Postby Signman on Tue Sep 12, 2017 12:16 am

What is the most panels/watts I can put up using a FM80?
Signman
Member
 
Posts: 7
Joined: Mon Jul 24, 2017 7:27 pm
Location: NSW Australia
My RE system: 3kw Outback Inverter model VFX2612E
Flexmax60 controller
2x300AH 12v sealed valve regulated lead acid AGM Batteries.
6 x 64w Panels
3 x 190w Panels
7 x 250w Panels

Re: FM80

Postby petertearai on Tue Sep 12, 2017 12:39 am

12 volts from memory 1200 watts .You can download the fm 80 manual . it is in there .
2220 pv. fm80. 4times rolls 450 ah 24 volts. victron battery monitor. outback fxr 2000 watt inverter
petertearai
OutBack Guru
 
Posts: 314
Joined: Fri Aug 06, 2010 4:35 pm
Location: NewZealand North Island
My RE system: 2220 watt pv, fm80, outback fxr 2000 watt inverter. Rolls s600 times 4 24 volt system victron battery moniter. optics RE

Re: FM80

Postby Signman on Tue Sep 12, 2017 2:04 am

Thanks... Where are you from in NZ?
Signman
Member
 
Posts: 7
Joined: Mon Jul 24, 2017 7:27 pm
Location: NSW Australia
My RE system: 3kw Outback Inverter model VFX2612E
Flexmax60 controller
2x300AH 12v sealed valve regulated lead acid AGM Batteries.
6 x 64w Panels
3 x 190w Panels
7 x 250w Panels

Re: FM80

Postby SandyP on Tue Sep 12, 2017 2:06 am

Signman wrote:What is the most panels/watts I can put up using a FM80?


From the manual :

The output current limit of the FLEXmax 80 is 80 amps.

The largest PV array must have a rated short-circuit current of 64 amps or less under STC (Standard
Test Conditions).

At your battery voltage of 12 V, Outback recommends only using a 1000 W (at STC) panel array .
SandyP
OutBack Guru
 
Posts: 226
Joined: Tue Jun 21, 2011 4:44 am
Location: Victoria, Australia
My RE system: 8 x 190W 24V Suntech panels (4 strings of 2)
Mate2
Outback FM60 MPPT
12 x 2V Hoppecke GEL 660 Ah C100 - 24V System
Outback VFX3024 Inverter/Charger
Victron BMV-602s
Honda 5.5kW Genset

Re: FM80

Postby petertearai on Tue Sep 12, 2017 10:07 pm

Hi Im in Auckland
2220 pv. fm80. 4times rolls 450 ah 24 volts. victron battery monitor. outback fxr 2000 watt inverter
petertearai
OutBack Guru
 
Posts: 314
Joined: Fri Aug 06, 2010 4:35 pm
Location: NewZealand North Island
My RE system: 2220 watt pv, fm80, outback fxr 2000 watt inverter. Rolls s600 times 4 24 volt system victron battery moniter. optics RE

Re: FM80

Postby petertearai on Tue Sep 12, 2017 10:11 pm

Page 75 of my fm80 manual says recomended array size for 12 volts is 1250 W
2220 pv. fm80. 4times rolls 450 ah 24 volts. victron battery monitor. outback fxr 2000 watt inverter
petertearai
OutBack Guru
 
Posts: 314
Joined: Fri Aug 06, 2010 4:35 pm
Location: NewZealand North Island
My RE system: 2220 watt pv, fm80, outback fxr 2000 watt inverter. Rolls s600 times 4 24 volt system victron battery moniter. optics RE

Re: FM80

Postby SandyP on Tue Sep 12, 2017 10:38 pm

petertearai wrote:Page 75 of my fm80 manual says recomended array size for 12 volts is 1250 W


Maybe they have derated them, Spec sheet on Outback website : http://www.outbackpower.com/outback-pro ... exmax-6080
SandyP
OutBack Guru
 
Posts: 226
Joined: Tue Jun 21, 2011 4:44 am
Location: Victoria, Australia
My RE system: 8 x 190W 24V Suntech panels (4 strings of 2)
Mate2
Outback FM60 MPPT
12 x 2V Hoppecke GEL 660 Ah C100 - 24V System
Outback VFX3024 Inverter/Charger
Victron BMV-602s
Honda 5.5kW Genset

Re: FM80

Postby petertearai on Tue Sep 12, 2017 11:27 pm

yep . my fm 80 hard copy manual is marked 900-0082-01-00REV A .
Watts is amps times volts . So say 15 volts times 80 amps = 1200 watts.
Maybe derated because it is hard to control to not go over the 80amps . However in the real world probably ok with 1250 watts.
Although i think my 24 volt system history on the fm80 shows a maximum of 2600 watts . So my 2200 watts of panel has for a time been over powering my fm80.
I Have set the max amps on my fm80 to 75 amps , to hopefully help keep it within max limits .
2220 pv. fm80. 4times rolls 450 ah 24 volts. victron battery monitor. outback fxr 2000 watt inverter
petertearai
OutBack Guru
 
Posts: 314
Joined: Fri Aug 06, 2010 4:35 pm
Location: NewZealand North Island
My RE system: 2220 watt pv, fm80, outback fxr 2000 watt inverter. Rolls s600 times 4 24 volt system victron battery moniter. optics RE

Re: FM80

Postby Signman on Wed Sep 13, 2017 2:18 pm

Thanks for that Sandy. . . . Used to live in Whitianga. . . been back here, living in the bush in NSW. Cheers James
Signman
Member
 
Posts: 7
Joined: Mon Jul 24, 2017 7:27 pm
Location: NSW Australia
My RE system: 3kw Outback Inverter model VFX2612E
Flexmax60 controller
2x300AH 12v sealed valve regulated lead acid AGM Batteries.
6 x 64w Panels
3 x 190w Panels
7 x 250w Panels