Flexmax 80 Chargers front panel info

Post by mrt » Wed Jan 30, 2019 9:24 am

Good day all.
This is my first posting to this forum and I thank you for accepting my membership.
I have 2 Flexmax 80 chargers connected to my 48v batteries communicating via the hub. One of the chargers was replaced yesterday by a new unit due to lightning damage. The charger that was from the original setup is showing EQ (Equalising) on the front screen all the time whereas the newly replaced charger is showing Bulk all the time. Is this correct and/or acceptable?

bluespur
Forum Expert
Posts: 68
Joined: Wed Feb 23, 2011 2:32 pm
My RE system: VFX3024x2
Flexmax60x2
3000W total solar, 135w panel array and 220w panel array
Mate3
12xHawker Perfect Plus 8PZS120 FLA batteries
Own built generator Kubota D600 engine, 7.5Kw gen head

Re: Flexmax 80 Chargers front panel info

Post by bluespur » Thu Jan 31, 2019 1:29 pm

You should validate that all settings are the same between the 2 controllers, it sounds like your earlier one may have had changes from the default, and the new not. Also, you should ensure the controller voltage is correctly calibrated.
Cheers
Garth

mrt
Forum Whiz
Posts: 29
Joined: Wed Jan 30, 2019 9:12 am
My RE system: 2 x Outback GVFX 3048E Inverters
2 x Outback Flexmax - 80 battery controllers
1 x Outback Hub
1 x Victron BMV - 600s Battery Monitor
36 x 230 w solar panels
24 x 2v 2170 Ah C100 Hoppecke 12OPZS Deep Cycle batteries
Location: Hoedspruit, South Africa
Contact:

Re: Flexmax 80 Chargers front panel info

Post by mrt » Sat Feb 02, 2019 3:24 am

Thanks Garth.
I forced a Bulk action on the charger and now both chargers are in bulk mode and working perfectly.

Cheers :smile: :grin:

petertearai
Forum Guru
Posts: 397
Joined: Fri Aug 06, 2010 4:35 pm
My RE system: 2220 watt pv, fm80, outback fxr 2000 watt inverter. Shoto 12 times 2 volt exc400 lead carbon batterys 24 volt system victron battery moniter. optics RE
Location: NewZealand North Island

Re: Flexmax 80 Chargers front panel info

Post by petertearai » Sun Feb 03, 2019 11:09 pm

still a good idea to go through all the settings and get them the same . The EQ setting should not be on unless it has been set to auto EQ , or you have asked it to EQ .
In my opinion best not to have auto eq set .
2220 pv. fm80. 12 times 2 volt exc shoto lead carbon 450 AH 24 volts. victron battery monitor. outback fxr 2000 watt inverter

mrt
Forum Whiz
Posts: 29
Joined: Wed Jan 30, 2019 9:12 am
My RE system: 2 x Outback GVFX 3048E Inverters
2 x Outback Flexmax - 80 battery controllers
1 x Outback Hub
1 x Victron BMV - 600s Battery Monitor
36 x 230 w solar panels
24 x 2v 2170 Ah C100 Hoppecke 12OPZS Deep Cycle batteries
Location: Hoedspruit, South Africa
Contact:

Re: Flexmax 80 Chargers front panel info

Post by mrt » Sun Feb 03, 2019 11:44 pm

Thanks petertearai

I have set both chargers the same and the equalisation is set to auto. After consideration I agree with you - best not to set the chargers to auto equalisation due to equalisation automatically starting even with heavy DC loads. The battery water will have to be monitored also and maybe the equalisation takes place when I am not there. I will set the chargers for manual equalisation.