Charge Controllers remains in Bulk status

Postby lrperez99 on Thu Jun 27, 2019 7:48 am

Hi,
After doing an equalization, the charge controllers are behaving weird. This morning the controllers remained in Charged status and didn't produce solar energy. I had to turn it off/on and then started to generate but the status is always in Bulk. Before the equalization the controllers initiated in bulk and the changed to Float for the rest of the day. This could be a problem with the controllers or with the PV array?

Is there a way to run a diagnostic to the charge controllers?
Attachments
Charger1.pdf
Chargers - status
(909.59 KiB) Downloaded 23 times
lrperez99
Forum Member
 
Posts: 13
Joined: Thu Jan 11, 2018 7:09 am
Location: Trujillo Alto, Puerto Rico
My RE system:

Re: Charge Controllers remains in Bulk status

Postby Greg T Fordan on Thu Jun 27, 2019 8:13 am

At this time your system is in a Sell status. Both of your CCs are still in the Bulk state because they have not yet reach the target Absorb voltage of 57.6. They are likely to stay that way for as long as the Selling is going on.
Greg T Fordan
EngTech
Outback Power Technologies
User avatar
Greg T Fordan
OutBack Technical Service
 
Posts: 139
Joined: Fri Dec 29, 2017 2:56 pm
My RE system:

Re: Charge Controllers remains in Bulk status

Postby lrperez99 on Thu Jun 27, 2019 8:16 am

Thanks Greg. any idea why the charger stayed in charged state and didn't started to generate until I did a restart?
lrperez99
Forum Member
 
Posts: 13
Joined: Thu Jan 11, 2018 7:09 am
Location: Trujillo Alto, Puerto Rico
My RE system:

Re: Charge Controllers remains in Bulk status

Postby Greg T Fordan on Thu Jun 27, 2019 8:49 am

Maybe, after the equalization, at that time, the battery bank voltage was at or above the Float voltage level, so CC logic says "don't do anything". When that happens and you want charging to take place, you don't have to power cycle the CC. You will lose the day's harvest record doing it that way. On the CC display, point the arrow to Misc, then click RSTRT (4th button) and charging will recommence.
Greg T Fordan
EngTech
Outback Power Technologies
User avatar
Greg T Fordan
OutBack Technical Service
 
Posts: 139
Joined: Fri Dec 29, 2017 2:56 pm
My RE system:

Re: Charge Controllers remains in Bulk status

Postby lrperez99 on Thu Jun 27, 2019 11:21 am

Thanks. What confused me was seen the battery charging from the grid (see attached jpg) ant not from the controller. Lets see how behave tomorrow. Thanks again.
Attachments
Graph.jpg
Graph
lrperez99
Forum Member
 
Posts: 13
Joined: Thu Jan 11, 2018 7:09 am
Location: Trujillo Alto, Puerto Rico
My RE system:

Re: Charge Controllers remains in Bulk status

Postby Greg T Fordan on Thu Jun 27, 2019 11:24 am

Because the Equalization process was courtesy of the Grid.
Greg T Fordan
EngTech
Outback Power Technologies
User avatar
Greg T Fordan
OutBack Technical Service
 
Posts: 139
Joined: Fri Dec 29, 2017 2:56 pm
My RE system:

Re: Charge Controllers remains in Bulk status

Postby lrperez99 on Thu Jun 27, 2019 6:45 pm

Agree, but I forgot to mention that the equalization was done yesterday around 12:30 pm. Also tonight is still charging the battery from grid (see attached file). This behavior is different compared before the equalization.
Attachments
Graph1.pdf
(230.13 KiB) Downloaded 19 times
lrperez99
Forum Member
 
Posts: 13
Joined: Thu Jan 11, 2018 7:09 am
Location: Trujillo Alto, Puerto Rico
My RE system:

Re: Charge Controllers remains in Bulk status

Postby raysun on Thu Jun 27, 2019 9:35 pm

raysun
Forum Czar
 
Posts: 634
Joined: Tue Jul 26, 2016 5:57 am
My RE system:

Re: Charge Controllers remains in Bulk status

Postby Greg T Fordan on Fri Jun 28, 2019 12:05 pm

Under the Misc tab of CC. There are 3 options on the dropdown: There is no "Now" option ;-(
1. Off
2. Every 90 minutes
3. Every 90 mins if absorb/float
Greg T Fordan
EngTech
Outback Power Technologies
User avatar
Greg T Fordan
OutBack Technical Service
 
Posts: 139
Joined: Fri Dec 29, 2017 2:56 pm
My RE system: