main system CC 9 Current Limit 75 0 ADC On-Site 04/15/2018 01:09 AM

Config main system CC 8 Battery Voltage Calibrate -0.2 0 VDC On-Site 04/15/2018 01:09 AM

Config main system CC 8 Battery Voltage Calibrate -0.2 0 VDC On-Site 04/15/2018 01:09 AM

Config main system CC 9 EQ Voltage 62.4 0 VDC On-Site 04/15/2018 01:09 AM

Config main system CC 8 Hysteresis Time ON 1 0 Minutes On-Site 04/15/2018 01:09 AM

Config main system CC 9 Disconnect < 54.4 0 VDC On-Site 04/15/2018 01:09 AM

Config main system CC 9 Re-Bulk Voltage 48.8 0 VDC On-Site 04/15/2018 01:09 AM

Config main system CC 9 Threshold 10 0 VDC On-Site 04/15/2018 01:09 AM

Config main system CC 9 Enable Voltage > 140 0 VDC On-Site 04/15/2018 01:09 AM

Config main system CC 8 ON Time 4 0 Hours On-Site 04/15/2018 01:09 AM

Config main system CC 8 Aux Status Auto Off -- On-Site 04/15/2018 01:09 AM

Config main system CC 9 Re-Connect > 57.6 0 VDC On-Site 04/15/2018 01:09 AM

Config main system CC 9 Absorb Voltage 58.8 0 VDC On-Site 04/15/2018 01:09 AM

Config main system CC 8 Aux Status Auto Off -- On-Site 04/15/2018 01:09 AM

Config main system CC 8 Hysteresis Time ON 1 0 Minutes On-Site 04/15/2018 01:09 AM

Config main system CC 9 Re-Bulk Voltage 48.8 0 VDC On-Site 04/15/2018 01:09 AM

Config main system CC 9 Enable Voltage > 58.8 0 VDC On-Site 04/15/2018 01:09 AM

Config main system CC 9 Current Limit 75 0 ADC On-Site 04/15/2018 01:09 AM
User avatar
Megunticook
Forum Virtuoso
 
Posts: 94
Joined: Fri Sep 29, 2017 4:08 am
Location: Maine
My RE system: 6.4 kW solar array (21 QCell 305 panels in strings of 3)
GS8048A FLEXpower Radian (Radian 8048A, 2 FlexMax 80 cc's, Mate 3s, FlexNet DC, Hub)
8x6v Rolls-Surette 550 FLA batteries, 428AH

Re: strange behavior overnight

Postby Greg T Fordan on Mon Apr 16, 2018 2:31 pm

Megunticook wrote:When I looked at the Event History in Optics, I saw a massive amount of activity after midnight, but can't make heads or tails of it. What exactly happened? Did some sort of update get pushed down from the server?


Hi Megunticook,
There were no updates that were recently pushed to the server. We've seen some systems that behave similar to what happened to your system, where the configuration values are cycling back and forth from a good number to zero. The upcoming MATE3s FW update should be able too address that issue.
Greg T Fordan
EngTech
Outback Power Technologies
User avatar
Greg T Fordan
OutBack Technical Service
 
Posts: 58
Joined: Fri Dec 29, 2017 2:56 pm
My RE system: Radian, FM80, FNDC, 48V batt bank


Return to Mate3 / Mate3s

Who is online

Users browsing this forum: No registered users and 2 guests