Re: Skybox running 1.4.15

Each SkyBox needs to be programmed individually. I would use CONFIG1 as a starting point for each and update the appropriate settings that are related to capacity. Ah, end amps... to reflect the 3 batteries instead of 4.
by Gwendoly Espe
Tue Mar 03, 2020 1:33 pm
Forum: SkyBox Inverter
Topic: Skybox running 1.4.15
Replies: 3
Views: 3785

Re: Skybox running 1.4.15

Hello, The CONFIGURATION 1 and CONFIGURATION 2 are for the 3.8 SimpliPhi batteries. I believe CONFIGURATION 1 is for 4 X 3.8 SimpliPhi and CONFIGURATION 2 is for 6 X 3.8 SimpliPhi batteries. You could upload one of those and make the Ah, end amps, etc adjustments for your battery bank size. These CO...
by Gwendoly Espe
Sat Feb 22, 2020 4:33 pm
Forum: FLEXmax Charge Controllers
Topic: FM80 Hydro Diversion
Replies: 6
Views: 3385

Re: FM80 Hydro Diversion

I was informed that the FM60/80's never had that function working without solar. Not sure about the MXs.

The FM100 will operate the AUX port with or without solar.
by Gwendoly Espe
Mon Feb 10, 2020 12:51 pm
Forum: Mate3 / Mate3s
Topic: Mate3 wheel maintenance
Replies: 2
Views: 3377

Re: Mate3 wheel maintenance

brightspark wrote:
Wed Jan 29, 2020 11:52 am

Also is there a way to save the settings to the sd card? just in case someone resets it to default, I would like a backup.
https://www.youtube.com/watch?v=o-si8FNGgzs
by Gwendoly Espe
Wed Feb 05, 2020 11:48 am
Forum: SkyBox Inverter
Topic: Generator connection/use best practice w/ Skyboxx
Replies: 6
Views: 2785

Re: Generator connection/use best practice w/ Skyboxx

Mike, I leave my generator breaker closed and start the gennerator manually with a key fob remote. (cheap firman 3500 portable generator) After a preset delay (30 seconds but programable on the generator tab as Rayson mentioned) Skybox automatically passes the generator thru to the critical loads. ...
by Gwendoly Espe
Wed Jan 29, 2020 3:21 pm
Forum: SkyBox Inverter
Topic: Stacked SkyBox Inverters and Battery Banks
Replies: 1
Views: 2650

Re: Stacked SkyBox Inverters and Battery Banks

My question is about how the battery bank(s) are handled when stacking the SkyBox Inverters. To my understanding... when stacking these inverters each requires a separate battery bank. This concerns me as how does the system use each bank of batteries equally to prevent one from aging faster than t...
by Gwendoly Espe
Mon Jan 27, 2020 1:17 pm
Forum: RADIAN Series
Topic: GS7048 Inverter Shutdown
Replies: 3
Views: 3137

Re: GS7048 Inverter Shutdown

I have a stacked of 2 of 7kw outback inverters, on optics showing low soc while the other inverters using same batteries are not displaying this same error message. This will cause the inverter to shutdown. I need an explanation to this cause and possibly a solution.Thanks Is your system still havi...
by Gwendoly Espe
Thu Jan 23, 2020 11:34 am
Forum: RADIAN Series
Topic: GS7048 Inverter Shutdown
Replies: 3
Views: 3137

Re: GS7048 Inverter Shutdown

Are your Low Battery Cut Out Settings the same voltage?
by Gwendoly Espe
Wed Jan 22, 2020 12:16 pm
Forum: OutBack Energy Cell Batteries
Topic: Battery not staying at absorption
Replies: 15
Views: 7345

Re: Battery not staying at absorption

It sounds like this is resolved?
by Gwendoly Espe
Wed Jan 22, 2020 12:05 pm
Forum: RADIAN Series
Topic: Radian Inverter PREPA Parameters
Replies: 7
Views: 3747

Re: Radian Inverter PREPA Parameters

Agreed! I've already updated it, it should be on the website starting yesterday.
by Gwendoly Espe
Tue Jan 21, 2020 3:19 pm
Forum: FLEXmax Charge Controllers
Topic: Firmware Updates
Replies: 1
Views: 2272

Re: Firmware Updates

The FM60/80 are not field upgrade-able. The others may have purchased theirs more recently. If you want to upgrade your FM60, you will need to send it to us for manual firmware update. Call technical support to get details on how that works.
by Gwendoly Espe
Tue Jan 21, 2020 12:21 pm
Forum: OutBack Energy Cell Batteries
Topic: Battery not staying at absorption
Replies: 15
Views: 7345

Re: Battery not staying at absorption

Can you update your profile to include the equipment in your system and OpticsRE profile, if you have one? Where are you seeing this, on the inverter or charge controller?
by Gwendoly Espe
Tue Jan 21, 2020 11:41 am
Forum: RADIAN Series
Topic: Radian Inverter PREPA Parameters
Replies: 7
Views: 3747

Re: Radian Inverter PREPA Parameters

If you look at the requirement again, it says % of nominal voltage. So 45% of 120 = 54V . 120% of 120V is 144V. The settings are correct.
by Gwendoly Espe
Mon Jan 20, 2020 2:24 pm
Forum: RADIAN Series
Topic: Radian Inverter PREPA Parameters
Replies: 7
Views: 3747

