badr15
Forum Member
Posts: 12
Joined: Fri Mar 27, 2020 1:05 am
My RE system: 24 panels 6 panels connected in serie(VOC 267 V) On 4 matrices 7.2 kW
Solar panels 24 panels installed on one base on sandy ground in the desert
must pv35-12kw inverter and ac charge
FLEXmax 100 AFCI charge controller
Outback FLEXnet DC monitor with 1 shunt for inverter
Outback MATE3s system controller
Outback Hub
battery 150 amp Circuit Breaker
battery hoppecke model: (8hpzs840) 2V (24pics) lead acid @ 48 volts 840AH
Running OpticsRE since March 2020
Location:Desert camp 70 miles north of riyadh saudi arabia @ elevation 250 ft

technical problems

Post by badr15 » Fri Mar 27, 2020 1:30 am

I hope to help me
I bought (FLEXmax 100 AFCI) and controller (mate3s) with hub
I have two problems:
1 - When programming mate3s it works for some time then it stops working and restarts? What is the solution?

2- When the device is connected to the batteries, the fan attached to the device works for a second, then it stops and never works, and when I touch the device very hot, the temperature reaches 50? What's the solution? To make the fan run...

system information:
System volts:48V
battery amp: 840AH
MATE3S Firmware:1.4.2
FM100-300VDC-AFCI Firmware:2.0.1
Is the software version compatible?

raysun
Forum Emperor
Posts: 2105
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower One: FX3048T, (2) FM80, MATE3s, FlexNetDC
Outback 200NC batteries (8 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: technical problems

Post by raysun » Fri Mar 27, 2020 9:45 am

badr15 wrote:
Fri Mar 27, 2020 1:30 am
I hope to help me
I bought (FLEXmax 100 AFCI) and controller (mate3s) with hub
I have two problems:
1 - When programming mate3s it works for some time then it stops working and restarts? What is the solution?

2- When the device is connected to the batteries, the fan attached to the device works for a second, then it stops and never works, and when I touch the device very hot, the temperature reaches 50? What's the solution? To make the fan run...

system information:
System volts:48V
battery amp: 840AH
MATE3S Firmware:1.4.2
FM100-300VDC-AFCI Firmware:2.0.1
Is the software version compatible?
Assuming both pieces of hardware are undamaged, the described behavior is definitely not normal. Something is amiss, perhaps in the system wiring, or another deficiency.

What is the complete list of equipment in the installation?

What is the specific model of battery?

Is the system all new?

Was the system installed by a trained technician or is it DIY?

pss
Forum Guru
Posts: 484
Joined: Mon Jul 24, 2017 8:40 am
My RE system: 8330 watts in three strings, Flexmax 60 x 3, Radian 8048A, GSLC load center, Mate 3S, Hub 10.3, FN-DC and 900 Amp, 48V Trojan T105-RE battery bank.

Re: technical problems

Post by pss » Fri Mar 27, 2020 9:52 am

When the fan comes on in the charge controller is not programmable. Try to measure temps using a hand held laser thermometer you can buy in many stores. Report temps here, like at vents.
Next question: do you observe mate physically reboot or just by looking at events reported in Optics RE?

badr15
Forum Member
Posts: 12
Joined: Fri Mar 27, 2020 1:05 am
My RE system: 24 panels 6 panels connected in serie(VOC 267 V) On 4 matrices 7.2 kW
Solar panels 24 panels installed on one base on sandy ground in the desert
must pv35-12kw inverter and ac charge
FLEXmax 100 AFCI charge controller
Outback FLEXnet DC monitor with 1 shunt for inverter
Outback MATE3s system controller
Outback Hub
battery 150 amp Circuit Breaker
battery hoppecke model: (8hpzs840) 2V (24pics) lead acid @ 48 volts 840AH
Running OpticsRE since March 2020
Location:Desert camp 70 miles north of riyadh saudi arabia @ elevation 250 ft

