Re: Does this hardware exist?

@Heimhenge

I like your neat diagram. What app or drawing software are you using?
by EMCF
Thu Mar 05, 2020 12:28 pm
Forum: My OutBack Power System
Topic: help with 1-line diagram
Replies: 28
Views: 6631

Re: help with 1-line diagram

Adding a 100A disconnect between charge controller and battery is clearly called for. Since the FM100 has built-in arc fault protection, it need not be anything other than a standard 100A DC panel mount breaker. TBH, if there's room in the DC panel to mount another breaker, it will be faster, cheap...
by EMCF
Thu Mar 05, 2020 8:43 am
Forum: My OutBack Power System
Topic: help with 1-line diagram
Replies: 28
Views: 6631

Re: help with 1-line diagram

My take. Everything looks good, with the exception of missing disconnect means between FM100 and batteries. What I recommend is remove the existing breaker that I highlighted and place it between FM100 and batteries. You do not have to physically move the breaker, of course. Just modify the connecti...
by EMCF
Fri Feb 14, 2020 11:35 am
Forum: Marine Applications
Topic: VFX2812 Limiting Charging Current?
Replies: 6
Views: 1428

Re: VFX2812 Limiting Charging Current?

It is configured to limit AC current to 14A for charging (the maximum) and my current AC input voltage is 108V(this marina is a little low). That should mean that I have about 108A DC that could be given to the batteries if I am charging to 14V. For some reason I am only seeing 40A. The ambient tem...
by EMCF
Sat Jan 04, 2020 1:01 pm
Forum: My OutBack Power System
Topic: Shunts & SOC
Replies: 1
Views: 1579

Re: Shunts & SOC

The shunt readings are showing correct readings. When the shunt on inverter shows positive reading, it means the inverting is charging the battery. When the shunt for the CCs shows negative reading, that means none of the CCs are doing any charge and just showing the idle current consumed by the CCs.
by EMCF
Wed Dec 04, 2019 11:32 am
Forum: Off Grid Applications
Topic: Re-try autostart when genny is cold (second time works, can it be programmed?)
Replies: 4
Views: 961

Re: Re-try autostart when genny is cold (second time works, can it be programmed?)

I am confused. Where does Outback gear comes into play in your issues? If you are using AGS on the MATE, the Gen turn ON signal is a constant 12VDC from the AUX output of the inverter. The Gen stop signal is when the AUX output becomes 0VDC.So I'm not clear on your first try and second try situation.
by EMCF
Wed Nov 27, 2019 10:12 am
Forum: Off Grid Applications
Topic: Off Grid upgrade
Replies: 108
Views: 15442

Re: Off Grid upgrade

sodamo wrote:
Wed Nov 27, 2019 9:39 am
But they come with the 12 Rolls Surettes and 21 Aquions that preceded. and a few hundred gallons of generator fuel. :grin:
But your Almighty Hawaiian dollars overcame all that :grin: Is that even 1:1 with the mainland dollars? lolz
by EMCF
Wed Nov 27, 2019 9:24 am
Forum: Off Grid Applications
Topic: Off Grid upgrade
Replies: 108
Views: 15442

Re: Off Grid upgrade

sodamo wrote:
Wed Nov 27, 2019 9:13 am
LOL, not so sure you’d like the path that got me here :grin:
I'd take all that, and then some, including your 12X 3.8 type Simpliphi :-"
by EMCF
Wed Nov 27, 2019 9:04 am
Forum: Off Grid Applications
Topic: Off Grid upgrade
Replies: 108
Views: 15442

Re: Off Grid upgrade

I would be glad to inherit your first world problems, David \:D/
by EMCF
Thu Nov 21, 2019 4:04 pm
Forum: RADIAN Series
Topic: 3 phase stacking GSLC's
Replies: 16
Views: 5029

Re: 3 phase stacking GSLC's

Your description of the Multi Phase Coordination feature admits that Outback knows the system should reject incomplete (2 of 3 phases) external AC input, because it would be dangerous to connected equipment to pass that electricity on. In the same way, the inverters shouldn't CREATE incomplete thre...
by EMCF
Wed Nov 20, 2019 4:28 pm
Forum: RADIAN Series
Topic: 3 phase stacking GSLC's
Replies: 16
Views: 5029

Re: 3 phase stacking GSLC's

I don't think so on the 4th though. Multi Phase Coordination, at least in the quick setup guide I found a reference to it in, refers to the inverters working together to reject a flawed external 3 ph source. This capability indicates that Outback realizes it's a problem to pass thru an incomplete 3...
by EMCF
Tue Nov 19, 2019 4:40 pm
Forum: AC Coupling
Topic: Need an advice to select GS4048 or GS8048
Replies: 6
Views: 2504

Re: Need an advice to select GS4048 or GS8048

What is the brand of your GT inverter? One thing you need to ask around is if your kind of GT inverter plays well with a Radian(GS) inverter. The other thing is, one of the requirements is the Outback inverter must be of higher capacity than the GT inverter. In their application note example,Radian ...
by EMCF
Thu Nov 14, 2019 12:20 pm
Forum: RADIAN Series
Topic: 3 phase stacking GSLC's
Replies: 16
Views: 5029

