Hello

For the the last few days I have been having issue with the FNDC. Here is what it is doing.

SOC is reading 71 percent and battery voltage is reading 43.9 volts. This seems to me to be way the heck off as the inverters drop out.

I have only 1 shunt.

So i looked at the graphs for he night and here is the info.

53.9 volts at 8:00 am
53.2 VFX 3638
52.8 VFX 3648
53 FM60
FNDC 53.9
I was charging form grid.
Any ideas and help would be great.
Thanks
oh is a brand new Rolls 400 AMP hours battery bank this summer.
stretch69
Forum Member
 
Posts: 9
Joined: Sun Jul 24, 2016 12:33 pm
Location: Goderich Ontario Canada
My RE system: 6 - 36 volt 290 watt panels for a total of 1740 watts. 3 strings of 2 panels each.
4 - 48 volt 260 watt panels for a total of 1040 watts. 2 stings of 2 panels each.
2 VFX3648 inverters
2 FM60-150 VDC charge controller 1 MATE 3 1 4 port HUB 1 PS2AC/DC backplane
8 S-600 Rolls Surrette 6 volt cells. New on July 23:)

Re: FNCD Issues

Postby Sandra Herrera on Sun Oct 30, 2016 8:14 am

Hello,
This may be a minor programming issues, over time the FN-DC drifted out of calibration. This is because of changes on the batteries, as they are aging the setting should change on the FN-DC.
Please review this documents, and make the programming adjustments. Also make sure your single shunt is capturing all the charging and discharging sources.

http://outbackpower.com/downloads/docum ... p_note.pdf
Sandra Herrera
Applications Engineering