Re: technical problems

Post by badr15 » Fri Mar 27, 2020 11:57 am

No need for laser thermometer The device show temperature in the settings on opticsre, the mate3s display and controller does not respond to pressing and then restarts

fcwlp
Forum Guru
Posts: 295
Joined: Wed Jan 22, 2020 9:40 am
My RE system: GS8048A, FM80 w/3,600 W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed
I also install and maintain grid-tied and off-grid systems, details will be given for these system if required
Location: 80 miles NE of Phoenix at 5500'

Re: technical problems

Post by fcwlp » Fri Mar 27, 2020 5:49 pm

badr15 wrote:
Fri Mar 27, 2020 1:30 am
MATE3S Firmware:1.4.2
FM100-300VDC-AFCI Firmware:2.0.1
Is the software version compatible?
The Mate3s firmware at 1.4.2 is the latest. For the FM100 AFCI, the website does not list a firmware version yet. The original FM100 (GFCI only) uses firmware version 1.2.0.
badr15 wrote:
Fri Mar 27, 2020 1:30 am
When the device is connected to the batteries, the fan attached to the device works for a second, then it stops and never works, and when I touch the device very hot, the temperature reaches 50?
A temperature of 50C is not considered to be hot for semiconductor technology. Per p.38 of the original FM100 manual, the fan turns off at 50C, on at 58C, output derating begins at 70C and over temp error is 90C. What are you reading in OpticsRE for the FM100's Output FET Temperature?

fcwlp
Forum Guru
Posts: 295
Joined: Wed Jan 22, 2020 9:40 am
My RE system: GS8048A, FM80 w/3,600 W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed
I also install and maintain grid-tied and off-grid systems, details will be given for these system if required
Location: 80 miles NE of Phoenix at 5500'

Re: technical problems

Post by fcwlp » Fri Mar 27, 2020 5:49 pm

badr15 wrote:
Fri Mar 27, 2020 1:30 am
MATE3S Firmware:1.4.2
FM100-300VDC-AFCI Firmware:2.0.1
Is the software version compatible?
The Mate3s firmware at 1.4.2 is the latest. For the FM100 AFCI, the website does not list a firmware version yet. The original FM100 (GFCI only) uses firmware version 1.2.0.
badr15 wrote:
Fri Mar 27, 2020 1:30 am
When the device is connected to the batteries, the fan attached to the device works for a second, then it stops and never works, and when I touch the device very hot, the temperature reaches 50?
A temperature of 50C is not considered to be hot for semiconductor technology. Per p.38 of the original FM100 manual, the fan turns off at 50C, on at 58C, output derating begins at 70C and over temp error is 90C. What are you reading in OpticsRE for the FM100's Output FET Temperature?

badr15
Forum Member
Posts: 12
Joined: Fri Mar 27, 2020 1:05 am
My RE system: 24 panels 6 panels connected in serie(VOC 267 V) On 4 matrices 7.2 kW
Solar panels 24 panels installed on one base on sandy ground in the desert
must pv35-12kw inverter and ac charge
FLEXmax 100 AFCI charge controller
Outback FLEXnet DC monitor with 1 shunt for inverter
Outback MATE3s system controller
Outback Hub
battery 150 amp Circuit Breaker
battery hoppecke model: (8hpzs840) 2V (24pics) lead acid @ 48 volts 840AH
Running OpticsRE since March 2020
Location:Desert camp 70 miles north of riyadh saudi arabia @ elevation 250 ft

Re: technical problems

Post by badr15 » Sat Mar 28, 2020 12:53 am

Thank you for your prompt response to technical support and for more information on the problem

Battery information
Battery system: 48v
Battery capacity: 840AH
Model batteries:8hpzs840
Batteries brand:hoppecke

Solar panels information
Solar panels:24 pieces
voc:44.51V
ISC:8.54A
PMAX:300W
I Connect the panels respectively 6 panels and voc:from 223.5V to 258V

Connect the wire
i connected wire grounding to device
Solar power cables are equipped with a circuit breaker
Battery wire provided with a circuit breaker

