GSCM - Network Capable Gen Start Control Module?

Postby Zip92 on Wed Jan 09, 2019 9:19 pm

Does anyone know of a network capable GSCM? I have an Atkinson Mini D that does into error mode at my remotely located cabin. Unless I install a network camera and a relay attached to a network controlled wifi receptacle, I have no way to monitor or reset the GSCM if it goes into error more, say from HZ over/under.

I don’t suppose the Mate3s can send a reset command to the GSCM?

So, I ask, are there any better Gen Start control modules out there that can be monitored and controlled remotely?

Adam
User avatar
Zip92
Forum Member
 
Posts: 18
Joined: Wed Jan 04, 2017 5:14 pm
Location: Ontario Canada
My RE system: Canadian Remote Cabin - Solar + Diesel Gen
COMM: Mate3s
INV: x2 VFX3524
CC1: MX-60
CC2: Conext MPPT 80
SOLAR1: 6x 123w (Sharp ND-L3EJEA)
SOLAR2: 12x 250w
BATT: RollsSurrette 24v (2v x 12) S2-1275AGM
GEN: Cummins 10kw Deisel w/ Atkinson GSCM Mini D

Re: GSCM - Network Capable Gen Start Control Module?

Postby sodamo on Thu Jan 10, 2019 12:59 am

Not familar with your module, but I wonder..
Possibly use the Aux function of either CC or Inverter to turn power on/off to Mini D via your Mate3?
David
Please visit http://vacation.ninolehawaii.com
sodamo
Forum Guru
 
Posts: 472
Joined: Mon Apr 03, 2006 1:55 am
Location: Ninole, Hi
My RE system: Totally off grid
36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
4 FX3048T
RTS
4 FM 80 charge controllers
FNDC w/3 shunts
Mate 3
OpticsRE - Piha Kahuku
21 Aquion Aspen 48S (46.2 kw)
24Kw Yangdong Genset (Affordable Generators - Poor support)
10Kw MEP 803a
Honda EU7000i

Davis VantagePro2 Wx Station
On line at: http://www.weatherlink.com/user/sodamo/

Re: GSCM - Network Capable Gen Start Control Module?

Postby Zip92 on Thu Jan 10, 2019 5:04 am

The AUX function sends sends the start signal to the Mini-D. Once the Mini-D receives that signal, then it initiates the start sequence which is first to 'glow' for 7 seconds, then a crank command for a few seconds to start the gen. When the Mate/AGS turns off the AUX signal, then the Mini-D tells the gen to shutdown. The Mini-D is powered by the 12v battery that starts the diesel gen.
User avatar
Zip92
Forum Member
 
Posts: 18
Joined: Wed Jan 04, 2017 5:14 pm
Location: Ontario Canada
My RE system: Canadian Remote Cabin - Solar + Diesel Gen
COMM: Mate3s
INV: x2 VFX3524
CC1: MX-60
CC2: Conext MPPT 80
SOLAR1: 6x 123w (Sharp ND-L3EJEA)
SOLAR2: 12x 250w
BATT: RollsSurrette 24v (2v x 12) S2-1275AGM
GEN: Cummins 10kw Deisel w/ Atkinson GSCM Mini D

Re: GSCM - Network Capable Gen Start Control Module?

Postby Kurt Lundquist on Thu Jan 10, 2019 8:36 am

Power the Mini-D with the other inverter AUX port. You can use OpticsRE to remotely cycle the AUX port OFF/ON to reset the Mini-D if there is an AGS error.

Let us know if that works out for you.

Cheers,

-Kurt
Kurt Lundquist
Renewable Energy Project Engineer
http://alphaenergy.us/
User avatar
Kurt Lundquist
Alpha Energy Engineering
 
Posts: 1142
Joined: Tue May 31, 2011 7:23 am
Location: Arlington, WA
My RE system: VFX3524, Mate3, 200Ah 24V AGM Battery Bank

Re: GSCM - Network Capable Gen Start Control Module?

Postby sodamo on Thu Jan 10, 2019 10:20 am

Thanks Kurt, that’s what I meant, but you explained it mo betta.
David
Please visit http://vacation.ninolehawaii.com
sodamo
Forum Guru
 
Posts: 472
Joined: Mon Apr 03, 2006 1:55 am
Location: Ninole, Hi
My RE system: Totally off grid
36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
4 FX3048T
RTS
4 FM 80 charge controllers
FNDC w/3 shunts
Mate 3
OpticsRE - Piha Kahuku
21 Aquion Aspen 48S (46.2 kw)
24Kw Yangdong Genset (Affordable Generators - Poor support)
10Kw MEP 803a
Honda EU7000i

Davis VantagePro2 Wx Station
On line at: http://www.weatherlink.com/user/sodamo/

Re: GSCM - Network Capable Gen Start Control Module?

