Advice on best way to setup my outback system

OutBack's newest innovation in balance-of-system components

Moderators: OutBack, OutBack Moderator Team

Post Reply
HondaLee
Forum Member
Posts: 16
Joined: Thu Dec 13, 2018 11:16 am
My RE system: FLEXmax 500
Vfx3648
FLEXmax 80
Flex ware Gvx3648

Advice on best way to setup my outback system

Post by HondaLee » Sat Dec 15, 2018 10:28 am

Thank you in advance for sharing your knowledge!
I will start by telling you what outback equipment I own
FLEXmax 500 with model VFX3648 inverters
FLEXmax 250 with model GVFX3648 Inverter
Two FLEXmax 80 charge controllers
48vdc 500 amp hour agm battery bank
One solar array with 3500 watts with plans to install second array
I have grid power to my house with manual generator transfer switch
Goals: to reduce electric bill as much as possible and have backup power
What are my options to acomplish my goals with what I already own and what is the best way to set it up?

Mike Curran
Forum Emperor
Posts: 1195
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one MX60 (2007)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied GVFX3524's classic stacked for 120/240VAC (2007)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied.

Outback Skybox - Barn roof: (2019)
- 14 (2x7) Talesun 275W
- 2 SimpliPhi 3.8 batteries, 48V, 150Ah total
- future AC coupled input from one row of Westinghouse AC modules*
- future AC coupled input from 14 Talesun 275W, Enphase M215 modules*
* waiting for firmware update from OB

All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: Advice on best way to setup my outback system

Post by Mike Curran » Sat Dec 15, 2018 8:42 pm

Based on my own experience and assuming you need 240volts AC, I would use the flexware 500 only - I don't know if or how the GVFX would work with your 2 VFX's. Unfortunately your VFX's cannot sell back to the grid so any time your PV exceeds your loads (and your battery is fully charged) your solar resource will be wasted. Also, if I understand VFX operation correctly your house will be running on either the grid (e.g.,when you have low battery voltage) or your battery but never both at the same time.

I am assuming your question is more toward how to set up the AC side as the DC seems pretty straightforward. You won't need your second FM80 until you install your second array as one FM80 can easily handle your 3500 watt array to a 48 volt battery.

If your battery and solar resource are sufficient to support your entire house and your house loads don't exceed the 2 VFX's throughput limit (50 amps AC apiece I believe), then wire as shown in attached one-line, with your 2 VFX3648's classic-stacked for 240 volts output and all house loads fed from the VFX's.
15449315058211874130072.jpg
If not sufficient then you might have to break out your essential loads to a separate auxiliary panel. This panel would be fed from your inverters as above while your remaining house loads are fed directly from the grid. I'd keep the generator/transfer switch at the input to the aux panel, which assures your essential loads have the generator as backup. However with this setup your non-essential house loads would have no backup power. This is how my system is wired.

Hope this helps, maybe at least a starting point for discussion.
http://www.tigoenergy.com/site.php?95b2dca2-ca6c
https://enlighten.enphaseenergy.com/public/systems/Hctc107221

HondaLee
Forum Member
Posts: 16
Joined: Thu Dec 13, 2018 11:16 am
My RE system: FLEXmax 500
Vfx3648
FLEXmax 80
Flex ware Gvx3648

Re: Advice on best way to setup my outback system

Post by HondaLee » Sun Dec 16, 2018 9:55 am

Thanks mike for responding to my question. I was following you till you were talking about generator to aux panel. What I have done at present is pretty much what you described except I just disconnected circuits from main home breaker panel and wired them to outback ac panel breakers. The problem with this is I was trying to charge my Chevy volt and it wouldnÔÇÖt charge and goes straight to fault. And I donÔÇÖt know why.
I was reading that the Gvfx FLEXmax 250 could be wired into grid with a separate solar array thus lowering my electric bill for loads I canÔÇÖt run through other inverters.
I called outback a few years back and they told me I could send my non grid tied inverters back to them and they would do a conversion on them to grid tied and send back and do it for free ,but now IÔÇÖm reading they now charge for it.
This morning I looked at my FM 80 and saw something I had not seen before it said high VOC . I have 4 panels wired in series 3 at 37.5 and one at 36.6 so IÔÇÖm not sure how it would get to high.

