80a GFDI tripping w/ 600w array

Discussion about OutBack Inverters in Off Grid Applications

Moderators: OutBack, OutBack Moderator Team

Post Reply
Smclark59
Forum Member
Posts: 8
Joined: Tue Jan 24, 2017 8:16 am
My RE system: FlexPower 1 3.5kw, 2-300w solar world panels. generator backup

80a GFDI tripping w/ 600w array

Post by Smclark59 » Wed Nov 15, 2017 9:09 am

I have a Flexpower One with a VFXR 3524A Inverter/Charger and two PV arrays 2x300 and 2x280 in parallel. A week ago my 80a GFDI tripped on a sunny day. Today with one array online the GFDI trips immediately. Power coming was 26a. What is wrong?

User avatar
Jorge Guzman
Strategic Platforms
Posts: 248
Joined: Thu May 29, 2014 9:44 am
My RE system: VFXR3524A, FM80, MATE3. 3x 260W REC. 4x Trojan L16 FLA 370Ah.
Location: Arlington, WA

Re: 80a GFDI tripping w/ 600w array

Post by Jorge Guzman » Wed Nov 15, 2017 10:47 am

A GFDI may trip for two reasons. Exceeding the 80A OCP limit or exceeding the .5A ground fault current limit.
It doesn't seem as you are over producing or exceeding the 80A OCP limit so you may want to focus on a ground fault. One way to find out when solar generation is at max, measure your DC Voltage between your negative to ground any potential could be a problem.
Jorge Guzman
Sr. Strategic Platforms Analyst


Watch easy to follow video tutorials:
https://www.youtube.com/c/wattschool