Cooling
Cooling is the problem
I temporarily cool the divice with external fan
The problem of cooling device fan need a solution to run
The problem of the cooling fan in the device does not work, and when i restart the device and disconnect it from the batteries it works fan again and then turns off, i need a solution and operate it

I installed the device myself due to the lack of technician in my country. When our technicians see the device (FLEXmax 100 AFCI) they describe it as new to them and they cannot install or program it

Picture of device settings
http://www.4up4.com/uploads/file_2020-03-28_074827.jpg

Image

badr15
Forum Member
Posts: 12
Joined: Fri Mar 27, 2020 1:05 am
My RE system: 24 panels 6 panels connected in serie(VOC 267 V) On 4 matrices 7.2 kW
Solar panels 24 panels installed on one base on sandy ground in the desert
must pv35-12kw inverter and ac charge
FLEXmax 100 AFCI charge controller
Outback FLEXnet DC monitor with 1 shunt for inverter
Outback MATE3s system controller
Outback Hub
battery 150 amp Circuit Breaker
battery hoppecke model: (8hpzs840) 2V (24pics) lead acid @ 48 volts 840AH
Running OpticsRE since March 2020
Location:Desert camp 70 miles north of riyadh saudi arabia @ elevation 250 ft

Re: technical problems

Post by badr15 » Sat Mar 28, 2020 4:15 am

New devices(FM100-300VDC-AFCI) I purchased from Amazon
Seller Name:Outback Power
The strange thing is how the device (FM100-300VDC-AFCI) comes with this version(Firmware:2.0.1) and it is not present in the company website and I have not updated it ?

raysun
Forum Emperor
Posts: 2105
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower One: FX3048T, (2) FM80, MATE3s, FlexNetDC
Outback 200NC batteries (8 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: technical problems

Post by raysun » Sat Mar 28, 2020 5:40 am

The two issues reported: firmware variations and operating temperature, are minor and not likely causing the problems reported.

There are no reports of firmware incompatibility in current models of OB equipment that i am aware of, and certainly none that cause operational failures, so I suggest setting firmware updates aside as lower priority. Finding the true cause of operational deficiencies should take priority.

Operating temperature is an important factor, but usually comes into play when temperatures exceed rated operating ranges. As a general rule of thumb, operating electronics at a lower temperature is better, but higher temperatures, within proper limits, are entirely acceptable. The power FETs in the equipment operating in the 50°C range is entirely normal, and in fact may be below the point of needing to turn on the cooling fan. That the fan runs for a few seconds at startup then stops is a normal part of the startup diagnostics, and is to be expected.

If there was a true thermal overload event, the equipment would shut down with an error that would be registered in the event logs. 50°C+ isn't that overload point. In fact, it would be nearly 100°C. At that temperature, i expect you would definitely be hearing the fan running.

TBH, it appears that focus is being placed on metrics that are easy to see when looking into the configuration screens, but IME, these are unlikely to be the root cause of the problems encountered.

Something else in the setup, external to the system modules, is more likely the source. Further analysis and diagnostics are necessary, it would appear.

To help further, it would be beneficial to update your profile with a complete list of all equipment in the system. Solar panel models and array configuration, PV combiner box and disconnects. battery model and capacity, inverter, DC Panel and circuit breakers/disconnects, AC panel and circuit breakers, etc.

At this point you may not know what to look for to debug the system, and we can't see enough information to help fully.

An important exercise for debugging, and a great tool that can come from it is to trace every wire and connection in the system, and drawing a simple diagram. The act of doing this may well turn up a wiring error that you, or we, can identify, and that you can correct.

