I have a new installation consisting of an FX3232M and a mate. As I read through the setup manual for equalizing it says to specify the voltage and the hours of charge, but nothing about early termination of the charge cycle if the Specific Gravity readings stabilize before the end of the specified time? Is their a way to interrupt the charge before the cycle times out?
Captain Keith
Forum Junior Member
Posts: 1
Joined: Thu Sep 12, 2013 8:02 am
My RE system: Outback VFX3232M with mate.

Re: Equalizing Charge cycle

Postby BlackCherry04 on Fri Sep 13, 2013 7:27 pm

Press the ACin hot key 4 times and choose EQ, this where you start or stop the EQ. To terminate early, choose stop. You can also start / stop a Bulk cycle from the same menu page.

What you were quoting is the charger set up. That is for setting the EQ voltage and time for the EQ cycle.
Forum Virtuoso
Posts: 87
Joined: Sat Feb 09, 2013 8:50 am
My RE system: Various Different On and Off Grid