Mate 3s not saving configuration.

Mate3 and Mate3s communications devices for Outback Power
Post Reply
marckeez
Forum Junior Member
Posts: 4
Joined: Thu Jun 11, 2020 7:51 am
My RE system: VFXR3648A with a Flex Max 80 Mate 3s, FlexNet DC, all came pre-wired from Wholesale solar. Batteries are Fullriver 6 VDC in a 48 VDC bank. Solar panels are Astronegy 280watt and have a total of 12 for 3360 total watts using a Outback combiner with Rapid shut-down UL1741.

Mate 3s not saving configuration.

Post by marckeez » Wed Jun 24, 2020 12:39 pm

My system is set up to sell-back to the grid. I setup all parameters to sell to grid and then save the current configuration and the Grid sell Off-set keeps going back to N (no off-set) which does not turn the inverter on to sell to grid. I have changed this several times now to Y (Yes for off-set) and save config. Off-set is set to 1V less than Float. Please help. Thx...
Last edited by marckeez on Thu Jun 25, 2020 10:14 am, edited 1 time in total.

Mike Curran
Forum Emperor
Posts: 1586
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 repl'd MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied GVFX3524's classic stacked for 120/240VAC (2007)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied, no longer AC- coupled

Outback Skybox - Barn roof: (2019)
- 14 (2x7) Talesun 275W (DC array input to SB charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 modules

All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: Mate 3s not saving configuration.

Post by Mike Curran » Wed Jun 24, 2020 3:59 pm

Do you have your charge controller set to enable grid-tie mode? This can be done thru the Mate3:
Screenshot_20200624-185654_Adobe Acrobat.jpg
Also note, offset is not a programmable function per the 8048 manual:
Screenshot_20200624-190720_Adobe Acrobat.jpg
http://www.tigoenergy.com/site.php?95b2dca2-ca6c
https://enlighten.enphaseenergy.com/public/systems/Hctc107221

marckeez
Forum Junior Member
Posts: 4
Joined: Thu Jun 11, 2020 7:51 am
My RE system: VFXR3648A with a Flex Max 80 Mate 3s, FlexNet DC, all came pre-wired from Wholesale solar. Batteries are Fullriver 6 VDC in a 48 VDC bank. Solar panels are Astronegy 280watt and have a total of 12 for 3360 total watts using a Outback combiner with Rapid shut-down UL1741.

Re: Mate 3s not saving configuration.

Post by marckeez » Wed Jun 24, 2020 6:50 pm

I had my VFXR 3648 A set to grid mode and manually set the charge controller to GT mode (as instructed in a vendor video) but they both reverted back to non Grid Tied mode. Just reset both to Grid Tied mode and did a save. I recently had a issue with bad cable and system was not getting a good PV connection to the charge controller. I replaced a cable and GFI breaker and needed to totally power down the system. This may be why the off-set was not saved. Does the VFXR 3648 A not save the off-set like the Radian?

Mike Curran
Forum Emperor
Posts: 1586
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 repl'd MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied GVFX3524's classic stacked for 120/240VAC (2007)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied, no longer AC- coupled

Outback Skybox - Barn roof: (2019)
- 14 (2x7) Talesun 275W (DC array input to SB charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 modules

All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: Mate 3s not saving configuration.

Post by Mike Curran » Thu Jun 25, 2020 4:09 am

Sorry, thought you had a Radian, but in any case offset is not programmable for a VFXR either.
Screenshot_20200625-070502_Adobe Acrobat.jpg
I am not an expert on offset but just from reading the manual, the important thing to note is that your inverter will go into and leave "offset" operation depending on what's happening with your system at the time. You cannot set it and expect it to stay enabled.
http://www.tigoenergy.com/site.php?95b2dca2-ca6c
https://enlighten.enphaseenergy.com/public/systems/Hctc107221