Postby jeffminsc on Fri May 19, 2017 8:58 am

I have my system connected to Optics RE but can not for the life of me figure out how to connect directly to the mate 3. What am I missing. or can I not do that?
jeffminsc
Junior Member
 
Posts: 2
Joined: Mon May 15, 2017 1:04 am
My RE system: 4 flexmax 80 charge controlers
1 mate 3
1 flex net dc
1 VFXR2812A inverter

Re: Connect to Mate 3

Postby Mike Curran on Fri May 19, 2017 4:37 pm

In OpticsRE dashboard click on "Device map" then click on "Gateway device Mate3" at the right side of the screen above your other numbered device icons.

Hope this helps.
Mike Curran
OutBack Guru
 
Posts: 370
Joined: Sat Aug 28, 2004 6:28 pm
Location: Chagrin Falls, Ohio
My RE system: Outback:
- 8 (2x4) Evergreen 180's into one MX60
- 6 (2×3) ALEO S79-300's into one FM80
- 2 grid-tied GVFX3524's classic stacked for 120/240VAC
- 12 Surrette/Rolls 2V x 1766Ah
- Hub10.3, Mate3, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.

Westinghouse Solar:
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied.

Re: Connect to Mate 3

Postby jeffminsc on Mon May 22, 2017 6:30 am

Guess I was not clear in my description. I would like to hook up to my system with out going through Optic Re. I thought there was a way to have a network without going through the internet. Thanks for the reply.
jeffminsc
Junior Member
 
Posts: 2
Joined: Mon May 15, 2017 1:04 am
My RE system: 4 flexmax 80 charge controlers
1 mate 3
1 flex net dc
1 VFXR2812A inverter

Re: Connect to Mate 3

Postby OffgridHiker on Mon May 22, 2017 4:19 pm

Enter your MATE3 local IP address while on your local network and you should see a web page.
OffgridHiker
OutBack Whiz
 
Posts: 33
Joined: Fri Nov 18, 2016 6:12 pm
My RE system: Offgrid, 48V

2x VFX3648 (AC Generator)
FX60 (1980W Solar)
FM60 (2475W Solar)
FNDC
MATE3
HUB10

Re: Connect to Mate 3

Postby EMCF on Thu May 25, 2017 1:00 pm

Here's your detailed procedure:
1. Connect your power cable and ethernet cable to the back of MATE3 (they are both Cat5 cables)
2. Navigate to Ethernet address screen. Lock>141>Settings>System>Ethernet Addresses
3. Ensure DHCP is set as Enabled
5. Press UP button once.
6. Power cycle MATE3 (unplug and replug power cable)
7. Wait for about 60 seconds, then press PORT button. On the very top you will see an IP address.
8. Enter that IP address in your browser. Do not enter the zeros in front of the number. Ex. 192.168.001.064 should be entered as 192.168.1.64. Press Enter on your PC keyboard
9. Now you should have the Outback web page getting populated on your screen. Remember that this is a monitor only page. No control function. (We wish!)
EMCF
OutBack Expert
 
Posts: 57
Joined: Thu Jul 21, 2016 10:22 am
My RE system: FX3048, 4 200a batteries, FM60. 3 kw array

Re: Connect to Mate 3

Postby foo on Thu May 25, 2017 5:41 pm

Thanks for posting these instructions.
I didn't power cycle and wait the 60 seconds after enabling the DHCP.

I'm going to try that now. Keeping my fingers crossed...
foo
OutBack Whiz
 
Posts: 44
Joined: Thu Jun 30, 2016 1:25 pm
My RE system: VFXR3524A Inverter
3.5kW Solar Array @48V
24V Battery Bank - 210AH (4x105AH @12V) -FLA
Mate3
Renogy Tracer 4210 40 Amp MPPT Charge Controllers x 3, 12/24V 100VDC Input
Outback Power FLEXmax FM80 MPPT Solar Charge Controller

Re: Connect to Mate 3

Postby foo on Thu May 25, 2017 6:53 pm

No difference.

Port button still doesn't do anything at the main screen.

Also, the port light still fades off as if it is losing power. I wanted this to work so badly...

Everything else is perfect, I hate having to send the unit back.
foo
OutBack Whiz
 
Posts: 44
Joined: Thu Jun 30, 2016 1:25 pm
My RE system: VFXR3524A Inverter
3.5kW Solar Array @48V
24V Battery Bank - 210AH (4x105AH @12V) -FLA
Mate3
Renogy Tracer 4210 40 Amp MPPT Charge Controllers x 3, 12/24V 100VDC Input
Outback Power FLEXmax FM80 MPPT Solar Charge Controller

Re: Connect to Mate 3

Postby EMCF on Fri May 26, 2017 6:40 am

Time to call Tech Support for RMA. That is hardware problem on your MATE3.