Re: Current drops when switching from generator to batteries

This is common with gens that have their own built in cool down timer, The FX cuts AUX then drops the AC input but as it still "sees" incoming AC it reconnects after a short delay,,,, and then the gen stops, Giving low voltage/HZ error which is actually what is doing the switching, Unfortunately by ...
by blackswan555
Fri Sep 21, 2018 12:27 pm
Forum: Off Grid Applications
Topic: Genset Selecton
Replies: 41
Views: 16350

Re: Genset Selecton

Go to inverter 1 in hub port 1 for your aux, AGS etc gen start, as I mentioned, can not remember why, Maybe 8 years ago, but using FNDC relay was a problem

Tim
by blackswan555
Thu Sep 20, 2018 2:36 am
Forum: Off Grid Applications
Topic: Genset Selecton
Replies: 41
Views: 16350

Re: Genset Selecton

You need to get the hydrometer out and read SGs for a true indication of charge. Also remember there are 3 volt start settings, 2 min, 2 hr & 24 hr, I put them 0.4v apart on a 48v system, I can not remember what my usual settings were, but something like 2min 47.6v, 2hr 48v, 24hr 48,4v to give about...
by blackswan555
Fri Sep 14, 2018 12:54 pm
Forum: Off Grid Applications
Topic: Generator battery questions.
Replies: 2
Views: 1648

Re: Generator battery questions.

Depends on what you want to spend, A maintainer type battery charger is good but expensive (Well not quite as good as they say on the box) otherwise an "el cheepo" battery charger and a timeswitch giving the gen "a couple of hours a week" is my prefered option,

Tim
by blackswan555
Thu Sep 13, 2018 4:50 am
Forum: FLEXmax Charge Controllers
Topic: Current flowing backwards through FM80?
Replies: 23
Views: 8829

Re: Current flowing backwards through FM80?

May be worth swapping the controllers round on the shunts ( looks reasonably easy ?) See if the problem "follows" the controller or is it pre ?

Tim
by blackswan555
Thu Sep 13, 2018 3:34 am
Forum: OutBack
Topic: Trying to help a mate
Replies: 11
Views: 5054

Re: Trying to help a mate

A quick google says they are FLAs ? So you need to get a hydrometer to check SGs for a real state of battery charge, Looking at your lower picture you are only getting 1 hr of absorb, Which I suspect is because system has been left at default settings ? That would mean you are only getting one hour ...
by blackswan555
Wed Aug 22, 2018 2:14 am
Forum: RADIAN Series
Topic: Not Ideal but need to buy some time.
Replies: 11
Views: 4920

Re: Not Ideal but need to buy some time.

http://rollsbattery.com/public/docs/user_manual/Rolls_Battery_Manual.pdf is a good read & reference point, Your own battery manual would be a good starting place but do not forget if they are "Fork lift" batteries (Traction batteries as they are known) The charge regime will be a little different as...
by blackswan555
Tue Aug 21, 2018 1:44 am
Forum: RADIAN Series
Topic: Not Ideal but need to buy some time.
Replies: 11
Views: 4920

Re: Not Ideal but need to buy some time.

a fork lift battery, a 12k gen set and a few other odds and ends thrown in to make it work properly. Now here is my question and I know this is not IDEAL but I was wondering could I make it work until spring? Yes no problem, A lot of my previous sites, Some with no solar, the others,,,,, Nowhere ne...
by blackswan555
Tue Aug 14, 2018 8:00 am
Forum: FLEXmax Charge Controllers
Topic: 12v Solar Array vs 24v ..
Replies: 32
Views: 11334

Re: 12v Solar Array vs 24v ..

I think your settings are not far off (Could go a little higher on absorb voltage) I believe what we are seeing here is your batteries are VERY low, Nothing above shows you have even reached your absorb voltage, Which you would expect to see for 3 or more hours "on a good day" I guess that may be du...
by blackswan555
Sat Aug 04, 2018 9:21 am
Forum: OutBack Energy Cell Batteries
Topic: NC200 load voltage
Replies: 4
Views: 5807

Re: NC200 load voltage

Unsure as to what you mean by "charge voltage"; I'm under the impression that isnt specifically set, that the charge controller determines the voltage depending on the charge stage. Is that an incorrect assumption? No you have to set it "absorb voltage" from the manual "Absorb Charging Voltage 2.4 ...
by blackswan555
Sat Aug 04, 2018 5:32 am
Forum: OutBack Energy Cell Batteries
Topic: NC200 load voltage
Replies: 4
Views: 5807

Re: NC200 load voltage

What are you using to control charge ? voltage and time or SOC from your battery monitor ?

But to start, Your charge voltage is too low and your absorb time too short, refer to manuals for correct settings.

Tim
by blackswan555
Fri Jul 27, 2018 11:15 am
Forum: RV Applications
Topic: Convert Inverter: 50Hz @230 to 60Hz @ 240?
Replies: 4
Views: 6299

Re: Convert Inverter: 50Hz @230 to 60Hz @ 240?

Where in the world and what do you want to use it for ? EG 60hz & 230v is often the "norm" in parts of Asia, Apart from motors will run a little slower, most other things do not care ?
Tim

PS, filling your profile in as fully as you can will help us to help you :smile:
by blackswan555
Wed Jul 25, 2018 12:30 pm
Forum: FLEXmax Charge Controllers
Topic: load rail voltage ...
Replies: 16
Views: 5353

Re: load rail voltage ...