Re: 3 phase stacking GSLC's

Last I heard, the 110v versions of the vfx (I think) and Radian (I'm pretty sure) can't be configured in a three phase stack, so if that's true then your case isn't supported anyway. Either way, "keep supplying partial 3 phase power" should DEFINITELY not be the only way, and shouldn't even be the ...
by EMCF
Fri Nov 08, 2019 3:35 pm
Forum: RADIAN Series
Topic: 3 phase stacking GSLC's
Replies: 16
Views: 5029

Re: 3 phase stacking GSLC's

Jason, this is a reply to your 1:11 pm post. I may have not described my DC connections very clear. The negative and positive bus are actually both have common connections, with the difference that the battery breakers are in the positive cables. The basic GSLC usually comes with 2 shunts, one for C...
by EMCF
Fri Nov 08, 2019 10:22 am
Forum: AC Coupling
Topic: AC coupled - batteries not charging from solar array during outage
Replies: 89
Views: 18687

Re: AC coupled - batteries not charging from solar array during outage

Please explain why you are showing a link to a generator's frequency/speed control, when we are dealing with a non-mechanical inverter here? :-k
by EMCF
Fri Nov 01, 2019 8:22 am
Forum: Off Grid Applications
Topic: FXR 2812A cut-off voltage shut down issue
Replies: 10
Views: 1469

Re: FXR 2812A cut-off voltage shut down issue

Of course, MATE2 will not work!
by EMCF
Thu Sep 12, 2019 4:52 pm
Forum: RADIAN Series
Topic: 3 phase stacking GSLC's
Replies: 16
Views: 5029

Re: 3 phase stacking GSLC's

The safe and official way to connect the DC busses is, from battery bank, run one separate positive cable in series with a breaker to each GSLC. Yes, your negative can be common, and without a breaker. Run one cable to "phase A" GSLC, then make jumper cable to "phase B" GSLC, and another jumper cabl...
by EMCF
Tue Mar 26, 2019 9:49 am
Forum: Off Grid Applications
Topic: Stacking - Other options?
Replies: 11
Views: 3224

Re: Stacking - Other options?

Is there a specific reason to prevent the downstream inverter from back feeding its surplus production to the upstream Radian? Seems to me that the upstream Radian might make use of that surplus power to charge its batteries. Is it because the upstream Radian may not be able to use the power and th...
by EMCF
Mon Mar 25, 2019 3:58 pm
Forum: Off Grid Applications
Topic: Stacking - Other options?
Replies: 11
Views: 3224

Re: Stacking - Other options?

Yes, Kurt's solution is the best and the "by the book" solution. But if @bear really wants to experiment, the concerns aired can be mitigated, I think. To avoid selling by the downstream inverter, set the sell voltage to an unreal/unreachable voltage, like 60V, or the sell current to 0A, for double ...
by EMCF
Mon Mar 25, 2019 1:12 pm
Forum: Off Grid Applications
Topic: Stacking - Other options?
Replies: 11
Views: 3224

Re: Stacking - Other options?

I am rethinking my earlier opinion. I think that set-up where the output of one Radian goes to the AC In of the second Radian is a little more complicated than I thought. We want them to share the load equally, just like 2 paralleled generators, but what if the recipient Radian goes pass-thru? That ...
by EMCF
Mon Mar 25, 2019 8:13 am
Forum: Off Grid Applications
Topic: Stacking - Other options?
Replies: 11
Views: 3224

Re: Stacking - Other options?

xxxxxx...If the first option is not possible, then can the one's output act as the grid input for the second? Yes, that should safely work. Once the recipient Radian accepts the other Radian's AC input, you theoretically ties in the AC out (load). The load fed to either Radian is now being fed to b...
by EMCF
Fri Mar 22, 2019 9:26 am
Forum: OutBack Energy Cell Batteries
Topic: Battery Test Procedures, RE800
Replies: 9
Views: 4183

Re: Battery Test Procedures, RE800

They went into service March 29, 2017. To your comment below on 4000 watts, even my coffee pot @ 1500w will cause the voltage to drop enough to run the gen. Not good, at 2 years, with a supposedly high capacity type battery bank. Even an ordinary, good conditioned 4-12V VRLA batteries can handle 15...
by EMCF
Fri Mar 22, 2019 8:16 am
Forum: OutBack Energy Cell Batteries
Topic: Battery Test Procedures, RE800
Replies: 9
Views: 4183

Re: Battery Test Procedures, RE800

670 Ah. Keep in mind the sun was up and PV's active.In the past I have not had any problem drawing such a load. I have 220 power tools that at start up hit 5000 watts and then run at 3000. and no troubles. Oh ok. I re-read the post, it was after sunrise. So how long have you been using the battery ...
by EMCF
Thu Mar 21, 2019 4:30 pm
Forum: OutBack Energy Cell Batteries
Topic: Battery Test Procedures, RE800
Replies: 9
Views: 4183

Re: Battery Test Procedures, RE800

With 4000w of DC load plus the initial 100W, that seems a lot to handle for your battery bank. It should draw 70+Amps and in no time will bring down the battery voltage from its initial 56.7V.
What is their total AH as per nameplate?
by EMCF
Thu Mar 21, 2019 12:04 pm
Forum: OutBack Energy Cell Batteries
Topic: Battery Test Procedures, RE800
Replies: 9
Views: 4183

Re: Battery Test Procedures, RE800

ok, I got it now, the batteries are 2v, and they call them cells.