Good luck. We're here to help.
Last edited by raysun on Sat Mar 28, 2020 10:50 am, edited 1 time in total.

badr15
Forum Member
Posts: 12
Joined: Fri Mar 27, 2020 1:05 am
My RE system: 24 panels 6 panels connected in serie(VOC 267 V) On 4 matrices 7.2 kW
Solar panels 24 panels installed on one base on sandy ground in the desert
must pv35-12kw inverter and ac charge
FLEXmax 100 AFCI charge controller
Outback FLEXnet DC monitor with 1 shunt for inverter
Outback MATE3s system controller
Outback Hub
battery 150 amp Circuit Breaker
battery hoppecke model: (8hpzs840) 2V (24pics) lead acid @ 48 volts 840AH
Running OpticsRE since March 2020
Location:Desert camp 70 miles north of riyadh saudi arabia @ elevation 250 ft

Re: technical problems

Post by badr15 » Sat Mar 28, 2020 8:23 am

Thank you for trying to solve the problem
and it remains for me to examine the installation steps and restore the factory settings to the device and I will inform you of the cause of the problem when solving it

fcwlp
Forum Guru
Posts: 295
Joined: Wed Jan 22, 2020 9:40 am
My RE system: GS8048A, FM80 w/3,600 W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed
I also install and maintain grid-tied and off-grid systems, details will be given for these system if required
Location: 80 miles NE of Phoenix at 5500'

Re: technical problems

Post by fcwlp » Sat Mar 28, 2020 10:41 am

badr15 wrote:
Sat Mar 28, 2020 12:53 am
Cooling
Cooling is the problem
I temporarily cool the divice with external fan
The problem of cooling device fan need a solution to run
The problem of the cooling fan in the device does not work, and when i restart the device and disconnect it from the batteries it works fan again and then turns off, i need a solution and operate it
fcwlp wrote:
Fri Mar 27, 2020 5:49 pm
A temperature of 50C is not considered to be hot for semiconductor technology. Per p.38 of the original FM100 manual, the fan turns off at 50C, on at 58C, output derating begins at 70C and over temp error is 90C.
Cooling is not a problem. You are showing an output FET temperature of 57C. The fan does not even turn on until 58C and you will not get an overtemp error until 90C. FYI, my primary career is as a semiconductor packaging engineer. Typical FETs are rated at junction temperatures of 100C or 125C, so Outback is being conservative in how hot they are allowing them to get. This is not something you need to be concerned about. If you are using a metric for acceptable devices temps for a CPU or GPU, these devices with 100+ million transistors are substantially different than the 1 transistor in a FET.

The FM100-AFCI CC having firmware at 2.0.1 not showing on the website is not an issue. The firmware shown for the original FM-100 on the website is different as the FM100-AFCI is a new CC with an AFCI function that required new firmware. Historically Outback has had very few CC firmware revisions and the user still can not update the firmware on FM60/FM80s.

Looking at your FM100-AFCI OpticsRE output, it looks like you are charging and discharging your batteries. At this point, I would focus on making sure your charging parameters are correct for your batteries.

Are you still having an issue with the MATE3s?

badr15
Forum Member
Posts: 12
Joined: Fri Mar 27, 2020 1:05 am
My RE system: 24 panels 6 panels connected in serie(VOC 267 V) On 4 matrices 7.2 kW
Solar panels 24 panels installed on one base on sandy ground in the desert
must pv35-12kw inverter and ac charge
FLEXmax 100 AFCI charge controller
Outback FLEXnet DC monitor with 1 shunt for inverter
Outback MATE3s system controller
Outback Hub
battery 150 amp Circuit Breaker
battery hoppecke model: (8hpzs840) 2V (24pics) lead acid @ 48 volts 840AH
Running OpticsRE since March 2020
Location:Desert camp 70 miles north of riyadh saudi arabia @ elevation 250 ft

Re: technical problems

Post by badr15 » Fri Apr 03, 2020 1:09 pm

I restored the factory setting then the fan worked and the problem was solved

mate3s work fine without problems

Thank you for responding to technical support to solve my problem, and this calculates your success .. Thank you




I have one more question
Filed at opticsre output power 6kW Capacity
While the product data (FLEXmax 100 AFCI)is 7000 watts and the system I have 48 volts is this normal?
I have a system connector 6 power panels respectively
4 sets were connected
I have 24 solar panels, all 6 connected together
Solar Panel Information
Image

Do I need another device or does the device meet my need

fcwlp
Forum Guru
Posts: 295
Joined: Wed Jan 22, 2020 9:40 am
My RE system: GS8048A, FM80 w/3,600 W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed
I also install and maintain grid-tied and off-grid systems, details will be given for these system if required
Location: 80 miles NE of Phoenix at 5500'

Re: technical problems

Post by fcwlp » Sat Apr 04, 2020 9:17 am

Hi, you have two issues with the present panel configuration.
1) With six panels in series, at -10C (14F) your Voc is ~295 which is caution area and at -16.2C (3F) you are over 300V which will cause an FM100 shutdown.
2) Your total panel wattage is 7,200, which is over the 7,000W limit.

