X-240 Fan kit

Discussion about OutBacks "PS" enclosures

Moderators: OutBack Moderator Team, OutBack

X-240 Fan kit

Postby RobL on Sat Jun 12, 2004 4:20 pm

Just tried to pop a X-240 and fan kit into a PS2AC and I appear to be missing the transformer shroud. I sent off a plaintive note to my supplier but then looking more carefully at the installation drawing it would appear the shroud is designed for the larger PSAC. Is this correct?

If it is, then I humbly ask you to make that more clear in your documentation. If I have no other choice, then I intend to mount the fan over the box vent opening, pressurize the box and vent the hot air out the top through a (screened) 2" opening. I'm wondering if I should derate the transformer down fom the 6kVA (fan-assisted) rating if I don't use the fan shroud? I am using the X-240/fan combo to convert the 240VAC from my 6 kW generator to 120 for the the inverter chargers and my AC loads.

Rob
RobL
OutBack Guru
 
Posts: 319
Joined: Thu Oct 23, 2003 11:01 pm
Location: Vancouver, BC
My RE system: (1) VFX3524, (3) FM60, 4KW PV, Kubota 6.5KW, Honda EU2000, Hub with Mate2, Surrette S430 and S1380 banks wired for 24V. This is my third system. started with a Dunlite 2KW Windcharger into 120V bank of 8D's into Honeywell rotary inverters in 1978.

Postby Scott Payne on Mon Jun 14, 2004 1:39 pm

Rob,
In a PS2AC the x-240 does not use the FAN shroud. A fan can be mounted on the right hand side of the box (right with normal orientation), there is a bump out for the fan on the side.

I'm wondering if I should derate the transformer down fom the 6kVA (fan-assisted) rating if I don't use the fan shroud?

Yes, 6kVA is to much even with the fan mounted in the side of the AC box.

If it is, then I humbly ask you to make that more clear in your documentation.

No need to be humble :lol: Our documentation is our weak point, I encourage everyone to yell and scream about it :wink: Squeaky wheel and all.

Thanks for the feedback,
Scott
Scott Payne
 

Postby RobL on Mon Jun 14, 2004 4:01 pm

Thanks Scott,

Yes, the fan fits there nicely. I've got it blowing in and will fabricate an aluminum baffle to force more air up towards the transformer. I punched out a bunch of knockouts out of the box- top and will cover with some screening. Then I'll do the dreaded "hand on the transformer" test and see how long I can keep it there at my 4.8kW design minimum (It's between the generator and the inverters/AC loads as a step-down transformer).

Cheers

Rob
RobL
OutBack Guru
 
Posts: 319
Joined: Thu Oct 23, 2003 11:01 pm
Location: Vancouver, BC
My RE system: (1) VFX3524, (3) FM60, 4KW PV, Kubota 6.5KW, Honda EU2000, Hub with Mate2, Surrette S430 and S1380 banks wired for 24V. This is my third system. started with a Dunlite 2KW Windcharger into 120V bank of 8D's into Honeywell rotary inverters in 1978.

Re: X-240 Fan kit

Postby WGB on Sun May 02, 2010 6:47 am

Instead of my hand, I would try an IR thermo gun.
WGB
Junior Member
 
Posts: 3
Joined: Tue Apr 27, 2010 1:57 pm
My RE system: Outback Series Quad
With VFX3524 inverters

Re: X-240 Fan kit

Postby RobL on Mon May 03, 2010 9:45 am

Hi WGB

That was an old old thread...I would love to have had one of those IR guns. The hand was...well...all I had at hand at the time. For the record, the transformer has worked flawlessly all these years. I just bought a second one to run a 240 VAC well pump off the inverters.

Regards

Rob
RobL
OutBack Guru
 
Posts: 319
Joined: Thu Oct 23, 2003 11:01 pm
Location: Vancouver, BC
My RE system: (1) VFX3524, (3) FM60, 4KW PV, Kubota 6.5KW, Honda EU2000, Hub with Mate2, Surrette S430 and S1380 banks wired for 24V. This is my third system. started with a Dunlite 2KW Windcharger into 120V bank of 8D's into Honeywell rotary inverters in 1978.

Re: X-240 Fan kit

Postby WGB on Mon May 03, 2010 12:09 pm

RobL wrote:Hi WGB

That was an old old thread...I would love to have had one of those IR guns. The hand was...well...all I had at hand at the time. For the record, the transformer has worked flawlessly all these years. I just bought a second one to run a 240 VAC well pump off the inverters.

Regards

Rob


LOL, I guess that was some time ago!
Glad its working for you.
WGB
Junior Member
 
Posts: 3
Joined: Tue Apr 27, 2010 1:57 pm
My RE system: Outback Series Quad
With VFX3524 inverters

Re:

Postby JRHill on Tue Apr 19, 2016 11:14 am

RobL wrote:see how long I can keep it there at my 4.8kW design minimum


Yup, since 2003 you should have a good idea of how many watts you can run through the X-240? ;-) I'm just curious as in the winter, the only continuous load on this step down circuit from the genset would be for battery charging and that is only 20 amps @ 120v, when active. Obviously, there are minor household loads too. Last winter season I had the AC current limit set at 29 AAC (3480w) and even with a 25a breaker, it never tripped. I don't have a fan on it but it is with the rest of the stuff in a crawl space which is chilly on the winter.

Just curious as 4.8kW seemed a bit of a stretch over margins of safety.

Thx,
Jim
User avatar
JRHill
OutBack Guru
 
Posts: 326
Joined: Thu Feb 17, 2011 12:12 pm
Location: South central WA
My RE system: -House: FM 80, VFX 3648, FlexnetDC, FlexWare xformer, Mate 3 / Hub, WattPlot/, 2925w SunTech 195, Trojan L16RE-B Batteries. Backup 1: Champion 75531i 3100, backup 2: 11kw Miller Bobcat;
-Well: Grundfos 11-SQF-2 pump, controller & AC switch (CU200, IO101), Morningstar 15a/48vdc Controller, 780w SunTech 195, Trojan golf cart batteries.
-All running since July '11 with no critical problems.


Return to PS Enclosures

Who is online

Users browsing this forum: No registered users and 2 guests

cron