Grid Sell and Electric Meter

Post by Yoe » Sun Apr 07, 2019 10:57 am

Do you need a special meter in order to "sell back" to the grid?

What would happen if someone enabled it before full utility approval for testing purposes?

Mike Curran
Forum Emperor
Posts: 1195
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one MX60 (2007)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied GVFX3524's classic stacked for 120/240VAC (2007)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied.

Outback Skybox - Barn roof: (2019)
- 14 (2x7) Talesun 275W
- 2 SimpliPhi 3.8 batteries, 48V, 150Ah total
- future AC coupled input from one row of Westinghouse AC modules*
- future AC coupled input from 14 Talesun 275W, Enphase M215 modules*
* waiting for firmware update from OB

All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: Grid Sell and Electric Meter

Post by Mike Curran » Sun Apr 07, 2019 4:33 pm

For my initial grid-tied system of 1,440 watts capacity (2007), I got a permit from my utility but (I'm assuming) because my output to the grid was so low, they never changed out my original meter, until I added 6,450 watts in 2012. Still, with the old meter I could observe the disk that turns as you're using grid power and on sunny days it would slow or even start to turn "backwards".

However, I have heard that some non-net meters may not account for your grid feedback at all and may even erroneously show your feedback as use, charging you for energy you've fed to the grid. For testing purposes probably not a problem but best to get the permit, and if your system is large enough, a new, net meter. Without it you really can't accurately account for what you're selling to the grid.
http://www.tigoenergy.com/site.php?95b2dca2-ca6c
https://enlighten.enphaseenergy.com/public/systems/Hctc107221

gregorio
Forum Member
Posts: 16
Joined: Thu Jan 17, 2019 6:36 pm
My RE system: Current: Radian GS8048A/GSLC174-AC (in manual bypass mode)
SolarEdge SE6000 (AC Coupled).
Standalone SolarEdge SE7600.
SolarWorld 250W panels
In Progress: Generac 22kVA Generator
Coming Soon: Lithium Battery (leaning towards Discover Energy AES 6.6kWh)

Re: Grid Sell and Electric Meter

Post by gregorio » Mon Apr 08, 2019 1:02 pm

When my 10kW system was getting inspected for approval in 2015, I left it on after it passed inspection. However, my utility company (PGE) did not credit me for any power I sent to the grid until they got all paperwork in order. That took about 3 weeks. My meter was already net metering capable because it was not changed.

jbakker
Forum Guru
Posts: 192
Joined: Fri Feb 23, 2018 6:47 am
My RE system: 2 VFX3648 Inverters 2 FM60 150VDC Charge Controllers Mate3 3.4 KW of panels 15kw JC Onan NG Generator made in 1975 I love that generator almost as much as my wife.
7 banks of 14 cells each from a 2017 Chevy Volt. Parallel for the AMP Hour. 7 Chinese made BMS systems.
Location: Goderich Ontario Canada

Re: Grid Sell and Electric Meter

Post by jbakker » Wed Apr 10, 2019 4:48 am

On my system I have played with a couple of grid tie cards.
I have one of the so called smart meters. Now when using from the Grid there is a little arrow that scrolls from left to right facing the meter.
When I was feeding the grid back the arrow from right to left and there was an exclamation symbol on the display as well, so I was feeding the grid.
The question is was can the utility company sense this? I have no agreement to feed back as the town has no interest in net metering.

User avatar
mexsudo
Forum Member
Posts: 17
Joined: Wed Mar 13, 2019 7:40 pm
My RE system: 8 290 watt panels: Canadian Solar
4 AGM 12v 115Ah batteries: Duravolt DGG115-2
Inverter: Outback VFXR3648A, 3600VA
Charge Controller: Outback FLEXmax 60, FM60-150VDC
System Display and Controller: Outback MATE3s
Location: Ensenada, Baja California, Mexico

Re: Grid Sell and Electric Meter

Post by mexsudo » Wed Apr 10, 2019 5:48 am

Last month when my grid connection was first made we stepped out to the meter, it was indeed spinning backwards.
it was a 20 year old conventional meter.
I recorded the readings and it was counting down at a rate that made sense, and again ran normally when the sun was not out.
This would raise huge red flags with CFE (our federal electric agency) if the meter reader saw it turning backwards, or it was noted in the office that my use went down radically (power theft).
Grid-tie is permissible, and encouraged here, but a contract is required.
They bank my power for one year, and I draw from it as needed, 1:1 ratio. I think that is cool.

After my installer had me connected he prepared the paperwork for the formal contract with CFE and submitted it for me.
A few days later the meter was replaced with a modern digital one that has an elaborate display that I don't quite understand, but it does have an arrow showing the direction of flow. It supposedly collects more data, has a wifi indicator. The meter reader said that wifi does not work, he will still return and read the meter as before.
I checked on line, the contract was approved. My next invioce should reflect the changes.
peter ehlert (mexsudo)

User avatar
Megunticook
Forum Guru
Posts: 210
Joined: Fri Sep 29, 2017 4:08 am
My RE system: 6.4 kW solar array (21 QCell 305 panels in strings of 3)
GS8048A FLEXpower Radian (Radian 8048A, 2 FlexMax 80 cc's, Mate 3s, FlexNet DC, Hub)
8x6v Rolls-Surette 550 FLA batteries, 428AH
Location: Maine
Contact:

