I wanted to verify that this is correct since I am installing my new batteries.. It is a 48V battery bank.

I am pairing 2/0 copper from the battery bank back to the PSDC. The positive cables will be connected via 2 lugs to the 175A breaker for the 3648 inverter. From the 175A breaker I need to connect a cable back to the DC positive bus bar. Question is what size should this cable be? DC positive bus bar can take up to 1/0.. and I have left over 1/0.. perhaps I should just use that.. :smile:

I originally thought with 3 lugs on the breaker I would have to deal with cables going in three orthogonal directions but it looks like I can simply flip one upside down so they can stack one on top of the other and only have 2 different directions..

Have to say again how nice it is to have studs on the breakers!

User avatar
mvrck
Forum Czar
Posts: 615
Joined: Mon Oct 17, 2005 10:03 am
My RE system: 3.1 kW (BP 60W) on 2x MX60s
560W (Kaneka 60W) on 1 Classic 150
1080W (Day4) on 1 Tristar MPPT 60
GVFX3524 + PS2AC/DC, MATE, HUB4, Charles 24V 30A Charger, Generac S4001, Trimetric 2020, WattPlot, greenMonitor Lite, 400AH Bank (4 ea Rolls Surrette S530 Batteries), and a lot of other solar refuse...
Location: Austin, Texas
Contact:

Post by mvrck » Wed Nov 01, 2006 1:11 pm

The size should match the current requirements of the items connected the positive bus, like MX60s, etc...

If the 1/0 is the proper type like THWN-2 and you have a good lug for it to bolt onto the buss plate, then let 'er rip...

Thanks
Maverick
 