Re: Need an advice to select GS4048 or GS8048

Looking at the gs4048/8048 manual, it appears you're right about the max power output from either L1 or L2:Screenshot_20191119-192815.jpgAs far as max PV input from an AC - coupled array, per OB's app note on AC coupling, it looks like it's 6kw:Screenshot_20191119-194232.jpg Here's links to the per...
by mkimid
Wed Nov 20, 2019 9:53 am
Forum: AC Coupling
Topic: Need an advice to select GS4048 or GS8048
Replies: 6
Views: 3509

Re: Need an advice to select GS4048 or GS8048

What is the brand of your GT inverter? One thing you need to ask around is if your kind of GT inverter plays well with a Radian(GS) inverter. The other thing is, one of the requirements is the Outback inverter must be of higher capacity than the GT inverter. In their application note example,Radian...
by mkimid
Tue Nov 19, 2019 3:46 pm
Forum: AC Coupling
Topic: Need an advice to select GS4048 or GS8048
Replies: 6
Views: 3509

Need an advice to select GS4048 or GS8048

Hi, I have a plan to add an AC coupled back-up on my GTI system. I have installed sub-panel (for essential power), the peak load usage should be 0.1~3kW and, I have 320W(OTI inverter output) x 16 panel = ~5kW for the back-up system, I have expected that GS4048 is more than enough for me when conside...