It seems to me that you have "el chepo" inverter and you are trying to blame you present fault on something that is pretty much industry standard ( if you have decent equipment,,, Not the first time I have read similar "problems") ?

Tim
by blackswan555
Mon Jul 23, 2018 12:57 pm
Forum: Flex Power One
Topic: Settings to increase charging Amps by generator
Replies: 12
Views: 9463

Re: Settings to increase charging Amps by generator

A little item that NO battery monitor takes into consideration,,,, Well a very big item if your want try to count amps in and out ,https://en.wikipedia.org/wiki/Peukert%27s_law

Tim
by blackswan555
Mon Jul 23, 2018 12:53 pm
Forum: Flex Power One
Topic: Settings to increase charging Amps by generator
Replies: 12
Views: 9463

Re: Settings to increase charging Amps by generator

Recently the batteries reached 50 percent State of Charge (SOC) Please do not take "that number" as a realistic State of charge in your actual batteries, it is a guess, that you have to take so many things into consideration,,,, its a guess (ok, it applies to all battery monitors, total guess, it d...
by blackswan555
Mon Jul 23, 2018 6:05 am
Forum: Off Grid Applications
Topic: generator
Replies: 34
Views: 10685

Re: generator

Firstly do not trust ANY battery monitor, They are only as good as they are set up and WILL drift over time, They should be recalibrated to SGs often, SGs are the only real way of knowing your battery state of charge, I equalized my batteries occasionally. I also have a hydrometer and took readings ...
by blackswan555
Mon Jul 23, 2018 3:29 am
Forum: Off Grid Applications
Topic: generator
Replies: 34
Views: 10685

Re: generator

I don't want to work my generator that hard. Can I set my I (I'm just guessing here) my bulk charge at, say, 58.8 and time it to run for 1 - 1 1/2 hours and then start on the absorb and float cycles? No, It does not work like that, Bulk is the first part of charge where the system is "trying " to g...
by blackswan555
Sun Jul 22, 2018 1:06 pm
Forum: Off Grid Applications
Topic: generator
Replies: 34
Views: 10685

Re: generator

Do you have FNDC ?
by blackswan555
Sun Jul 22, 2018 4:02 am
Forum: Off Grid Applications
Topic: generator
Replies: 34
Views: 10685

Re: generator

I am replacing batteries after 9 years. They've held up right well. I had 16 Surrette 530's. I'm replacing with 24 Surrette 550's (basically the same battery.) Any tips you can give me re the settings on my mate? In theory I should have 1200 plus amp hours and 48 volts. Have you ordered them yet ? ...
by blackswan555
Sat Jul 21, 2018 2:59 am
Forum: Off Grid Applications
Topic: generator
Replies: 34
Views: 10685

Re: generator

Make sure the model you have ordered is "2 wire start" capable, Also check the warranty conditions, Many are not covered for off grid use,,,,,, ](*,)

Tim,

Got a link to whatever you have ordered ?
by blackswan555
Thu Jul 12, 2018 3:07 pm
Forum: Off Grid Applications
Topic: Days Since Full now 48.1
Replies: 6
Views: 2037

Re: Days Since Full now 48.1

I do not bother with BCF or to be honest the FNDC at all, I prefer just to set an absorb time based on SGs, Whilst the FNDC is probably about one of the best on the market, It does not "compute" https://en.wikipedia.org/wiki/Peukert%27s_law or temp etc,, , None of the " battery monitors" do, Please ...
by blackswan555
Thu Jul 12, 2018 4:02 am
Forum: Off Grid Applications
Topic: Days Since Full now 48.1
Replies: 6
Views: 2037

Re: Days Since Full now 48.1

Have you got a Hydrometer and are reading cells to cross reference what the FNDC is telling you ? The FNDC is only as good as it set up and WILL drift over time anyway, Trust your hydrometer and calibrate the FNDC to "agree" with it and reconfirm often, Resetting it, Unplug and replug it, That will ...
by blackswan555
Sat Jul 07, 2018 3:47 pm
Forum: MX60 Charge Controller
Topic: Are my charge controllers obsolete?
Replies: 7
Views: 5544

Re: Are my charge controllers obsolete?

What are your absorb voltages and times ? Do you have temp compensation and what are your daytime loads ? It seems to me that you may already have enough incoming PV but it is possibly not optimised for its best ?

Tim
by blackswan555
Fri Jul 06, 2018 1:59 pm
Forum: RV Applications
Topic: I need an Alternative to PSDC for DC overcurrent protection
Replies: 1
Views: 2832

Re: I need an Alternative to PSDC for DC overcurrent protect

yes you can but you will need a little larger fuse, eg your inverter is 2000w at 12v , so 166amps at that, with the surge potential of these inverters, 200a would probably be a minimum,

Tim
by blackswan555
Fri Jul 06, 2018 1:02 pm
Forum: OutBack
Topic: Southern California Heat Wave Performance
Replies: 2
Views: 1951

Re: Southern California Heat Wave Performance

If you can find your panel coefficient of temperature rating that will give a good idea of loss with temp, Most are around 0.5% per deg C over 25c ( some "better" ones are rated at 40c) Also do not forget that normal STC (Standard test conditions) ratings are at 25c with 1000w per square meter of pe...