Re: Grid Sell and Electric Meter

Post by Megunticook » Wed Apr 10, 2019 11:40 am

Yoe wrote:Do you need a special meter in order to "sell back" to the grid?
My POCO, Central Maine Power, replaced my analog meter with a pair of analog meters--one "in" and one "out." When CMP pushed the smart meters on all their customers I opted out, which is why we got the double analog meters. From what I understand most modern smart meters can measure current flowing in either direction.
Yoe wrote:What would happen if someone enabled it before full utility approval for testing purposes?
That's not a good idea. You'd certainly be jeopardizing your interconnection agreement. From the POCO's perspective, they want to make sure your system is safe and won't backfeed during an outage and get someone hurt. In my case I it only took about 5-6 weeks to get the meters installed and get the green light to put our system online.
https://sunnypower.org

AntonyH
Forum Junior Member
Posts: 1
Joined: Sat Apr 13, 2019 9:10 am
My RE system: Outback grid tie, flex ate mate3 . 12x300. Volt panels. 4x 200ah gel batteries connected 48volts

Re: Grid Sell and Electric Meter

Post by AntonyH » Wed Apr 17, 2019 4:45 am

Hi, My first post about my Outback power system. I have had a system working for about 5 years , using 12x 300w panels, 12x100ah batteries linked to supply 48 volts,
I have a Flexmax M80 inverter and a grid tie systwm to sell on line which has been working very well until the batteries over heated. I have changed to 4x200ah gel batteries as well as installing 6x 350volt extra panels. How do I change the settings to use these batteries and new panels?.
Control is thro a Mate3s
Hope you can help?

badwolf
Forum Member
Posts: 9
Joined: Fri Dec 18, 2015 4:42 pm
My RE system: Outback Radian GS8048 (first generation), 860aH@48v lead acid battery bank, two Midnight Classic 150 charge controllers, with 7000KW PV.

Re: Grid Sell and Electric Meter

Post by badwolf » Fri Nov 08, 2019 6:08 pm

So I have a real problem with this.

Inverter: GS 8048
Batteries: 860Kwh lead acid
CC: 2 Midnight Classic 150s
Solar: 24 275w panels

I am out in the Ozarks of Missouri and there is nobody that knows these grid interactive systems in the whole state.

I had about 7.5KW of panels installed in 2014, but it didn't get finished. I changed contractor in the middle because they didn't want to deal with the grid for issue, so I went with a guy who said he could finish it. He botched everything (years later I found out that he had wired one string backwards and it had been causing the breaker to trip in the junction box).

In any case, when it came time to get it approved, he told me that we needed to dig a separate line to the poll and sell back on that line. After many weeks of working with this system he had no idea how it worked!! So we got on the phone with the utility (CoMo electric, it's scoop). The utility said that anything that would spin the meter backwards was a no-go. Could never find a way to get them to approve it.

So for the past 3 years since I commissioned it, I have been running the system without an agreement in place and using battery backup mode only (no sell back). I have a 3 pile transfer on the shed so it just looks like I am switching back and forth to the grid manually.

In the mean time I have been using the HBX mode or "grid use time" to run batteries down to store the extra energy. I estimate that I have been using losing about 30 to 40 percent of the available production and have also been depleting the lead in the batteries. I have been tempted to sell back and run meter backwards instead of killing batteries and wasting energy but I don't want to push my luck since I don't have an agreement.

If anyone knows how to talk to utility company or could help me out then it would be highly appreciated.

Mike Curran
Forum Emperor
Posts: 1195
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one MX60 (2007)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied GVFX3524's classic stacked for 120/240VAC (2007)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied.

Outback Skybox - Barn roof: (2019)
- 14 (2x7) Talesun 275W
- 2 SimpliPhi 3.8 batteries, 48V, 150Ah total
- future AC coupled input from one row of Westinghouse AC modules*
- future AC coupled input from 14 Talesun 275W, Enphase M215 modules*
* waiting for firmware update from OB

All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: Grid Sell and Electric Meter

Post by Mike Curran » Fri Nov 08, 2019 6:23 pm

I couldn't find anything on CoMo's website re net metering. But according to this website https://renewmo.org/missouri-clean-ener ... ction-act/ net metering is legally required to be available to all residential utility customers in Missouri. There's a phone number on the site, I'd give them a call. Good luck!
http://www.tigoenergy.com/site.php?95b2dca2-ca6c
https://enlighten.enphaseenergy.com/public/systems/Hctc107221

badwolf
Forum Member
Posts: 9
Joined: Fri Dec 18, 2015 4:42 pm
My RE system: Outback Radian GS8048 (first generation), 860aH@48v lead acid battery bank, two Midnight Classic 150 charge controllers, with 7000KW PV.

Re: Grid Sell and Electric Meter

Post by badwolf » Sat Nov 09, 2019 5:03 pm

Mike Curran wrote:
Fri Nov 08, 2019 6:23 pm
I couldn't find anything on CoMo's website re net metering. But according to this website https://renewmo.org/missouri-clean-ener ... ction-act/ net metering is legally required to be available to all residential utility customers in Missouri. There's a phone number on the site, I'd give them a call. Good luck!
This is super helpful. Can you also point to a resource that defines net metering in such a way that energy is being bought and sold from the same L1,L2, and neutral and not separate for buy and sell?

Thanks!