Resizing PV Array for 3 FM80s

Postby domatic on Wed Sep 13, 2017 12:46 pm

Just got off the phone with Tech Support after 2 blown fans (2 years of use) it appears we are over working our 2 FM80's one showed 5600 watts and other 4500 watts. We originally spec for 33 x 250 watt panels but due to a stock issue we were given 33 x 300 watts. Now it seems that we need to add another FM80 to handle it due to constant fan use.

Our current string setup =

Fm80/1- 3 x LG300 in series parallel of 5
Fm80/2 - 3 x LG300 in series parallel of 6

What would be optimal setup for 3 FM80's

Being new to PV My guess is =

Fm80/1- 3 x LG300 in series parallel of 4
Fm80/2 - 3 x LG300 in series parallel of 4
Fm80/3 - 3 x LG300 in series parallel of 3

Any suggestions, are greatly appreciated.
Luke
domatic
Member
 
Posts: 21
Joined: Wed Oct 14, 2015 7:02 am
My RE system: OFF GRID - 33 x 300w LG Mono Radian 7048 @ 240v 60hz Single Phase - GS Load Center - 2 x Flexmax 80 - Mate3 - 8 x Trojan Industrial IND17 @ 48V, 960 AH - Honda eu6500is on Atkinson MINI-i controller.

Re: Resizing PV Array for 3 FM80s

Postby jguzman on Thu Sep 14, 2017 8:27 am

Luke,

Have you tried OB's string Sizing tool?
http://outbackpower.com/outback-support ... izing-tool
Jorge Guzman
Technical Support Supervisor


Watch easy to follow video tutorials:
https://www.youtube.com/c/wattschool
jguzman
Applications Engineering
 
Posts: 143
Joined: Thu May 29, 2014 9:44 am
Location: Arlington, WA
My RE system: GVFX3524, FM80, MATE3. 3x 260W REC. 4x Trojan L16 FLA 370Ah.