With these panels, unless you are in a area that never goes below freezing, I would recommend a maximum of 5 panels in series and limit it 4 strings for one FM100. If you want to get two FM100s you could add another 16 to your current 24 or reconfigure the current 24 into 3 parallel strings of 4 panels.

raysun
Forum Emperor
Posts: 2105
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower One: FX3048T, (2) FM80, MATE3s, FlexNetDC
Outback 200NC batteries (8 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: technical problems

Post by raysun » Sat Apr 04, 2020 9:22 am

fcwlp wrote:
Sat Apr 04, 2020 9:17 am
Hi, you have two issues with the present panel configuration.
1) With six panels in series, at -10C (14F) your Voc is ~295 which is caution area and at -16.2C (3F) you are over 300V which will cause an FM100 shutdown.
2) Your total panel wattage is 7,200, which is over the 7,000W limit.

With these panels, unless you are in a area that never goes below freezing, I would recommend a maximum of 5 panels in series and limit it 4 strings for one FM100. If you want to get two FM100s you could add another 16 to your current 24 or reconfigure the current 24 into 3 parallel strings of 4 panels.
Watching my 5600W nominal arrays hit 5.9kW for about 10 min yesterday with a cloud edge effect, (109A charging current - the limit set by Global Charger Control), I'm glad that the arrays are split between 2 FM80s with headroom for such an event.

The 6kW indication on the OpticsRE "donut" can be changed in the System Tools/Devices page. Click the gear icon on the main page, then the "network of devices" icon. The setting is in whole kW, so select 7.

badr15
Forum Member
Posts: 12
Joined: Fri Mar 27, 2020 1:05 am
My RE system: 24 panels 6 panels connected in serie(VOC 267 V) On 4 matrices 7.2 kW
Solar panels 24 panels installed on one base on sandy ground in the desert
must pv35-12kw inverter and ac charge
FLEXmax 100 AFCI charge controller
Outback FLEXnet DC monitor with 1 shunt for inverter
Outback MATE3s system controller
Outback Hub
battery 150 amp Circuit Breaker
battery hoppecke model: (8hpzs840) 2V (24pics) lead acid @ 48 volts 840AH
Running OpticsRE since March 2020
Location:Desert camp 70 miles north of riyadh saudi arabia @ elevation 250 ft

Re: technical problems

Post by badr15 » Mon Apr 06, 2020 10:50 am

My system works in the Kingdom of Saudi Arabia and the temperature does not reach zero except for a week or x days a year so I thinh that the system will work without problems according to my arrangements
Thank you for answering my questions

raysun
Forum Emperor
Posts: 2105
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower One: FX3048T, (2) FM80, MATE3s, FlexNetDC
Outback 200NC batteries (8 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: technical problems

Post by raysun » Mon Apr 06, 2020 11:13 am

badr15 wrote:
Mon Apr 06, 2020 10:50 am
My system works in the Kingdom of Saudi Arabia and the temperature does not reach zero except for a week or x days a year so I thinh that the system will work without problems according to my arrangements
Thank you for answering my questions
Maximum panel power is generally experienced at colder temperatures, but is not the only way it can be achieved. Here in Hawaii, the average temperature is moderately high, and never reaches freezing at my locale. In general use, ambient temperature derates maximum panel power about 20% on average. My 5.6kW arrays (on 2 controllers) usually peak at around 4.2kW.

