Energy Dynamics - Anyone can explain?

Postby michaelASG on Tue Aug 08, 2017 2:54 pm

I wonder why the system works like this. I get 1.2 KW from the PV, while there is a 240W load, inverter is still grabbing 120W from the Grid.
System is set for Grid zero

WHY????
Attachments
energy dynamics.jpg
michaelASG
Member
 
Posts: 15
Joined: Mon Jul 31, 2017 10:03 am

Re: Energy Dynamics - Anyone can explain?

Postby Mike Curran on Tue Aug 08, 2017 4:35 pm

It looks like your battery is taking most of the PV. I can't speak to grid zero operation, but for my system if the battery's charge parameters aren't met it will ship PV to the battery until they are. Is your charge controller in bulk or absorb stage? That could explain it.
Mike Curran
OutBack Guru
 
Posts: 275
Joined: Sat Aug 28, 2004 6:28 pm
Location: Chagrin Falls, Ohio
My RE system: Outback: 8 (2x4) Evergreen 180's into one MX60, 6 (2×3) ALEO S79-300's into one FM80, 2 grid-tied GVFX3524's classic stacked for 120/240VAC, 12 Surrette/Rolls 2V x 1766Ah, Hub10.3, Mate3, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.

Westinghouse Solar: 30 (2x15) 235W panels with Enphase M215 microinverters. 6,450 nameplate watts AC, grid-tied.

Re: Energy Dynamics - Anyone can explain?

Postby michaelASG on Tue Aug 08, 2017 5:50 pm

Was in Bulk. Absorb starts at 61.5V
michaelASG
Member
 
Posts: 15
Joined: Mon Jul 31, 2017 10:03 am

Re: Energy Dynamics - Anyone can explain?

Postby jguzman on Wed Aug 09, 2017 2:08 pm

Also keep in mind in Grid Zero mode you will always be buying about 1~ amp which is why it shows 120W from Grid.

For further reading on this function, check out our App note:
http://outbackpower.com/downloads/docum ... -18-14.pdf

Jorge
Jorge Guzman
Technical Support Supervisor


Watch easy to follow video tutorials:
https://www.youtube.com/c/wattschool
jguzman
Applications Engineering
 
Posts: 137
Joined: Thu May 29, 2014 9:44 am
Location: Arlington, WA
My RE system: GVFX3524, FM80, MATE3. 3x 260W REC. 4x Trojan L16 FLA 370Ah.

Re: Energy Dynamics - Anyone can explain?

Postby michaelASG on Wed Aug 09, 2017 8:29 pm

I guess the only way to have a real Grid Zero (emphasis on Zero) is to disconnect the AC input somehow. Or maybe in a future update to allow a 0 setting for the DOD Amps, instead of 1. But it's kinda baffling to have lots of amps coming from the CC and still have to grab 120 Watts from the Grid...