Setting a Generator Max run time using Mate3

Discussion about OutBack Inverters in Off Grid Applications

Moderators: OutBack, OutBack Moderator Team

Setting a Generator Max run time using Mate3

Postby Phgnw8 on Fri Oct 13, 2017 1:59 am

Hi,

My stsem is a 7KW Radian inverter + PV + battery with 50KVA generator. I set the AGS Voltage Start function to start/stop the generator for battery charging. So the AGS starts the generator when the voltage falls below my voltage set point. My challenge is the gen runs for too long a time, sometimes 9-10hrs. Most times I have to stop the gen manually as it could run even longer trying to complete the absorb cycle for it to stop on its own. I want the gen to not exceed a run time of 4 hours (to save on fuel costs), regardless of AGS start trigger, and regardless if it doesn't complete the absorb cycle.

How can I achieve this anyone please?

George
Phgnw8
Member
 
Posts: 5
Joined: Mon Feb 13, 2017 9:53 am
My RE system: Vfx3048e, Radian 704e Inverter's, fm60/80, 10kw panels, AGM & Flooded batteries

Re: Setting a Generator Max run time using Mate3

Postby Sandra Herrera on Fri Oct 13, 2017 2:37 pm

George,
You need to adjust the charger setting on the inverters
Password-Settings-Inverter-Battery charger
Start by adjusting the absorb time, set it to 0.1. You need to test this until you have it correct for your system.
Sandra Herrera
Applications Engineering


OutBack Power Technologies
User avatar
Sandra Herrera
OutBack Management
 
Posts: 202
Joined: Wed Jul 08, 2015 8:54 am
Location: Arlington, Washington

Re: Setting a Generator Max run time using Mate3

Postby Phgnw8 on Thu Nov 02, 2017 3:20 pm

Thanks Sandra, I’ve just done that, will monitor and see how it goes.
Phgnw8
Member
 
Posts: 5
Joined: Mon Feb 13, 2017 9:53 am
My RE system: Vfx3048e, Radian 704e Inverter's, fm60/80, 10kw panels, AGM & Flooded batteries

Re: Setting a Generator Max run time using Mate3

Postby JRHill on Thu Nov 02, 2017 5:39 pm

Whoa, really? 50kVA? Yeah, fuel savings would be paramount.
User avatar
JRHill
OutBack Guru
 
Posts: 291
Joined: Thu Feb 17, 2011 12:12 pm
Location: South central WA
My RE system: -House: FM 80, VFX 3648, FlexnetDC, FlexWare xformer, Mate 3 / Hub, WattPlot/, 2925w SunTech 195, Trojan L16RE-B Batteries. Backup 1: Champion 75531i 3100, backup 2: 11kw Miller Bobcat;
-Well: Grundfos 11-SQF-2 pump, controller & AC switch (CU200, IO101), Morningstar 15a/48vdc Controller, 780w SunTech 195, Trojan golf cart batteries.
-All running since July '11 with no critical problems.

Re: Setting a Generator Max run time using Mate3

Postby Phgnw8 on Sun Nov 19, 2017 12:43 am

Hi Sandra,

Not noticed any effect after setting charger settings as suggested. The Bulk charging takes quite a while. On several occassions it hit the 5hr point and was still bulk charging, I had to manually turn off gen.

I used to have a XantrexXW inverter with an overide max time shut off function for the gen. This function enables user to set the max time the gen can run regadless if it is started manually or automatically. I usually set to 4hrs. Seems Outback needs to include this feature - or let me into how to achieve a 4hr max gen run time??


George
Phgnw8
Member
 
Posts: 5
Joined: Mon Feb 13, 2017 9:53 am
My RE system: Vfx3048e, Radian 704e Inverter's, fm60/80, 10kw panels, AGM & Flooded batteries