Inconsistent Ground-Fault Detector Interuptor Wiring Diagram

Discussion about the Power System DC Disconnect (PSDC)

Moderators: OutBack Moderator Team, OutBack

Post Reply
ttpiper
Forum Whiz
Posts: 25
Joined: Fri Jul 23, 2010 7:47 am
My RE system: Off-grid, dual VFX3648, FM60 CC, 12 - 240W panels, 8 Trojan L16H-AC (435 A-hr @ 20 hr rate) in one series string (48 VDC). FNDC with LI,L2,CC Shunts. Mate3 with USB interface. 10KW Generac standby generator
Location: Bridgton, Maine

Inconsistent Ground-Fault Detector Interuptor Wiring Diagram

Post by ttpiper » Wed Nov 17, 2010 9:51 am

The Outback wiring diagram for a dual inverter configuration, which is available on the Outback website, shows the GFDI wired between the PV array and the Charge Controller. The GFDI installation instructions shows the unit wired between the Charge Controller and the Battery Bank. Anyone know which is the correct configuration?

SHerrera

Re: Inconsistent Ground-Fault Detector Interuptor Wiring Diagram

Post by SHerrera » Wed Nov 17, 2010 10:33 am

Sorry about the confusion.
The wiring diagram posted on our website is for are older product GFP.
The new product is the GFDI, and it should be installed between controller and batteries.
The instructions on the GFDI manual is correct.