Discussion about OutBack Inverters in Off Grid Applications

Moderators: OutBack, OutBack Moderator Team

Post Reply
Solarmusher
Forum Member
Posts: 16
Joined: Mon Jul 22, 2013 11:00 am
My RE system: Off grid with VFX3648 x2 on Midnite Epanel x2, Hub + Mate, PSX-240, 750Ah Rolls S-480 battery bank, +/-3.2kw Pv array on roof, 2x Midnite Classic 200 controllers + Whizbang battery monitor, Trimetric 2030, SPD300 x4, various/cheap gas generators x3, 1200 watts solar electric DC water heater.
Location: Quebec, CA

FW500 and dual VFX3648

Post by Solarmusher » Mon Jul 22, 2013 12:52 pm

Hi all,
I have an old FW500 that I was using 5 years ago with one VFX3648, I'd like to use it with dual VFX3648 in a new set up and have a few questions:
Do I need one or two 2/0 cable pairs from battery to each 175A disconnect ?
I already have one VFX3648 which is 5 years old, could I add and stack a new unit (not bought yet) with I suppose very different firmwares?
I've had several problem with my old VFX but it's another story, Romex was missing in the inverter, is that a problem?
Do I need two or just one Outback surge protections on each inverters?
All advices greatly appreciated.
Thanks
Erik

User avatar
MyEnergyWarehouse
Forum Whiz
Posts: 41
Joined: Tue Mar 05, 2013 5:38 am
My RE system: Radian Inverter, Mate 3, FM 80
Location: Indiana
Contact:

Re: FW500 and dual VFX3648

Post by MyEnergyWarehouse » Fri Aug 16, 2013 5:22 am

Hello Eric,

Excellent project that you have! I believe I can answer two questions below.

Do I need one or two 2/0 cable pairs from battery to each 175A disconnect ? One pair to each breaker will do if less than 8 feet

Do I need two or just one Outback surge protections on each inverters? One outBack surge protector on each inverter.

Can you educate me on "Romex was missing in the inverter"? Thank you.