Re: Radian Inverter PREPA Parameters

The PREPA settings should match the requirement, we'll look into that. I would recommend one of two things: 1) Try uploading the GIP file again, perhaps something happened in the process? OR 2) If you would like to quickly fix this, try looking at APP NOTE: Go to Page 6 under To Enter the Grid Suppo...
by Gwendoly Espe
Tue Jan 07, 2020 1:22 pm
Forum: SkyBox Inverter
Topic: Skybox control over generator charge input
Replies: 4
Views: 2541

Re: Skybox control over generator charge input

Stacking is available for Skybox! Just need to make sure you have a newer version of the firmware as the stacking feature is not available prior to firmware revision 1.2.22. Checkout Page 54 of the Skybox Manual if you need more information. Skybox will prioritize the protected loads over charging a...
by Gwendoly Espe
Mon Jan 06, 2020 12:47 pm
Forum: AC Coupling
Topic: Enphase Envoy microinverter detection thru Skybox
Replies: 21
Views: 10032

Re: Enphase Envoy microinverter detection thru Skybox

Back to the original topic: I've reconfigured my AC arrays so that my two rows of Westinghouse Solar modules (installed in 2012) are back to being simply grid tied, while the newer AC array (2019) is AC coupled to the Skybox output. I've also plugged the Envoy into the same circuit as the Westingho...
by Gwendoly Espe
Mon Jan 06, 2020 11:58 am
Forum: Off Grid Applications
Topic: Mate3S programming for 12v system
Replies: 1
Views: 1638

Re: Mate3S programming for 12v system

Hello, You shouldn't see 700W the entire time, but you may see it at a point in time during the charge cycle. It looks like in your AGS settings, you are using only Voltage Start. Once the batteries reach the target voltage, it will take less energy/power to maintain it there. The current (amps) to ...
by Gwendoly Espe
Thu Jan 02, 2020 2:29 pm
Forum: OutBack
Topic: Charging batteries with Outback
Replies: 1
Views: 2040

Re: Charging batteries with Outback

Thanks for sharing! \:D/
by Gwendoly Espe
Fri Dec 06, 2019 1:07 pm
Forum: Off Grid Applications
Topic: Removing Battery Connection
Replies: 11
Views: 2428

Re: Removing Battery Connection

From the VFXR manual: VFXRA The inverter is also controlled by a high battery cut-out limit. If the DC voltage rises above this limit, the inverter immediately stops functioning and gives a High Battery V error. This function is intended to protect the inverter’s output and loads. Continuing to inve...
by Gwendoly Espe
Fri Dec 06, 2019 12:03 pm
Forum: RADIAN Series
Topic: GS8048 replacement with GS8048A-01
Replies: 5
Views: 3436

Re: GS8048 replacement with GS8048A-01

Ensure your MATE3 is at firmware Version 003.017.000 (OPTICS RE) or higher. Older firmware versions of MATE3 are not compatible with the new GS8048A-01. ALL MATE3s are compatible with GS8048-01. Then I would check all of your AC Input Current Limits. This App Note covers the limits to check: Upgradi...
by Gwendoly Espe
Mon Dec 02, 2019 2:16 pm
Forum: Website & Forum
Topic: Having trouble accessing support
Replies: 1
Views: 2342

Re: Having trouble accessing support

Hello,

We apologize for the slow response. An OutBack SkyBox expert will be reaching out to you to assist you.
by Gwendoly Espe
Sun Nov 24, 2019 4:06 pm
Forum: FLEXnet DC
Topic: Newb Questions
Replies: 8
Views: 3484

Re: Newb Questions

FNDC is monitoring the State of Charge of the batteries. Check out page 6 (page 5 in pdf print) of the manual: FNDC Manual All shunts are wired the same, but notice that the inverter can charge the batteries or discharge the batteries. When the inverter is charging the batteries, it should be positi...
by Gwendoly Espe
Wed Nov 20, 2019 7:45 am
Forum: SkyBox Inverter
Topic: Resetting system maximums
Replies: 1
Views: 2600

Re: Resetting system maximums

The peak power value was captured in manufacturing, prior to the time being set. There is currently no method of resetting that value.
by Gwendoly Espe
Wed Nov 13, 2019 10:12 am
Forum: AC Coupling
Topic: Enphase Envoy microinverter detection thru Skybox
Replies: 21
Views: 10032

Re: Enphase Envoy microinverter detection thru Skybox

Edit : I'm just rewatching OB's AC coupling webinar and in it they say that the connection through the (Radian) inverter is a simple transfer relay contact. Assuming the same connection for Skybox, I wonder why this straight through connection prevents the Envoy from detecting the microinverters on...
by Gwendoly Espe
Mon Nov 11, 2019 1:47 pm
Forum: AC Coupling
Topic: Enphase Envoy microinverter detection thru Skybox
Replies: 21
Views: 10032

Re: Enphase Envoy microinverter detection thru Skybox

Hello Mike, It looks like the Envoy uses power line communication. I bet with a transformer-less topology that power line communication is disrupted through all the electronic switching in between the input and output. Have you had any issues with the AFCI and the Envoy? Devices that use power line ...