However, there is a phenomenon called cloud-edge effect that frequently drives array power much higher. When clouds pass in front of, and then away from the sun, the cloud edge can refract and concentrate light energy to a very high degree. If this "laser beam" of concentrated light shines on the panels, output can be driven to much higher than normal output. I have seen the arrays peak out at 6.1kW for periods exceeding two minutes in such a situation.

If your locale never has cold, and never has clouds, then you likely can "get away with" arrays that are over specification. Should there be an overpower event, however, the charge controller's FETs can act as very expensive fuses. Or worse, the charge controller can simply dump the overload directly to the battery. Sudden, high, over-charges can result in some pretty spectacular and catastrophic battery failures.

Do as you think best, but erring on the side of caution is never the wrong path.

fcwlp
Forum Guru
Posts: 295
Joined: Wed Jan 22, 2020 9:40 am
My RE system: GS8048A, FM80 w/3,600 W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed
I also install and maintain grid-tied and off-grid systems, details will be given for these system if required
Location: 80 miles NE of Phoenix at 5500'

Re: technical problems

Post by fcwlp » Mon Apr 06, 2020 11:25 am

badr15 wrote:
Mon Apr 06, 2020 10:50 am
My system works in the Kingdom of Saudi Arabia and the temperature does not reach zero except for a week or x days a year so I thinh that the system will work without problems according to my arrangements
Thank you for answering my questions
You are o'k with regards to temperature with six panels in series but with your 24 panels (4 strings of 6) you are over the maximum wattage allowed for the FM100 under nominal conditions and as raysun pointed out you will be way over with cloud edge effects.

Since you are in a sunny area, like my location in Arizona, another way to look at your present design is that you are wasting ~2,000W of PV. The FM100 can only output 100A which at 50VDC is 5,000W. You will have a much better design if you split your present array between two FM100s, both from the perspective of reliability but also increased power harvesting.

raysun
Forum Emperor
Posts: 2105
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower One: FX3048T, (2) FM80, MATE3s, FlexNetDC
Outback 200NC batteries (8 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: technical problems

Post by raysun » Mon Apr 06, 2020 11:29 am

fcwlp wrote:
Mon Apr 06, 2020 11:25 am
badr15 wrote:
Mon Apr 06, 2020 10:50 am
My system works in the Kingdom of Saudi Arabia and the temperature does not reach zero except for a week or x days a year so I thinh that the system will work without problems according to my arrangements
Thank you for answering my questions
You are o'k with regards to temperature with six panels in series but with your 24 panels (4 strings of 6) you are over the maximum wattage allowed for the FM100 under nominal conditions and as raysun pointed out you will be way over with cloud edge effects.

Since you are in a sunny area, like my location in Arizona, another way to look at your present design is that you are wasting ~2,000W of PV. The FM100 can only output 100A which at 50VDC is 5,000W. You will have a much better design if you split your present array between two FM100s, both from the perspective of reliability but also increased power harvesting.
"Dead contollers gather no power" does not have the same cache as "Dead men tell no tales", but the results are similar.

badr15
Forum Member
Posts: 12
Joined: Fri Mar 27, 2020 1:05 am
My RE system: 24 panels 6 panels connected in serie(VOC 267 V) On 4 matrices 7.2 kW
Solar panels 24 panels installed on one base on sandy ground in the desert
must pv35-12kw inverter and ac charge
FLEXmax 100 AFCI charge controller
Outback FLEXnet DC monitor with 1 shunt for inverter
Outback MATE3s system controller
Outback Hub
battery 150 amp Circuit Breaker
battery hoppecke model: (8hpzs840) 2V (24pics) lead acid @ 48 volts 840AH
Running OpticsRE since March 2020
Location:Desert camp 70 miles north of riyadh saudi arabia @ elevation 250 ft

You provided me a great solution

Post by badr15 » Tue Apr 07, 2020 5:16 pm

raysun and fcwlp You are right in your remarks
I will divide the array into two devices, each 2 x 6 device
For a power output of 3.6 kW per device, for a total of 7.2 kW
And take advantage of wasted energy
You provided me a great solution, thank you for that