Postby blackswan555 on Thu Jan 10, 2019 11:48 am

Do you know if the GSCM needs constant voltage ? My thinking is could you use a double pole relay running the normal AGS to interrupt its 12v feed when AGS is not active ?

Tim
My comments are based on my experience and research, They are not endorsed or checked by Outback.I am an independent British electrician living in Spain, So please take this into account when reading /acting on my post`s.
blackswan555
Forum Emperor
 
Posts: 2634
Joined: Sat Aug 30, 2008 5:50 am
Location: Ibiza Spain,
My RE system: Other peoples, VFX "E" versions, FLA`s, Generators.

Re: GSCM - Network Capable Gen Start Control Module?

Postby Zip92 on Thu Jan 10, 2019 1:27 pm

Great tips guys; thank you. Right now I use a 12v relay plugged into a WiFi receptacle to do the 'reset'. The AUX and DP relay options sound like they would work as well.

How would I tell the Mate3s to activate/interrupt this second AUX?

@Tim, yes the GSCM requires constant voltage. Cutting the voltage to reset should work. That's essentially what I do now through the use of a 12v relay connected to a wifi controlled receptacle... Perhaps there's a more automated way to do it?

Adam
User avatar
Zip92
Forum Member
 
Posts: 18
Joined: Wed Jan 04, 2017 5:14 pm
Location: Ontario Canada
My RE system: Canadian Remote Cabin - Solar + Diesel Gen
COMM: Mate3s
INV: x2 VFX3524
CC1: MX-60
CC2: Conext MPPT 80
SOLAR1: 6x 123w (Sharp ND-L3EJEA)
SOLAR2: 12x 250w
BATT: RollsSurrette 24v (2v x 12) S2-1275AGM
GEN: Cummins 10kw Deisel w/ Atkinson GSCM Mini D

Re: GSCM - Network Capable Gen Start Control Module?

Postby Kurt Lundquist on Thu Jan 10, 2019 2:07 pm

Zip92 wrote:How would I tell the Mate3s to activate/interrupt this second AUX?


Let's say you are using the port 2 inverter AUX to power the GSCM. In OpticsRE you would go to the port 2 device, scroll down to the AUX port, then set it to off. After the AUX switches off you would then set the AUX to ON. I don't think there is a more automated way to make it happen because an AGS error will keep the OB system from trying to auto start the gen. Either way, you have to manually set AGS to OFF then AUTO again to get it back into auto mode if the generator fails to start.

-Kurt
Kurt Lundquist
Renewable Energy Project Engineer
http://alphaenergy.us/
User avatar
Kurt Lundquist
Alpha Energy Engineering
 
Posts: 1142
Joined: Tue May 31, 2011 7:23 am
Location: Arlington, WA
My RE system: VFX3524, Mate3, 200Ah 24V AGM Battery Bank

Re: GSCM - Network Capable Gen Start Control Module?

Postby blackswan555 on Thu Jan 10, 2019 3:11 pm

yes the GSCM requires constant voltage. Cutting the voltage to reset should work. That's essentially what I do now through the use of a 12v relay connected to a wifi controlled receptacle... Perhaps there's a more automated way to do it?

I am thinking the DP relay is 1, the two wire trigger for AGS start. 2, It cuts power to the GSCM when not "on" , If the GSCM would work with power on and start signal at the same time in effect giving a reset every time it is activated,

Another point that may or may not be correct, Techs please confirm either way, IIRC AGS will have 3 attempts at starting gen before error ?

Tim
My comments are based on my experience and research, They are not endorsed or checked by Outback.I am an independent British electrician living in Spain, So please take this into account when reading /acting on my post`s.
blackswan555
Forum Emperor
 
Posts: 2634
Joined: Sat Aug 30, 2008 5:50 am
Location: Ibiza Spain,
My RE system: Other peoples, VFX "E" versions, FLA`s, Generators.

Re: GSCM - Network Capable Gen Start Control Module?

Postby Kurt Lundquist on Fri Jan 11, 2019 3:04 pm

blackswan555 wrote:echs please confirm either way, IIRC AGS will have 3 attempts at starting gen before error ?


AGS does not make 3 attempts. When the generator needs to start AGS activates the AUX port on the device that is specified in the AGS setup and starts the "Fault Timer". If the OutBack system does not connect to an AC source before the AGS Fault time runs out then AGS logs an error and will not attempt to start the generator again. You have to manually set AGS to OFF then AUTO to reactivate AGS. I think the user programmable Fault time is 17 minutes by default.

-Kurt
Kurt Lundquist
Renewable Energy Project Engineer
http://alphaenergy.us/
User avatar
Kurt Lundquist
Alpha Energy Engineering
 
Posts: 1142
Joined: Tue May 31, 2011 7:23 am
Location: Arlington, WA
My RE system: VFX3524, Mate3, 200Ah 24V AGM Battery Bank