X-240 Help

Discussion about OutBack Inverters in Off Grid Applications

Moderators: OutBack, OutBack Moderator Team

Post Reply
ejerrym
Forum Whiz
Posts: 41
Joined: Mon Dec 29, 2008 5:20 am
My RE system: 24 x 175 W Shell Solar (SolarWorld) panels (4200 Watts total) divided into two arrays each configured as 6 parallel strings of two panels. Two MX-60's and two VFX3648 inverters charging a 48VDC Hup Solar-One battery bank. 15 kW diesel back-up generator.

X-240 Help

Post by ejerrym » Tue Oct 15, 2013 12:52 pm

I have a 120 VAC single inverter system and a 240 volt generator. I know I can use the X-240 to balance the generator, but is there a way to also have 240 available for loads like a compressor that will only operate with the generator running?

dhamilton
OutBack Technical Service
Posts: 59
Joined: Tue Sep 13, 2011 9:42 am
My RE system: 2x VFXR3524A, FLEXmax80, 6x EnergyCell 106NC, Mate3

Re: X-240 Help

Post by dhamilton » Wed Oct 16, 2013 11:12 am

One way you could accomplish this so you only need one x-240 would be to wire up the system as follows.

Generator > 240 Load Panel (Compressor) > x-240 > AC input of inverter > AC output to 120 Load panel.

I hope this helps.

timmartin
Forum Guru
Posts: 278
Joined: Thu Dec 02, 2010 8:31 am
My RE system: ...
Sharp 120W Panels (12)
SunPerfect 230W Panels (9)
Whisper 100 Wind Turbine
Outback FM60 charge controller
Outback FM80 charge controller
Outback VFX3648 inverter/chargers (2)
Outback FlexNet DC
CALB CA400 LiFePO4 3.2V batteries
(32 cells paired together, 1 string = 51.2V 800Ah)

Re: X-240 Help

Post by timmartin » Tue Oct 22, 2013 10:15 am

Yup, I have my 240v well pump wired up as dhamilton described above. If you can live with the 240v loads only running when generator is running, then this is the way to wire it up.