Absorb Voltage too high?

An area for discussing the OutBack FLEXnet DC product.

Moderators: OutBack Moderator Team, OutBack

Absorb Voltage too high?

Postby Olaf on Thu Sep 13, 2018 11:28 am

Hi all.

Per the battery manufacturer's specs, my Absorb voltage is set to 58.8V in the CC, and 58.0 in the FX.
System is reporting a constant 59.8V from the batteries for the whole absorb duration ... :-k Something reporting wrong?
Shunt numbers seem a little random too. Please see attached.

Thanks for any feedback and thoughts you might have.

Screen Shot 2018-09-13 at 12.21.20 PM.png


Screen Shot 2018-09-13 at 12.21.32 PM.png
Olaf
Forum Member
 
Posts: 5
Joined: Sat Sep 01, 2018 10:33 pm
My RE system: 1.1 KW PV
48V FLA @ 385 AH
FX3048T
FM80
FNDC
Mate3 (3.17.1)

Re: Absorb Voltage too high?

Postby Kurt Lundquist on Thu Sep 13, 2018 1:36 pm

Are you using the battery temp sensor (RTS)? What is the battery bank temperature?

-Kurt
Kurt Lundquist
Renewable Energy Project Engineer
http://alphaenergy.us/
User avatar
Kurt Lundquist
Alpha Energy Engineering
 
Posts: 1094
Joined: Tue May 31, 2011 7:23 am
Location: Arlington, WA
My RE system: VFX3524, Mate3, 200Ah 24V AGM Battery Bank

Re: Absorb Voltage too high?

Postby Olaf on Thu Sep 13, 2018 1:42 pm

yes, using the temp sensor.
Battery temp is 18C / 64 F.

Thanks!
Olaf
Forum Member
 
Posts: 5
Joined: Sat Sep 01, 2018 10:33 pm
My RE system: 1.1 KW PV
48V FLA @ 385 AH
FX3048T
FM80
FNDC
Mate3 (3.17.1)

Re: Absorb Voltage too high?

Postby Kurt Lundquist on Thu Sep 13, 2018 2:02 pm

Temp compensation is .12V per degree C for a 48V system. If you are 7 degrees below 25°C then you can expect ~.84 of a volt of increase to the Absorb/Float charge targets. I'd say the 59.8V readout is within range of what the system is supposed to do with a cold battery bank.

Thanks,

-Kurt
Kurt Lundquist
Renewable Energy Project Engineer
http://alphaenergy.us/
User avatar
Kurt Lundquist
Alpha Energy Engineering
 
Posts: 1094
Joined: Tue May 31, 2011 7:23 am
Location: Arlington, WA
My RE system: VFX3524, Mate3, 200Ah 24V AGM Battery Bank

Re: Absorb Voltage too high?

Postby Olaf on Thu Sep 13, 2018 2:07 pm

Copy that. Thanks Kurt.