Mike Curran
Forum Emperor
Posts: 1195
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one MX60 (2007)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied GVFX3524's classic stacked for 120/240VAC (2007)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied.

Outback Skybox - Barn roof: (2019)
- 14 (2x7) Talesun 275W
- 2 SimpliPhi 3.8 batteries, 48V, 150Ah total
- future AC coupled input from one row of Westinghouse AC modules*
- future AC coupled input from 14 Talesun 275W, Enphase M215 modules*
* waiting for firmware update from OB

All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: Advice on best way to setup my outback system

Post by Mike Curran » Sun Dec 16, 2018 2:30 pm

HondaLee wrote: What I have done at present is pretty much what you described except I just disconnected circuits from main home breaker panel and wired them to outback ac panel breakers. The problem with this is I was trying to charge my Chevy volt and it wouldnÔÇÖt charge and goes straight to fault. And I donÔÇÖt know why.
What error message do you see when this happens?
HondaLee wrote: I was reading that the Gvfx FLEXmax 250 could be wired into grid with a separate solar array thus lowering my electric bill for loads I canÔÇÖt run through other inverters.
Maybe if you had a separate Mate3 and Hub you could do this but not sure how charge would be coordinated between the 2 systems... better to have a second battery bank. But by the time you do all that might be cheaper to sell your Flexware 250 and the GVFX3648, then pay Outback to upgrade your VFX's.
HondaLee wrote: This morning I looked at my FM 80 and saw something I had not seen before it said high VOC . I have 4 panels wired in series 3 at 37.5 and one at 36.6 so IÔÇÖm not sure how it would get to high.
That's entirely possible, if you had a cold morning and bright sun 4×37=148 volts, the FM80 VOC limit is 150 volts.
http://www.tigoenergy.com/site.php?95b2dca2-ca6c
https://enlighten.enphaseenergy.com/public/systems/Hctc107221

HondaLee
Forum Member
Posts: 16
Joined: Thu Dec 13, 2018 11:16 am
My RE system: FLEXmax 500
Vfx3648
FLEXmax 80
Flex ware Gvx3648

Re: Advice on best way to setup my outback system

Post by HondaLee » Mon Dec 17, 2018 8:55 am

The FLEXmax 250 has its own mate3 and hub.
You think there should be any issue with long term with excess voltage to charge controller?
From what I have read the one 36.6 volt panel in each string should have reduced the 37.5 panels if anything.if it did go over it had to be very little over.

Mike Curran
Forum Emperor
Posts: 1195
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one MX60 (2007)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied GVFX3524's classic stacked for 120/240VAC (2007)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied.

Outback Skybox - Barn roof: (2019)
- 14 (2x7) Talesun 275W
- 2 SimpliPhi 3.8 batteries, 48V, 150Ah total
- future AC coupled input from one row of Westinghouse AC modules*
- future AC coupled input from 14 Talesun 275W, Enphase M215 modules*
* waiting for firmware update from OB

All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: Advice on best way to setup my outback system

Post by Mike Curran » Mon Dec 17, 2018 11:00 am

VOC changes with temperature, it is not a fixed rating. The rated VOC is based on certain conditions that may differ once panels are mounted in the field. Assuming the VOC's you've cited are the manufacturer's ratings, you can expect them to change in operation and those voltages add up to being pretty close to the FM80's rated max, so you're going to exceed it occasionally.

All I know is your FM80 isn't meant to operate at inputs over 150 VDC, you're taking your chances. You don't say how your panels are arranged but you must have more than 4 to get 3500 watts. You might want to consider wiring them 3 in series × "x" number of similar strings in parallel.

As far as your flexware 250, again I don't know how you'd get its FM80 to coordinate charging with the flexware 500's chargers so a second battery bank might be best - unless someone else smarter than me thinks this could work. In any case I would not connect its AC output to the same circuits as the 500's output...

You've got an embarrassment of riches there :grin: - Mike