Discussion about the FM100, FM80, and FM60 Charge Controllers

Moderators: OutBack, OutBack Moderator Team

Charge paramters for Hawker FLA Batteries

Postby cgerke on Thu Mar 14, 2019 6:13 am

I am helping a friend setup a Radian system with FM80s CC, FNDC, Mate3s. He has Hawker FLA 2 Volt Batteries that are about 3 years old. I can not find what I consider reliable charging info. Currently, I have the CC set as follows: Absorb - 59V, 3 hours ; Float - 53.8, Eq. - 61 volts, 2 hours. The 8048 inverter is set slightly lower in volts. Any comments or guidance is appreciated.
cgerke
Forum Member
 
Posts: 11
Joined: Fri Jan 04, 2019 5:49 am
Location: Guanaja, Bay Islands, Honduras
My RE system: Radian GS8048A-300v panel. 2 FM-100s, 8KW solar, 12 KW diesel Gen, Flexnet DC and Mate 3. 6-SimpliPhi 3.5 LFP batteries.

Re: Charge paramters for Hawker FLA Batteries

Postby Kurt Lundquist on Thu Mar 14, 2019 7:47 am

Does the battery have a label that shows the model number? Sometimes the label has charging info but typically it is in volts per cell (Vpc) and it isn't always geared around a cycling application.

What is the size of the battery bank?

How much power does he have for charging?

The initial settings you posted seem ok but I would maybe bump Absorb up to 4 hours. Keep an eye on water consumption and specific gravities to help guide future tweaks to the charge parameters.

-Kurt
Kurt Lundquist
Renewable Energy Project Engineer
http://alphaenergy.us/
User avatar
Kurt Lundquist
Alpha Energy Engineering
 
Posts: 1242
Joined: Tue May 31, 2011 7:23 am
Location: Arlington, WA
My RE system: VFX3524, Mate3, 200Ah 24V AGM Battery Bank

Re: Charge paramters for Hawker FLA Batteries

Postby cgerke on Thu Mar 14, 2019 10:21 am

The only markings I can find are heat stamped on the top of the battery : "N28BJ" but nothing Googles. The size of the battery indicates that it is in the 600 AH range (just guessing) . The system has 48 batteries in 2 banks of 24, so 1200AH at 48Volts. The system has 3 Flexmax 80s with 27 ea x 305 watt panels (8200 watts approx). The system is "Laguna". You recently replied to a different post concerning "Bypass Mode". I will adjust the Absorb. parameters accordingly. Thanks for the help.
cgerke
Forum Member
 
Posts: 11
Joined: Fri Jan 04, 2019 5:49 am
Location: Guanaja, Bay Islands, Honduras
My RE system: Radian GS8048A-300v panel. 2 FM-100s, 8KW solar, 12 KW diesel Gen, Flexnet DC and Mate 3. 6-SimpliPhi 3.5 LFP batteries.